Punctured PEX
No matter what kind of tubing it is, I guess my main question is how to splice a new piece of tubing between two ends that are set in concrete. Is there such a things as a Uponor repair coupling?
Two btu per sq ft for degree difference for a slab
Comments
-
-
@Alan (California Radiant) Forbes . I have used this little gem of a crimp ring for years and with great success.
Two of these crimp rings with a "crimp" type coupling should make for a good repair.
It is important to remind you that the crimp rings are different for crimp type and expansion "uponor type."
You will need to use a crimp type coupling and not a expansion type coupling with these crimp rings.
There is a difference between
the two. The crimp type , if memory serves, has more contact barbs on it, and is meant to be used with crimp rings. This one pictured is made by Oetiker and should work well with a crimp coupling.
1 -
Helps if you can mark out the tubing with a thermal imaging camera. Also depends on how much 'damage' you can do.
Easiest is to carefully break up enough concrete to free up enough tubing to effect a splice in place.
If it's thin slab, wet bed, and you have access underneath, and it wouldn't make a mess, I'd probably break enough concrete to bend each end of the loop to make 2 splices under the floor, and finish the ceiling, if need be, with a flush access panel (for future inspection).
I guess it's a moot point that the tubing was that close to the toilet flange.There was an error rendering this rich post.
1 -
If it is in a curved section of the pex around the flange, that will be tougher to repair. I think you would need to expose a foot or more.
Now, at least one of the Pex B manufacturers is promoting expansion fittings on their B pex! So if their homework is correct either A or B is expandable.
If you do use a metal fitting or ring, it should be heat shrinked in a concrete pour.
If you can use a couple composite couplings and expander rings, no metal to worry about.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
-
Thanks everyone!I guess it's a moot point that the tubing was that close to the toilet flange.
I thought so too until the owner told me he was installing a Toto Unifit part.
I ordered some Oetiker rings along with the tool.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
-
I use the crush rings. The ones that the jaw of the tool completly encircles and physically crushed the black copper ring.
Those Ottenger (sp?) Stainless rings I call chich rings. I feel they dont put uniform pressure on the tube and the tube is more easily moved on the fitting as well. But they are loads easier to work with.
I'm always leery of expanding tube of unknown origin. Either of the crush or chich rings will work on all tubing. I shrink wrap the repairs before filling in with new concrete.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!2 -
Pretty much covered, but this is the way I've done it.
I think it is probably Pex A. My bane has been carpet layers that put tack strips in and drive a nail thru the tube.
I carefully chip, with a wood chisel, away the gyp-crete 6" on either side of the leak.
I cut the tube at the puncture.
I use a length of shrink tube (heavy duty) that will cover the joint.
I use a heat gun to the Pex to soften it and raise it up, slip on the shrink tube and Oetiker clamps. I use 1/2" for 1/2" Pex.
I expand the tubing and slip in a Shark-bit Pex B brass coupling, 1/2". Home Depot or Lowes.
I get the coupling in place and let the Pex shrink down.
I push the clamp on to the fitting which is a tight fit and use the tool to clamp it.
I move the shrink tube over the joint and use the heat gun to shrink it. I use a S-nail on each side of the repair to hold the Pex down to the sub floor.
The Oetiker clamps are stainless, but the small exposed brass of the coupling between the Pex needs protection from the concrete fill.
Test for leaks.
This works for me and I have never had a failure.
1 -
After more searching, we found the tubing ID: ThermaPEX which is a PEX A, but when the tubing was exposed, the leak turned out to be on the red tubing loop; perhaps Mr. PEX. Either way, the barbed fittings will make a good seal.
I'll be going back next Wednesday to make the repair.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab3 -
-
-
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab4 -
atta boy!Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Is it OK to reduce the ID with those fittings? I'd almost be tempted to put in a (gasp!) Sharkbite coupling--it wouldn't reduce the ID
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Every radiant manifold ive seen uses compression type (universal) pex connections. Those have insert fittings in the pex as well. 1/2" radiant loops generally are only 0.5-0.75 gallons/minute anyway.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
Thanks for the knowledge!!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
As it turns out, the fittings started to leak and we had to re-do the work with the Uponor method which I should have done in the first place.
I don't know if I tightened the crimp rings too tight or not tight enough. There's really no feedback when you're squeezing the crimping tool to tell you how far to go.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab2 -
I was honestly surprised you didn't use the expansion fittings the first time. As far as PEX goes, it's pretty much foolproof.
John0 -
@Alan (California Radiant) Forbes I gotta say, I have never had a problem with this crimp. Not a one.
Did you use uponor couplings?0 -
I think you void the warranty by using those crimp rings on that tube brand?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I was honestly surprised you didn't use the expansion fittings the first time. As far as PEX goes, it's pretty much foolproof.
I wasn't sure the tubing was PEX ADid you use uponor couplings?
I used these.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
I too, have seen those cinch clamps leak. I feel it's due to uneven pressure applied to the tube. When you use the cinch clamps the tube is easily moved back and forth on the fitting. Much more so than any other connection method.
I wonder if the red pex is Mr.Pex brand. I have used many thousands of feet of it. The oxygen barrier tube is only available in red.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
I would take another look at the fittings. They don't seem to be crimp couplings but expansion type couplings. The expansion type couplings will not work well with cinch crimp connectors. The couplings must be crimp type .0
-
The product description says:
"EASY TO USE: Fittings Work with Crimp Ring or Clamp Connection Methods"8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
If they were expansion fittings, they wouldn't have fit in the pipe unless an expansion tool was used first.Intplm. said:I would take another look at the fittings. They don't seem to be crimp couplings but expansion type couplings. The expansion type couplings will not work well with cinch crimp connectors. The couplings must be crimp type .
John0 -
I agree, it is a compromise ring connection intended for a one tool solution. It doesn't give 100% compression like the copper rings, especially right under the pinch point. Seems the tube spins freely under those clamps, unlike the copper rings.Solid_Fuel_Man said:I too, have seen those cinch clamps leak. I feel it's due to uneven pressure applied to the tube. When you use the cinch clamps the tube is easily moved back and forth on the fitting. Much more so than any other connection method.
I wonder if the red pex is Mr.Pex brand. I have used many thousands of feet of it. The oxygen barrier tube is only available in red.
I think the original intent for the Oetiker clamp was rubber type automotive hose, CV boots, beverage hose, a softer hose type.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
There were two reasons I went looking for a non-Uponor system: One was that I wasn't sure that the tubing was PEX A and the other was that I wanted a smaller coupling because I wasn't sure I could bend the tubing far enough to get the last coupling on without kinking it. And I didn't want to be rushed by the few precious seconds you have to insert a fitting after expanding the tubing.
It was great to have enough tubing exposed to be able re-work the connections with Uponor and I am grateful to @Intplm. to show me what worked for him. It turned out to be a wonderful experience in the school of hard knocks.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
I've used the Viega PureFlow coupling on these types of repairs for the past 10 years. The press assures a secure connection and the pressjaw fits into small spaces. I wrap the splice with 10mil tape before the patch is made.
https://www.viega.us/en/products/Catalog/Plastic-pipe-systems/PureFlow-Press/Couplings/Viega-PureFlow-Press-coupling-V5615.html0 -
Hi @Alan (California Radiant) Forbes "A wonderful Experience in the School of Hard Knocks" would make such a nice title for an article! Now all you have to do is write the article and see if Erin wants it as a resource here in the Systems Help Center.
Yours, Larry1 -
-
-
No, not really @MaxMercy . The I.D. is not at issue. That crimp should have worked there. However. Nothing is infallible so this just happens to be an instance that it leaked.MaxMercy said:
If they were expansion fittings, they wouldn't have fit in the pipe unless an expansion tool was used first.Intplm. said:I would take another look at the fittings. They don't seem to be crimp couplings but expansion type couplings. The expansion type couplings will not work well with cinch crimp connectors. The couplings must be crimp type .
John0 -
If they were expansion fittings, they wouldn't have fit in the pipe unless an expansion tool was used first.
I had the same thought.
@Intplm. : When you say expansion fitting, I think Uponor in which case @MaxMercy would be correct. You cannot insert the fitting without expanding the tubing.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
Sure! And that's a beautiful view, Larry.Larry Weingarten said:Hi @Alan (California Radiant) Forbes "A wonderful Experience in the School of Hard Knocks" would make such a nice title for an article! Now all you have to do is write the article and see if Erin wants it as a resource here in the Systems Help Center.
Yours, LarryPresident
HeatingHelp.com1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements