Removing residential hot water from oil-fired Weil Mclain Gold boiler

crabbingladycrabbinglady Member, Email Confirmation Posts: 1
edited September 24 in THE MAIN WALL
I have an oil-fired Weil Mclain Gold boiler that supplies residential hot water and radiator heat. We are looking to convert to a hot water tank and remove the residential hot water function from the boiler. Besides capping off the residential water in/out pipes on the boiler, do we need to change any controls on the boiler?

Comments

  • EzzyTEzzyT Member Posts: 1,023
    You’ll need to disconnect the wiring of temperature control from the burner circuit. 
    Creative Solutions Plumbing & Heating LLC
    Lic #12683
    Co-Owners: Fred Drescher, Jr & Eliezer "Ezzy" Travis
    Marketing & Operations: Dawn Drescher
    201.499.0223
    Follow us on Facebook.
    Check us out on Instagram: creative_solutions519
  • IronmanIronman Member Posts: 5,740
    Bob Boan


    You can choose to do what you want, but you cannot choose the consequences.
    SuperTech
  • STEVEusaPASTEVEusaPA Member Posts: 4,362
    You don’t cap off both the hot and cold ports on the coil.
    steve
    mattmia2SuperTech
  • Jamie HallJamie Hall Member Posts: 13,202

    You don’t cap off both the hot and cold ports on the coil.

    Cap one, but leave the other open. Doesn't matter which -- but it's essential that one be open.
    Br. Jamie, osb

    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.

    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • mattmia2mattmia2 Member Posts: 1,726
    I suppose you could screw the relief valve on one instead of leaving it open.
  • Jamie HallJamie Hall Member Posts: 13,202
    mattmia2 said:

    I suppose you could screw the relief valve on one instead of leaving it open.

    Maybe A relief valve -- but not the relief valve. That still needs to be at or very near the water heater itself, directly piped, with a free drain to atmosphere. So why bother? Put a stopper in -- maybe from a wine bottle? -- if the open end is bothersome to you...
    Br. Jamie, osb

    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.

    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • mattmia2mattmia2 Member Posts: 1,726
    From the coil you are abandoning.
  • EBEBRATT-EdEBEBRATT-Ed Member Posts: 7,223
    A boiler like yours has a low limit control to maintain boiler water temperature. Depending on what controls you have the low limit may or may not be able to be disconnected.

    If that's the case you have a few options. Turn the low limit down' leave it where it is, replace the control or install a relay on the line side of the control
  • STEVEusaPASTEVEusaPA Member Posts: 4,362

    You don’t cap off both the hot and cold ports on the coil.

    Cap one, but leave the other open. Doesn't matter which -- but it's essential that one be open.
    Isn't that what I said?
    steve