Removing residential hot water from oil-fired Weil Mclain Gold boiler
crabbinglady
Member, Email Confirmation Posts: 1
I have an oil-fired Weil Mclain Gold boiler that supplies residential hot water and radiator heat. We are looking to convert to a hot water tank and remove the residential hot water function from the boiler. Besides capping off the residential water in/out pipes on the boiler, do we need to change any controls on the boiler?
0
Comments
-
You’ll need to disconnect the wiring of temperature control from the burner circuit.0
-
I just answered this on HVAC-talk. Are you the same person?
https://hvac-talk.com/vbb/showthread.php?2222184-Removing-residential-hot-water-from-oil-Weil-Mclain-GoldBob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
-
Cap one, but leave the other open. Doesn't matter which -- but it's essential that one be open.STEVEusaPA said:You don’t cap off both the hot and cold ports on the coil.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I suppose you could screw the relief valve on one instead of leaving it open.0
-
Maybe A relief valve -- but not the relief valve. That still needs to be at or very near the water heater itself, directly piped, with a free drain to atmosphere. So why bother? Put a stopper in -- maybe from a wine bottle? -- if the open end is bothersome to you...mattmia2 said:I suppose you could screw the relief valve on one instead of leaving it open.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
From the coil you are abandoning.0
-
A boiler like yours has a low limit control to maintain boiler water temperature. Depending on what controls you have the low limit may or may not be able to be disconnected.
If that's the case you have a few options. Turn the low limit down' leave it where it is, replace the control or install a relay on the line side of the control0 -
Isn't that what I said?Jamie Hall said:
Cap one, but leave the other open. Doesn't matter which -- but it's essential that one be open.STEVEusaPA said:You don’t cap off both the hot and cold ports on the coil.
There was an error rendering this rich post.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements