Issue with Rheem 62-22694-11 Control board
K_Rogers
Member Posts: 3
Hello to all,
I have a problem with both heating and cooling. My unit is a Rheem Criterion. No power to a Honeywell mechanical mercury Thermostat. Even when I jumper the switch to make the fan/AC/heat come on, nothing happens. Symptoms are as follows:
Breaker is good.... nothing thrown. Unit receives power.
Rheem Criterion has the 62-22694-11 control board. Both the "PWR" and "OK" LED light up when the blower door button is depressed.....yet at the thermostat, I have no power.
Is there a fuse on the 62-22694-11 that I am missing?
Do I need to replace the 62-22694-11 even though it is showing it has power and is OK?
Thank you for your input
Regards,
Kyle
I have a problem with both heating and cooling. My unit is a Rheem Criterion. No power to a Honeywell mechanical mercury Thermostat. Even when I jumper the switch to make the fan/AC/heat come on, nothing happens. Symptoms are as follows:
Breaker is good.... nothing thrown. Unit receives power.
Rheem Criterion has the 62-22694-11 control board. Both the "PWR" and "OK" LED light up when the blower door button is depressed.....yet at the thermostat, I have no power.
Is there a fuse on the 62-22694-11 that I am missing?
Do I need to replace the 62-22694-11 even though it is showing it has power and is OK?
Thank you for your input
Regards,
Kyle
0
Comments
-
Have you tried jumping terminals on the board or checking power at the board. A good first step is to eliminate the t-stat and t-stat wiring as the cause."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I was thinking that the board had power because of the LED being lit. I haven't tried jumping the terminals on the board. Will comment with the results. BRB0 -
This is what I found out:
On the board :
Jumper Red and Green will make the fan come on and stay on. No issues.
Jumper the the Red and Yellow nothing happens - just a hum.
Tie into the Red and touch the Yellow, it will spark then the fan will come on. AC never comes on, then the fan will stop.
hmmmmmmm.0 -
The hum might be the condenser coming on without the fan.
What happens R to W? It should run the heat cycle.
At this point it looks like the board is good. Check the thermostat wiring and thermostat.0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 892 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements