Reading Electrical Schematics - Vent Damper
Member Posts: 4,836
Reading and understanding electrical schematics and ladder diagrams is not one of my strong points and I'd like to improve my troubleshooting abilities here, with your help, by asking some specific questions.
I often get "no heat" calls and find vent dampers no longer working, interrupting the safety chain and preventing the boiler from firing. I consider vent dampers non-essential and troublesome just like the car in front of me stopped at a green light while they are talking on their cell phone.
Referencing the schematic below, I see the vent damper receiving continuous 24 volts from "Y" (neutral) and "R" (hot) wires. When there is a call for heat and the master relay closes, 24 volts passes through closed aquastats and powers the vent damper "O" wire which somehow opens the vent damper and also closes a switch to wire terminal "P" which sends 24 volts to the power vent (if any), the remainder of the safety chain and eventually to the ignition control module to start the ignition process. So, to bypass the vent damper, all I have to do is make sure the vent damper is open and jumper the "O" and "P" wires, correct?
Yes. And with a defective damper I would remove R & Y from the damper as well.0
Years ago (maybe they still do, I dont know), Honeywell or the boiler manufacturer provided a Male molex jumper if the damper wasnt being installed. Just plug it into the aquastat.0
The above advise is spot on.
The way I visualize this, R and Y are the hot and common for the motor load. When R is energized, the damper motor opens the damper. O and P are connected to a switch which proves that the damper has in fact opened. It is just a switch in series with the flame rollout and others. In order for the boiler to fire, all of the safeties need to close."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Yes sir. And somehow make sure the damper blade can never close again.gwgillplumbingandheating.com
Sorry I disagree...Never bypass a Safety. That's what a volt meter is for. Wiring, screwing, welding the damper open does not replace the function of the Safety!0
All the controls being black boxes does not make it easier to read. It isn't organized so well either.
So 24 vac between o and y causes the motor to open the damper, then that trips an end switch that closes between o and p when the damper is open. This would be a lot easier to understand if they showed the damper instead of a disconnected plug.0 -
Right, if the damper is not being used, then remove it completely. Cut a piece of 26 ga. to fill the gap or go to the next joint. 3 screws per joint.0