Can someone please tell me if this Barometric Damper is oriented the correct way?

rccrfan
rccrfan Member Posts: 51
Hi, The damper is set to Vertical mount position based on the weight placement. However, this damper is mounted on an angled pipe. Should I rotate the damper so that it is completely vertical or is this ok as is? Thank you
«1

Comments

  • rccrfan
    rccrfan Member Posts: 51

  • Jamie Hall
    Jamie Hall Member Posts: 24,884
    The axle of the damper has to be horizontal to function properly.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    STEVEusaPAdelta TGrallert
  • ChrisJ
    ChrisJ Member Posts: 16,317
    I'd want it corrected as Jamie said and I'd take that as a vertical pipe. However I'd want the burner tuned using a combustion analyzer at which time the damper would be set for proper draft so the actual numbers near the weight wouldn't mean much.

    @STEVEusaPA Your thoughts?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    STEVEusaPA
  • rccrfan
    rccrfan Member Posts: 51
    So what I'm understanding is to unscrew the damper rotate it until the label sticker is horizontal and then leave the weight set as is (vertical setting). Correct?

    The door swings smoothly as it is now. I'm trying to understand why rotating the damper would matter if the door swings freely. Thank you.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited February 2020
    Wrong, as mentioned by @Jamie Hall & @ChrisJ. What Jamie said. The two protruding pivot pins (where it swings) should be horizontal (level).
    And the face has to be plumb. Then you can set a proper over fire draft.
    But the flue pipe is the wrong gauge...oops.

    There was an error rendering this rich post.

  • Steamhead
    Steamhead Member Posts: 17,387
    @rccrfan , it affects the way the weights balance each other. Whoever installed that didn't read the instructions.

    Where are you located?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • pecmsg
    pecmsg Member Posts: 5,301
    PVC on the relief valve?
    mattmia2kcopp
  • rccrfan
    rccrfan Member Posts: 51
    edited February 2020
    The boiler documentation indicates that the flue pipe should remain the same diameter as the boiler outlet (which is 5") so I'm not sure why you're saying it is the wrong diameter? The flue pipe goes into a stainless steel chimney liner which is also 5". The chimney is exterior on the side of the house with 2 flues. One for a wood stove and the other for the boiler.

    I'm in CT
  • ChrisJ
    ChrisJ Member Posts: 16,317
    > @rccrfan said:
    > The boiler documentation indicates that the flue pipe should remain the same diameter as the boiler outlet (which is 5") so I'm not sure why you're saying it is the wrong diameter? The flue pipe goes into a stainless steel chimney liner which is also 5". The chimney is exterior on the side of the house with 2 flues. One for a wood stove and the other for the boiler.
    >
    > I'm in CT

    He said gauge as in wall thickness. Though I'm not sure how he could tell from a picture.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    rick in Alaska
  • rccrfan
    rccrfan Member Posts: 51
    I don't understand what wall thickness is? Do you mean the actual thickness of the flue pipes? They're the approved vent pipes that the manual recommends. I'm just a homeowner I don't work in the trade and I am trying to better understand.
  • ChrisJ
    ChrisJ Member Posts: 16,317
    > @rccrfan said:
    > I don't understand what wall thickness is? Do you mean the actual thickness of the flue pipes? They're the approved vent pipes that the manual recommends. I'm just a homeowner I don't work in the trade and I am trying to better understand.

    The thickness of the metal the pipes are made from.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • rccrfan
    rccrfan Member Posts: 51
    Ok. Yea, they’re the ones that came with it.
  • rccrfan
    rccrfan Member Posts: 51

    Fixed. Thank you guys
  • ChrisJ
    ChrisJ Member Posts: 16,317
    > @rccrfan said:
    > (Image)
    >
    > Fixed. Thank you guys

    Is it plumb across the face?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • rccrfan
    rccrfan Member Posts: 51
    Yes, there is a ring/ridge on the damper And it sits flush against the pipe
  • rccrfan
    rccrfan Member Posts: 51



  • rccrfan
    rccrfan Member Posts: 51

  • Jamie Hall
    Jamie Hall Member Posts: 24,884
    Bravo!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    My bad, optical confusion :) Thought it was 6" flue pipe and 26 gauge, which it would have to be a minimum of 24 gauge. But your ok with 5" & 26 gauge.
    Now you need to set up the over fire draft with a draft gauge.

    There was an error rendering this rich post.

  • mattmia2
    mattmia2 Member Posts: 10,958
    pecmsg said:

    PVC on the relief valve?

    I like that they bothered to prime it even though it doesn't have an acceptable temperature rating.
  • rccrfan
    rccrfan Member Posts: 51
    I think its rated at 300 degrees, but yea I have never been crazy with the PVC there. I'll probably replace it at some point.
  • mattmia2
    mattmia2 Member Posts: 10,958
    international mechanical code 1006.6
    13. Be constructed of those materials listed in Section
    605.4 of the International Plumbing Code or materials tested, rated and approved for such use in accordance with ASME A112.4.1.
    international plumbing code 605.4 does not list a spec for pvc

    (or the residential sections stating the same)
  • HVACNUT
    HVACNUT Member Posts: 6,342
    Well it's plumb and level but it's not fixed.
    Looks like a Buderus G115.
    Draft needs to be adjusted for 0 to +.01 over fire and -.02 at the breach. The only way that can be done is with a draft gauge, 0 smoke, and combustion test.
    Do you have an experienced tech to service and maintain?
    They should leave a printout of the combustion report at the time of the annual maintenance.
    mattmia2
  • rccrfan
    rccrfan Member Posts: 51
    The boiler install isn’t new, what happened was the flue started deteriorating (1950’s Ranch exterior double flue brick chimney). I was hearing the actual clay pieces breaking off and falling down the chimney so I had a SS liner installed. The flue pipe with the damper was vertical on the old flue setup, the new SS Liner setup resulted in the flue pipe with the damper being angled as pictured.

    The boiler itself was setup 4 years back when it was installed ( combustion test, draft, smoke, which is zero, etc.)

    I just though it odd looking that the damper wasn’t rotated when the reinstalled the pipe it is on. It was a chimney company that installs these as well as wood stoves, rebuilds chimneys etc.

    Unfortunately based on my recent experiences with the younger workforce is that they’re not technically knowledgeable. They’re able to do the task at hand but when it comes to a more in depth understanding of how things work, they’re lacking. I would think that they would have saw the damper and have known enough to rotate it so the axle was horizontal.

    I know I could have called the company and complained etc. but for me it is just easier to correct the minor problem myself. I don’t want them sending the same guy back that should have known enough to do it right the first time. Which led me to this forum.

    I see it everywhere, the skilled trades are having a hard time filling technical jobs. Heck, I used home advisor to installs screen door and the young guy mounted the handle 4 inches away from the catch on the frame and tried to remedy it by mounting a 3 inch block of wood in the door frame for the catch to mount to. For that one I did call and complain and they paid me for a new door and I just did it myself - bad back and all. Motrin is cheaper than the stress of dealing with incompetence.
    ratio
  • HVACNUT
    HVACNUT Member Posts: 6,342
    edited February 2020
    > @rccrfan said:
    >
    > The boiler itself was setup 4 years back when it was installed ( combustion test, draft, smoke, which is zero, etc.)
    >
    >

    4 years is not annual maintenance.
    The new liner will alter the draft.
    Find an experienced old tech then, but get it serviced. It's not a refrigerator where you set in place and walk away. It needs love and attention.
    mattmia2
  • rccrfan
    rccrfan Member Posts: 51
    edited February 2020
    oh, it does get annual maintenance just to be clear. I was just telling the backstory.

    Every tech I've had out here since the early to mid 2000's has been the next gen of younger workers. I don't know if its a regional thing of being mostly younger trades people but yea, I haven't seen an old tech in years.

    Not just for boiler stuff either- I've had a new deck and stonework done- all 20 somethings. I've had a new roof- all youngsters. Even the guys that did the boiler and indirect water heater were young. Its changing of the guards around here.
  • BillyO
    BillyO Member Posts: 277
    you need experience in the trade, tell me how a young kid can come and correctly troubleshoot? we are the old timers and dinosaurs of the trade my friends.
  • rccrfan
    rccrfan Member Posts: 51
    This is why I try and understand stuff myself around the house. A rushed young guy worries me.

    I do tent the refrigerator with an old sheet once a year and blow the coil underneath off. The tent keeps the kitchen from getting cat hair and dust everywhere.
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Is that foil tape on single wall Flue pipe? Just checking. I see that all too often in my neck of the woods.
  • rccrfan
    rccrfan Member Posts: 51
    Its all single wall. I asked the chimney guy if it should be used and he said they use it on all reline jobs. It's rated at 300 degrees. They said the pipes are already making a good sealed connection and they use the tape as an added measure. Should I be concerned?
    mattmia2
  • BillyO
    BillyO Member Posts: 277
    when we were in our 20s we had 10 years of working under our belt, whether it be a paper route or washing dishes in local catering hall etc..... for mere peanuts for pay. These kids now at 20 are on their first job and want top pay after 3rd paycheck.
  • rccrfan
    rccrfan Member Posts: 51
    Forgot to mention that all the pipe joints are screwed together under the foil tape.
  • rccrfan
    rccrfan Member Posts: 51
    Yea I am one of those homeowners that follows behind workers when they're here. Back when I had my A/C installed I had to remind them that there were dip switches to configure the variable speed air handler for comfort "R" (Trane)

    For the deck I had to remind them to install the hurricane ties which were in the contract but they didn't install until I reminded them.

    The boiler and indirect were the prize. You won't believe it- they actually forgot the gasket between the boiler and the burner. He had to unbolt it and install the gasket. That was another one where I had to call the owner and chew him out about his installers. After that phone call, they were sure to be more watchful.

    I hate to be one of those pain in the **** homeowners but can you blame me? What if I didn't keep an eye on things around here? I don't want to imagine.
  • Grallert
    Grallert Member Posts: 780
    The tape is going to see flue temps higher than 300F and it's going to melt. Not that it really matters the tape is not needed in the first place the will or should always be a negative draft at those seams. If someone puts an analyzer on that boiler and checks the draft you might find that the draft regulator is not needed at all.
    Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker
  • rccrfan
    rccrfan Member Posts: 51
    edited February 2020
    I will say I have a good plumber I use. He did some drainwork in the basement to plumb the kitchen drain which was hooked to a drywell in the yard. at the time- he hooled it to the main city drain in the basement. I guess at some point in the 1990's the city installed sewer pipes and the septic tank here was taken out and the main sewer line was hooked to city sewer.

    For whatever reason the kitchen drain wasn't connected because it went through another part of the foundation to the drywell.

    Anyway, the plumber was good. He even lined up the writing on the PVC pipes when he would join to pieces together.
  • rccrfan
    rccrfan Member Posts: 51
    I did try and use my thermal temp laser to measure the pipes temperature but it’s reflective so the reading wasn’t accurate. The boiler breach is black cast iron though and it reads around 250 degrees.
    The actual flue temp via combustion anaylizer around 375 degrees so I am thinking the tape will eventually come unstuck. At that point I’d probably just get some 600 degree 3M foil tape and re do it.
  • mattmia2
    mattmia2 Member Posts: 10,958
    BillyO said:

    when we were in our 20s we had 10 years of working under our belt, whether it be a paper route or washing dishes in local catering hall etc..... for mere peanuts for pay. These kids now at 20 are on their first job and want top pay after 3rd paycheck.

    And they find that somewhere else so if the trades dont pay that you dont get the people that can think it through.

    Then you top that off with expecting them to do 5 jobs in one day and evaluate them on if they did x jobs in this time, not if they were correct.

    The business philosophy developed based on the short term stock price causes large companies to always pick "cheap" and "fast" of the good, cheap, fast triangle.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited February 2020
    You don't need any tape. 3 screws per joint, equally spaced.
    But the draft does need to be set with an analyzer/manometer.

    Can't believe (well I can) that either the person who lined the chimney, or anyone performing your annual maintenance, couldn't take the 8 seconds to properly orient the damper.
    Tells me they didn't set up your burner or do a proper combustion analysis either.

    There was an error rendering this rich post.

    mattmia2SuperTechicy78delta T
  • rccrfan
    rccrfan Member Posts: 51
    The liner was just done the other day. The annual boiler tune is in the fall so he wouldn't have seen that yet. The chimney guys were young and apparently didn't know better. Leading back to they're competent enough to do the lining labor and hookup but when it comes to more in depth knowledge they're lacking.

    I hate to think how many other liners they've done where this kind of configuration was needed and they didn't change the damper orientation. And a lot of homeowners don't know to check or even care. They put blind faith in that the company doing the work are thorough .
  • mattmia2
    mattmia2 Member Posts: 10,958
    The bigger issue is that if you change the vent configuration like that, the combustion needs to be re-adjusted to the new vent. If it is an oil burner or any other form of power burner that is an absolute must. Presumably someone at the company has a mechanical license and knows that.
    icy78