Watch this video of a boiler with nearly catastrophic results from a failed heat exchanger.
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Comments
-
Could have been a disaster0
-
Wow that's scary. Glad you were able to find it before something happened
Ray Wohlfarth
Boiler Lessons0 -
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Yeah sure. The heat exchanger is cracked above the water line. When things get going in there, water spills out of the crack and into the burner tubes and gas can’t get through. Thus, the campfire.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes2 -
Thank you! Absolutely terrifying
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
And there's really no safety switch, sensor or device that covers that and can shut down the boiler is there? Did you ascertain the cause of the cracked heat exchanger? How old was the boiler?
0 -
I installed it in 2011!
I haven’t laid eyes on the split yet but the Gateway guys will strip it down today and I’ll report back soon.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
-
Wow.... that is scary indeed!Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
Hi Chris,ChrisJ said:@JohnNY
What is the typical life you are seeing from the Burnham IN series in your area?
I don't want to start any unjustified negative buzz on a manufacturer but I've had a few of the IN series boiler come back to me. They were all installed between 2008 and 2012. I've got many Burnham boilers installed in the early '90s out there still going strong.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
-
-
-
Fingers crossed. My IN-5 is on year 100
-
This.Grallert said:I don't have face book. I wonder if there is another source for the vid?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
> @Steamhead said:
> (Quote)
> This.
Get Facebook.
There are many that wish you and Gordo were there.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
I looks like it was cought soon. I can't imagine it would be that clean with a huge flame running up those wires and gas line0
-
I've tried Facebook three times and had bad experiences every time. Among other things, I did not approve of what they were doing with my personal data. I didn't even know the half of it. I would never encourage anyone to trust Facebook with their personal info. It's just not worth it.ChrisJ said:Get Facebook.
There are many that wish you and Gordo were there.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
> @Hap_Hazzard said:
> (Quote)
> I've tried Facebook three times and had bad experiences every time. Among other things, I did not approve of what they were doing with my personal data. I didn't even know the half of it. I would never encourage anyone to trust Facebook with their personal info. It's just not worth it.
If you had problems with Facebook, that you apparently didn't even know what they were, I recommend starting another thread and not derailing this one.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Not. Gonna. Happen.ChrisJ said:> @Steamhead said:
> (Quote)
> This.
Get Facebook.
There are many that wish you and Gordo were there.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting4 -
-
If you want to shill for Facebook, I recommend YOU start another thread.ChrisJ said:
If you had problems with Facebook, that you apparently didn't even know what they were, I recommend starting another thread and not derailing this one.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
That's what I did the second and third times. It helps, but they will still track you, because they can still access any cookies that were set on their domain or partners' domains. Facebook is a very dangerous place to be.STEAM DOCTOR said:Do what I did. Make account with fake info. Allows you access to other peoples videos and the like
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
> @Hap_Hazzard said:
> (Quote)
> If you want to shill for Facebook, I recommend YOU start another thread.
What I said was in regards to the original post.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
-
> @JohnNY said:
> (Quote)
> Hi Chris,
> I don't want to start any unjustified negative buzz on a manufacturer but I've had a few of the IN series boiler come back to me. They were all installed between 2008 and 2012. I've got many Burnham boilers installed in the early '90s out there still going strong.
Do you feel the roll out switch would catch this issue even if on the opposite side? Or would two switches be better?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Try this link, Facebook paranoia sufferers: https://flic.kr/p/2ieci3tContact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes4 -
I guess one rollout switch between every two burners would be best according to the unusual and unfortunate condition caught on this video but at some point, I guess manufacturers need to weigh cost and benefit. Bad sitch.ChrisJ said:> @JohnNY said:
> (Quote)
> Hi Chris,
> I don't want to start any unjustified negative buzz on a manufacturer but I've had a few of the IN series boiler come back to me. They were all installed between 2008 and 2012. I've got many Burnham boilers installed in the early '90s out there still going strong.
Do you feel the roll out switch would catch this issue even if on the opposite side? Or would two switches be better?
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
@SlamDunk Happy Birthday! I'm just a couple of years behind you and not ready for the pasture just yet.
I had to go on my wife's Facebook account to see the video. I have never seen anything like that. Even if I did, I don't think I would have come up with a good explanation. Thanks, @JohnNY!
Facebook may be cool, but not a place for me. I don't like the way they do business. HeatingHelp is my Facebook.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab2 -
Wow! No wonder they're called "burn 'em."Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Thanks, @JohnNY . Never saw one that bad- did the burners rust shut from all the leaking water?JohnNY said:Try this link, Facebook paranoia sufferers: https://flic.kr/p/2ieci3t
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Hi, Frank. No. The water kind of got stuck in the gas slots in the burners and closed them off. Everything inside looks like new including the burners. This is a freak occurrence I'm sure. I've never seen anything this bad caused by a section leak.Steamhead said:
Thanks, @JohnNY . Never saw one that bad- did the burners rust shut from all the leaking water?JohnNY said:Try this link, Facebook paranoia sufferers: https://flic.kr/p/2ieci3t
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Those pics aren’t related to the boiler issue but yes, that was a 2-pipe air vent system that I controlled with 1-pipe TRVs.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements