Watch this video of a boiler with nearly catastrophic results from a failed heat exchanger.

JohnNYJohnNY Posts: 2,389Member
For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
"72°F Mechanical, LLC"
Or email John at [email protected]
John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.
«1

Comments

  • EBEBRATT-EdEBEBRATT-Ed Posts: 6,307Member
    Could have been a disaster
  • RayWohlfarthRayWohlfarth Posts: 784Member
    Wow that's scary. Glad you were able to find it before something happened
    Ray Wohlfarth
    Boiler Lessons
    Click here to take Ray's class.
    Click here to buy Ray's books.
  • ethicalpaulethicalpaul Posts: 1,336Member
    Thanks for the video, @JohnNY--

    Can you explain how the failed heat exchanger caused that to happen?
    1 pipe Utica 112 in Cedar Grove, NJ, 1913 coal > oil > NG
  • JohnNYJohnNY Posts: 2,389Member
    Yeah sure. The heat exchanger is cracked above the water line. When things get going in there, water spills out of the crack and into the burner tubes and gas can’t get through. Thus, the campfire.
    For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
    "72°F Mechanical, LLC"
    Or email John at [email protected]
    John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
    John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.
  • ethicalpaulethicalpaul Posts: 1,336Member
    Thank you! Absolutely terrifying
    1 pipe Utica 112 in Cedar Grove, NJ, 1913 coal > oil > NG
  • D107D107 Posts: 1,609Member
    And there's really no safety switch, sensor or device that covers that and can shut down the boiler is there? Did you ascertain the cause of the cracked heat exchanger? How old was the boiler?
  • JohnNYJohnNY Posts: 2,389Member
    I installed it in 2011!
    I haven’t laid eyes on the split yet but the Gateway guys will strip it down today and I’ll report back soon.
    For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
    "72°F Mechanical, LLC"
    Or email John at [email protected]
    John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
    John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.
  • GrallertGrallert Posts: 358Member
    I don't have face book. I wonder if there is another source for the vid?
  • ChrisJChrisJ Posts: 10,374Member
    @JohnNY
    What is the typical life you are seeing from the Burnham IN series in your area?

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Solid_Fuel_ManSolid_Fuel_Man Posts: 1,836Member
    Wow.... that is scary indeed!
    Serving Northern Maine HVAC, and Controls
  • JohnNYJohnNY Posts: 2,389Member
    ChrisJ said:

    @JohnNY
    What is the typical life you are seeing from the Burnham IN series in your area?

    Hi Chris,
    I don't want to start any unjustified negative buzz on a manufacturer but I've had a few of the IN series boiler come back to me. They were all installed between 2008 and 2012. I've got many Burnham boilers installed in the early '90s out there still going strong.

    For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
    "72°F Mechanical, LLC"
    Or email John at [email protected]
    John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
    John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.
  • EBEBRATT-EdEBEBRATT-Ed Posts: 6,307Member
    Good for roasting marshmallows. The only thing that could have saved it is a rollout switch.

    I don't know about other states but MA requires an electrical firomatic on the ceiling for oil...but not for gas.

    Wouldn't be a bad idea for any boiler or furnace. I know of 1 house that it saved
  • STEAM DOCTORSTEAM DOCTOR Posts: 977Member
    Wow. Seen endless leaking boilers. Never seen anything like that.
  • STEAM DOCTORSTEAM DOCTOR Posts: 977Member
    Personally, I have seen lots of Burnham In's not make it past 15 years
  • SlamDunkSlamDunk Posts: 690Member
    edited January 12
    Fingers crossed. My IN-5 is on year 10
  • SteamheadSteamhead Posts: 13,501Member
    Grallert said:

    I don't have face book. I wonder if there is another source for the vid?

    This.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • ChrisJChrisJ Posts: 10,374Member
    > @SlamDunk said:
    > Fingers crossed. My IN-5 is on year 10

    Steamaster or equivalent water treatment. I'm betting they would have no problem lasting.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ChrisJChrisJ Posts: 10,374Member
    > @Steamhead said:
    > (Quote)
    > This.

    Get Facebook.
    There are many that wish you and Gordo were there.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Intplm.Intplm. Posts: 1,034Member
    I was just going to ask the same thing. Is there another place to see that video? I would like to and do not want to become a facebook person..... Facebook seems to intrusive to me. @JohnNY🤔 ?
  • Leon82Leon82 Posts: 652Member
    edited January 12
    I looks like it was cought soon. I can't imagine it would be that clean with a huge flame running up those wires and gas line
  • Hap_HazzardHap_Hazzard Posts: 1,930Member
    ChrisJ said:

    Get Facebook.
    There are many that wish you and Gordo were there.

    I've tried Facebook three times and had bad experiences every time. Among other things, I did not approve of what they were doing with my personal data. I didn't even know the half of it. I would never encourage anyone to trust Facebook with their personal info. It's just not worth it.
    Just another DIYer | King of Prussia, PA

    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • ChrisJChrisJ Posts: 10,374Member
    edited January 12
    > @Hap_Hazzard said:
    > (Quote)
    > I've tried Facebook three times and had bad experiences every time. Among other things, I did not approve of what they were doing with my personal data. I didn't even know the half of it. I would never encourage anyone to trust Facebook with their personal info. It's just not worth it.

    If you had problems with Facebook, that you apparently didn't even know what they were, I recommend starting another thread and not derailing this one.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • SteamheadSteamhead Posts: 13,501Member
    ChrisJ said:

    > @Steamhead said:

    > (Quote)

    > This.



    Get Facebook.

    There are many that wish you and Gordo were there.

    Not. Gonna. Happen.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • STEAM DOCTORSTEAM DOCTOR Posts: 977Member
    Do what I did. Make account with fake info. Allows you access to other peoples videos and the like
  • Hap_HazzardHap_Hazzard Posts: 1,930Member
    ChrisJ said:


    If you had problems with Facebook, that you apparently didn't even know what they were, I recommend starting another thread and not derailing this one.

    If you want to shill for Facebook, I recommend YOU start another thread.
    Just another DIYer | King of Prussia, PA

    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • Hap_HazzardHap_Hazzard Posts: 1,930Member

    Do what I did. Make account with fake info. Allows you access to other peoples videos and the like

    That's what I did the second and third times. It helps, but they will still track you, because they can still access any cookies that were set on their domain or partners' domains. Facebook is a very dangerous place to be.
    Just another DIYer | King of Prussia, PA

    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • ChrisJChrisJ Posts: 10,374Member
    > @Hap_Hazzard said:
    > (Quote)
    > If you want to shill for Facebook, I recommend YOU start another thread.

    What I said was in regards to the original post.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • SlamDunkSlamDunk Posts: 690Member
    edited January 12
    It was 70 today, Jan 12. Who needs a boiler?
  • ChrisJChrisJ Posts: 10,374Member
    > @SlamDunk said:
    > It was 70 today, Jan 12. Who needs a boiler?

    But what is today but yesterday's tomorrow?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • SeanBeansSeanBeans Posts: 472Member
    I also am not on Facebook and would like to view the video. Facebook is addicting and takes up too much time, which will take away from my time here on heating help!
  • ChrisJChrisJ Posts: 10,374Member
    > @JohnNY said:
    > (Quote)
    > Hi Chris,
    > I don't want to start any unjustified negative buzz on a manufacturer but I've had a few of the IN series boiler come back to me. They were all installed between 2008 and 2012. I've got many Burnham boilers installed in the early '90s out there still going strong.

    Do you feel the roll out switch would catch this issue even if on the opposite side? Or would two switches be better?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • JohnNYJohnNY Posts: 2,389Member
    Try this link, Facebook paranoia sufferers: https://flic.kr/p/2ieci3t
    For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
    "72°F Mechanical, LLC"
    Or email John at [email protected]
    John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
    John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.
  • JohnNYJohnNY Posts: 2,389Member
    ChrisJ said:

    > @JohnNY said:

    > (Quote)

    > Hi Chris,

    > I don't want to start any unjustified negative buzz on a manufacturer but I've had a few of the IN series boiler come back to me. They were all installed between 2008 and 2012. I've got many Burnham boilers installed in the early '90s out there still going strong.



    Do you feel the roll out switch would catch this issue even if on the opposite side? Or would two switches be better?

    I guess one rollout switch between every two burners would be best according to the unusual and unfortunate condition caught on this video but at some point, I guess manufacturers need to weigh cost and benefit. Bad sitch.

    For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
    "72°F Mechanical, LLC"
    Or email John at [email protected]
    John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
    John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.
  • SlamDunkSlamDunk Posts: 690Member
    ChrisJ said:

    > @SlamDunk said:

    > It was 70 today, Jan 12. Who needs a boiler?



    But what is today but yesterday's tomorrow?

    It is also tomorrow's yesterday: )
  • @SlamDunk Happy Birthday! I'm just a couple of years behind you and not ready for the pasture just yet.

    I had to go on my wife's Facebook account to see the video. I have never seen anything like that. Even if I did, I don't think I would have come up with a good explanation. Thanks, @JohnNY!

    Facebook may be cool, but not a place for me. I don't like the way they do business. HeatingHelp is my Facebook.
    Often wrong, never in doubt.

    Click here to learn more about this contractor.
  • Hap_HazzardHap_Hazzard Posts: 1,930Member
    Wow! No wonder they're called "burn 'em."
    Just another DIYer | King of Prussia, PA

    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • SteamheadSteamhead Posts: 13,501Member
    JohnNY said:

    Try this link, Facebook paranoia sufferers: https://flic.kr/p/2ieci3t

    Thanks, @JohnNY . Never saw one that bad- did the burners rust shut from all the leaking water?
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • JohnNYJohnNY Posts: 2,389Member
    Steamhead said:

    JohnNY said:

    Try this link, Facebook paranoia sufferers: https://flic.kr/p/2ieci3t

    Thanks, @JohnNY . Never saw one that bad- did the burners rust shut from all the leaking water?
    Hi, Frank. No. The water kind of got stuck in the gas slots in the burners and closed them off. Everything inside looks like new including the burners. This is a freak occurrence I'm sure. I've never seen anything this bad caused by a section leak.

    For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
    "72°F Mechanical, LLC"
    Or email John at [email protected]
    John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
    John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.
  • ratioratio Posts: 2,179Member
    I gotta ask, @JohnNY, about the Gortons on the TRVs. Did they, …ummmm… work? Do anything?

    Two pipe air vent system? I'm confused!

  • JohnNYJohnNY Posts: 2,389Member
    Those pics aren’t related to the boiler issue but yes, that was a 2-pipe air vent system that I controlled with 1-pipe TRVs.
    For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
    "72°F Mechanical, LLC"
    Or email John at [email protected]
    John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
    John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.