Steam Pipe Insulation

2»

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,381
    You really should at least "blow out" the pigtail to make sure it's clear. It's so important to not destroying vents and/or wasting fuel.

    The swaying may come from others :)

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    TC83
  • denkelly
    denkelly Member Posts: 30
    I blew it out when I added the 3psi gauge. I heard the water splash out of the pigtail. Yes I added some water back. I will also check it again when I take the p-trol off. I'll have a straight shot and I'll run a pipe cleaner through it.

    I ordered the new p-trol for $109 shipped with tax from Amazon. I'll see if I can put together a rig to test it before I install it. Money is tight, but if I mess up the p-trol and have to run to the plumbing supply I'm paying full retail. Also I get 6 months no interest paying $18 a month. Maybe I'll save that much in fuel costs to cover that ... B)
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    edited December 2019
    denkelly said:

    I just found a 404A 1033 on Amazon for $100 I have a 1009.

    I'm not sure if you can tell from the model number if it's additive or subtractive, but if it's additive, it should say "cut-in" above the scale. If it says "cut-out," follow the instructions for subtractive.

    Just be sure not to get a 404B. That would be bad.
    denkelly said:

    The set screw is caked in loctite

    That's just there to keep it from moving due to vibration. It breaks away when you turn the screw, and you can replace it with nail polish.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
    denkelly
  • ethicalpaul
    ethicalpaul Member Posts: 6,381
    In his closeup picture on the previous page, the set screw can be seen to be fully and completely flooded and covered with loctite. You couldn't get an Allen key into it.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846

    In his closeup picture on the previous page, the set screw can be seen to be fully and completely flooded and covered with loctite. You couldn't get an Allen key into it.

    I couldn't? I bet I could. Maybe you couldn't. :D
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
    ethicalpauldenkellyNeild5
  • denkelly
    denkelly Member Posts: 30
    The one I bought says cut in just like the one that I have and I've confirmed that this part number is a direct replacement.

    I know I could get an allen key in there, it just needs some heat on it and I have the tools..... 4 main reasons I got a new one:
    1) Local plumbing supply wants $150, and this was $100
    2) This is a safety device, not just a controller.
    3) the differential is off too. The dial is set to 1, but it's actually 1.5+.
    4) it was 11 degrees last night, it's not summer. better to be conservative.
    ethicalpaul
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    denkelly said:

    I know I could get an allen key in there, it just needs some heat on it and I have the tools.....

    I'd try a drop of acetone first, then move on to a few other solvents if that doesn't work. Being part of a boiler control, they probably used something somewhat heat-resistant, so it would take a little more heat than I'd care to try to apply to the inside of a Pressuretrol to melt it.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
    ethicalpaul
  • nde
    nde Member Posts: 86
    That is a lot of pressure in a short time, even my 40% oversize boiler will run 40 minutes before even building to 10 ounces. Looks like the near piping (esp the equalizer) is possibly the cause, or you have some partial obstruction between in the main(s) somewhere.
  • denkelly
    denkelly Member Posts: 30
    nde said:

    Looks like the near piping (esp the equalizer) is possibly the cause

    what's the equalizer?

  • denkelly
    denkelly Member Posts: 30
    So the new p-trol came in and ran the same damned pressures... I have no idea why I expected it to work properly....

    So I put a little heat on the set screw in the old trol and had to turn that set screw almost a full turn to get this to .5 cut in and 1.5 cut out.

    It's 51 degrees outside and 76 in my house right from playing with this... LOL
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    The equalizer is a pipe that runs from the header to a tapping located near the bottom of the boiler casting. The equalizer tapping is at about the same level as the draincock, but the tapping is usually larger.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • TC83
    TC83 Member Posts: 23
    Pretty sure non-ferrous pigtails are not required by nyc code, and most insurers will also request it if not already done upon renewal inspections. I went through this a couple years back.
  • ethicalpaul
    ethicalpaul Member Posts: 6,381
    Pretty sure non-ferrous pigtails are not required by nyc code


    Did you mean now required?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • dopey27177
    dopey27177 Member Posts: 887
    This is why you need to insulate the steam piping.
    1. your heat loss with un-insulated steam piping is about 20%.
    2. un-insulated steam piping creates excess condensed steam (water) in the steam piping.
    3. This condition can cause damage to all the vent valves in the system as well as water Hammer.

    See my take on BTUs saved when the piping is insulated.

    This example is in chapter five of my book, Steam the Perfect Fluid for Heating and some of the Problems

    Jake
  • denkelly
    denkelly Member Posts: 30

    This is why you need to insulate the steam piping.
    e

    This is where I am confused. My boiler is WAY oversized (about double), and even though everything is working (minus some minor water hammer at cold startup in one radiator) couldn't insulating the pipes cause problems? I thought that's what someone on here said.

    I also don't understand what short cycling is and if my boiler is doing it or not.... Once the system is hot,
    - the Flame goes on for about 3 minutes and the pressure hits 1.5psi and the flame goes off,
    - pressure drops within a 2 or 3 minutes to .5 psi
    - flame goes on for about 3 minutes until it hits 1.5psi
    - repeat until the thermostat (2nd Gen Nest) is satisfied.

    This process seems wasteful to me but I don't know how a properly sized boiler is supposed to behave.

  • denkelly
    denkelly Member Posts: 30
    nde said:

    That is a lot of pressure in a short time, even my 40% oversize boiler will run 40 minutes before even building to 10 ounces. Looks like the near piping (esp the equalizer) is possibly the cause, or you have some partial obstruction between in the main(s) somewhere.

    If I had a blockage would everything be working so well? I get heat in my furthest radiator within 15 minutes from cold.
  • ethicalpaul
    ethicalpaul Member Posts: 6,381
    edited January 2020
    This is where I am confused. My boiler is WAY oversized (about double), and even though everything is working (minus some minor water hammer at cold startup in one radiator) couldn't insulating the pipes cause problems? I thought that's what someone on here said.


    Insulating in your case will act to make your boiler even more oversized. But you are wastefully heating your basement so you have to weigh one evil against the other.

    I also don't understand what short cycling is and if my boiler is doing it or not.... Once the system is hot,
    - the Flame goes on for about 3 minutes and the pressure hits 1.5psi and the flame goes off,
    - pressure drops within a 2 or 3 minutes to .5 psi
    - flame goes on for about 3 minutes until it hits 1.5psi
    - repeat until the thermostat (2nd Gen Nest) is satisfied.

    This process seems wasteful to me but I don't know how a properly sized boiler is supposed to behave.


    That is pretty short cycling, yeah, due probably as you say to your oversized boiler. I call it "cycling on pressure".

    I wouldn't call it wasteful. I would call it not optimal. Consider if it just kept burning fuel even though all your radiators are full of steam. Now THAT's wasteful!

    The way it's supposed to work is that your radiation can condense all the steam that your boiler can create, so that the boiler keeps running until the thermostat is satisfied, never building pressure over .5 psi or whatever.

    Edit: and one more thing just to make sure: Have you verified that your new main vents close due to steam reaching them before the first time your boiler shuts down on pressure cut-out?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    denkelly
  • dopey27177
    dopey27177 Member Posts: 887
    To correct this problem of short cycling due to an oversized boiler. If it is oil fired have your service company install a nozzle. That will cause the boiler to take a longer time to produce steam.

    If you are gas fired yo may need to change the gas burner.

    After that is done you can insulate your steam piping and save a whole lot of money in fuel costs.

    Jake
  • Jamie Hall
    Jamie Hall Member Posts: 24,493
    If it can be downfired. Not all boilers can and work well...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Hap_Hazzard
  • denkelly
    denkelly Member Posts: 30

    To correct this problem of short cycling due to an oversized boiler. If it is oil fired have your service company install a nozzle. That will cause the boiler to take a longer time to produce steam.

    If you are gas fired yo may need to change the gas burner.

    After that is done you can insulate your steam piping and save a whole lot of money in fuel costs.

    Jake

    Gas not oil. And I have the EG-50 which is the smallest of this series (to my knowledge) so I don't think changing gas burners is an option. Anyone familiar with the Weil McLain EG series?

  • denkelly
    denkelly Member Posts: 30
    "But you are wastefully heating your basement so you have to weigh one evil against the other."

    Basement is finished, so it's not being wasted. I have an office down there and work from home a few days a week. I'm actually setting up a fan to blow warm air from the boiler room into the basement.

    "The way it's supposed to work is that your radiation can condense all the steam that your boiler can create, so that the boiler keeps running until the thermostat is satisfied, never building pressure over .5 psi or whatever."

    That makes sense to me, thank you. Basically the steam should be condensing as fast as the boiler is producing it. So if everything is working OK, no banging or uneven heating then it's not the worst thing, just sub-optimal.

    "Edit: and one more thing just to make sure: Have you verified that your new main vents close due to steam reaching them before the first time your boiler shuts down on pressure cut-out?"

    I will check this out and report back. Thanks!
    ethicalpaul
  • denkelly
    denkelly Member Posts: 30
    My main vents close before the first cut out and I see 190 degrees plus at every radiator in the house just before or right at that first cutoff. That happens in about 10-15 minutes.

    I really appreciate everyones comments, helpfulness and friendly attitude.

    Since my only issue is some light noise in one radiator in the living room on first steam, I'm gonna call this better than it was and good enough. If I ever have to change the boiler I know to downsize it big time.
  • ethicalpaul
    ethicalpaul Member Posts: 6,381
    OK sounds like good ol’ cycling on pressure. There are worse things.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    denkelly
  • TC83
    TC83 Member Posts: 23
    @ethicalpaul apologies for the delayed response, i am not getting notifications of threads i am in. But yes, in NYC (possibly NYS?) non-ferrous pigtail pipe for controls are required as of July 2008. My insurer nicked me on that a few years ago and only noticed because we stood there chatting about parking while he filled out paperwork! Doesn't seem like its actively enforced.
    ethicalpaul
  • denkelly
    denkelly Member Posts: 30
    edited January 2020
    TC83 said:

    But yes, in NYC (possibly NYS?) non-ferrous pigtail pipe for controls are required as of July 2008.

    You're talking about the iron pipe on my new pressure gauge?

    If you folks think it's an issue, I can buy brass pipes. The pressuretrol is all brass, it's just the gauges that are iron.

  • KC_Jones
    KC_Jones Member Posts: 5,792
    denkelly said:



    Gas not oil. And I have the EG-50 which is the smallest of this series (to my knowledge) so I don't think changing gas burners is an option. Anyone familiar with the Weil McLain EG series?

    I take no responsibility for this, but I ran an EG-45 with 2 burners removed for 12 years without any issues, but I'm sure the pros on here will seriously frown on that. Boiler was 32 years old when it finally died, so it did not seem to impact the longevity.

    If you were really ambitious you could, in theory, tear the boiler apart and remove a middle section turning it into either an EG-40 or EG-45, burner change, casing change etc. If hiring a professional it would probably cost as much as a new boiler so not worth it.

    What size is the piping coming out of that boiler? I can't tell if it's 2" or 2 1/2". I think there is something to an oversized drop header utilizing both tappings on the boiler. When reading all the stories on here, that setup seems to more effectively tame the beast when the sizing is less than optimal. I of course only have conjecture on that point. If it is only 2" that could be part of the problem as it would be choking the output down adding to your problem.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    ethicalpaul
  • TC83
    TC83 Member Posts: 23
    @ethicalpaul like i said, they are technically required, but rarely it seems enforced. if you blew them out and they were clear of obstruction then i do not see it being a high priority. Maybe summer time maintenance or if they eventually plug up. I only did it because i got threatened with non-renewal of insurance! crazy people these companies at times.
    ethicalpauldenkelly
  • denkelly
    denkelly Member Posts: 30

    What size is the piping coming out of that boiler? I can't tell if it's 2" or 2 1/2". I think there is something to an oversized drop header utilizing both tappings on the boiler. When reading all the stories on here, that setup seems to more effectively tame the beast when the sizing is less than optimal. I of course only have conjecture on that point. If it is only 2" that could be part of the problem as it would be choking the output down adding to your problem.

    First, I'm not that ambitious. I'm not having issues getting heat, so I don't currently see a financial savings that would equal the cost of changing out major boiler parts or otherwise making major modifications. my monthly costs are not astronomical. My house is attached ad my worst gas bill when it's below 20 degrees all month won't top $180.

    That is a 2" pipe. 7 1/2" Circumference which has an OD of 2 3/8 and an ID of 2 according to my sources.

    I don't see me tearing into that either or adding to the other tapping for that matter.

    Thanks




  • denkelly
    denkelly Member Posts: 30
    If anyone is interested, I have been slowly lowering the pressure and cut out occurs about 1.2 psi now and the water hammer in my living room radiator has ceased.

    Thanks again to everyone.
    Hap_Hazzard
  • ethicalpaul
    ethicalpaul Member Posts: 6,381
    We're all interested :smiley: Congrats!