Over Venting the Mains? Weak heat to 2nd floor. Please reAD.

Options
tumbz
tumbz Member Posts: 94
I have a steam boiler that has 2 main runs. Each main is about 30-40 feet to the end. On the end of each main has a 3/4 nipple with a big mouth vent on each. Im thinking about making an antler and adding another big mouth, making it 2 big mouth vents for each of the 2 mains....

would that be over venting???

The reason im doing this is because my first floor heats sufficiently and satisfies the thermostat before my 2nd floor is fully heated. The 2nd floor radiators has large capacity air valves and the 1st floor has all the air valves closed to the lowest so they heat up slower...

But the 2nd floor still heats only.half way when the cycle shuts.down...

Would venting the mains more help.in my situation???

Thanks for your help.
«1

Comments

  • tumbz
    tumbz Member Posts: 94
    Options
    I have a steam boiler that has 2 main runs. Each main is about 30-40 feet to the end on 2 inch pipe. On the end of each main has a 3/4 nipple with a big mouth vent on each. Im thinking about making an antler and adding another big mouth, making it 2 big mouth vents for each of the 2 mains....

    would that be over venting???

    The reason im doing this is because my first floor heats sufficiently and satisfies the thermostat before my 2nd floor is fully heated. The 2nd floor radiators has large capacity air valves and the 1st floor has all the air valves closed to the lowest so they heat up slower...

    But the 2nd floor still heats only.half way when the cycle shuts.down...

    Would venting the mains more help.in my situation???

    Thanks for your help.
  • Jamie Hall
    Jamie Hall Member Posts: 23,327
    Options
    Venting the mains more won't help with the balance problem -- you've got enough (although, to be fair, it's almost impossible to over vent a main... ).

    What air vents are you using on the radiators? Some variable vents don't close down all that far. And some are, oddly, too fast. On the upstairs radiators, do they heat across the top and close the vent before the whole radiator is warm, by any chance?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Fred
    Fred Member Posts: 8,542
    Options
    How close is your thermostat to a radiator? It may be that the thermostat is being satisfied before the rest of the house reaches set point. If that's the case, slow the venting even more on the near by radiator.
  • tumbz
    tumbz Member Posts: 94
    Options
    all the radiators on the first floor has the same hoffman a1 vents. THey are all closed!!! I turned them down to the closed setting o the radiators heat slow.

    The upstairs radiators, i have maid o MIST size D vents which are supposed to be the FASTEST venting valves.

    But even doing this, only half the radiator gets hot upstairs on a regular cycled. FOR EXAMPLE, if i leave the boiler on for AN extra 10 minutes after the thermostat has been satisfied , then the upstairs radiators will fully be heated.


    Do i need to tap the upstairs radiators to add ANOTHER air vent to vent faster?
  • tumbz
    tumbz Member Posts: 94
    Options
    the thermostat is on the first floor, and i did closed all the vents on the first floor so they vent slower, giving the 2nd floor a chance to catch up with the faster vents upstairs.

    but even doing so, the upstairs only heats halfway during a regular cycle. Should i tap them to add an addition aIR vent ????
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    Those Hoffman 1As are hard to adjust

    The numbers do not mean anything. There's too much slop in the lid. Remove the nut on one and you'll see what I mean.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • tumbz
    tumbz Member Posts: 94
    Options
    Yes ur right chris, but i adjusted it so that they cover the hole and then held it down and tightened it..... I am almost sure they are pretty closed...

    I guess i can just try to close a few radiators by the BALL VALVE and let it run a regular cycle to test if the upstairs gets heated all the way?

  • tumbz
    tumbz Member Posts: 94
    Options
    @ChrisJ do you know of a better vent? How about those vent rite #1?
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    No, do not close the valves.

    I like Gorton vents but they're not adjustable.
    You could try a few G4s on the first floor and G6s on the second floor and see how it does.

    G5 is a good "normal" vent. 4 is really slow 6 is fast C is really really fast.

    I would start with 4s and 6s and go from there.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Danny Scully
    Danny Scully Member Posts: 1,425
    Options
    Vent-rites are great too, and adjustable.
  • Fred
    Fred Member Posts: 8,542
    Options
    Do you have a programmable thermostat? If so, is it set for "Steam" at 1CPH? They come from the factory set at 5CPH for forced air. It may be that the boiler isn't running long enough to get the radiators hot. Also, in most cases, radiators won't heat all the way across unless it is really cold outside and the boiler runs for a long time. It's the room temperature you should be trying to balance.
  • gfrbrookline
    gfrbrookline Member Posts: 753
    Options
    I am thinking @Fred is on the correct path. Is the upstairs comfortable temperature wise? If not and the thermostat is satisfied before the upstairs heats the thermostat is likely in the wrong location or set to the wrong CPH.

    From my experience a MoM D is way too aggressive for almost all radiators. I have a three story 6 unit condo building and started out thinking that more venting would help cool units, after a couple of years of trial and error I found the opposite to be true. The largest radiator vent I have is a Gorton 6 on a large 8 fin 36" high radiator on the third floor, I tried a D on it and it only heated on the sides and top, the center was always room temperature and the room got cooler. All of my vents are Gorton 4's and Vent rite #1's, had bad luck adjusting Hoffman 1A's.

    As far as the mains, the main vents basically vent the the mains so if the heat is equally distributed on the first floor your main venting is fine.
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 1,973
    Options
    Might not be a venting problem. Could be a wet steam problem. Wet steam will die the future it travels.
  • tumbz
    tumbz Member Posts: 94
    Options
    I think i should move my thermostat but if i move it upstairs, the first floor will be too hot!
  • tumbz
    tumbz Member Posts: 94
    Options
    i just checked my CPG. its at the slowest settings also.
  • tumbz
    tumbz Member Posts: 94
    Options
    im going to try the danfoss thermostatic valves on the rads closest to the thermostat so that it heats up last, giving the upstairs more run time before the cycle shuts down.

    THANKS GUYSSSSSSSSSSSSSSSSS ill report back
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    > @tumbz said:
    > im going to try the danfoss thermostatic valves on the rads closest to the thermostat so that it heats up last, giving the upstairs more run time before the cycle shuts down.
    >
    > THANKS GUYSSSSSSSSSSSSSSSSS ill report back

    No you do not want a txv near the thermostat!

    Just get a few Gorton 4s and go from there.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • John Ruhnke
    John Ruhnke Member Posts: 882
    Options
    Steam moves fast! Very fast! It takes seconds to travel to the tenth floor of a ten story building.

    It shouldn't take ten minutes to get steam to the second floor. Something is not designed correctly. Could be uninsulated piping or backpitched piping with some trapped condensate. To small a steam boiler? or Header? Wet steam? Clogged or undersized piping? Thermostat could be short cycling the boiler? Or the air doesn't get out fast enough.

    There is a problem that hasn't yet been solved. If you solve it the second floor radiators will heat just as fast as the first floor ones.
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • tumbz
    tumbz Member Posts: 94
    Options
    @John Ruhnke I insulated all the piping on the mains and around the boiler.

    My mains are 2 inch piping with 3/4 inch pipings teeing off to the first and 2nd floor rads.

    I changed both my main vents with big mouth vents, changed the pigtails, flushed my system, everything looks good and works well.

    Its just that the thermostat turns off since the first floor reaches the set temp before the 2nd floor gets fully hot. I guess thats the nature of a 1 pipe steam system.

    I dont know what else to do. I already put large venting air valves up stairs to try to get the steam there faster.

    The only other thing left to do is to slow down the heat on the first floor by the THermostat so the boiler runs 5-10 minutes longer to fully heat the 2nd floor. Im guessing my only other air vavlve choice is danfoss thermostatic vavles, since i can turn it all the way down..??

    What do you think?
  • tumbz
    tumbz Member Posts: 94
    Options
    @ChrisJ why not danfoss? Im thinking that if i try the gorton 4, and it still heats too fast, ill be out of luck and still need to buy a danfoss?
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    > @tumbz said:
    > @ChrisJ why not danfoss? Im thinking that if i try the gorton 4, and it still heats too fast, ill be out of luck and still need to buy a danfoss?

    The idea of a TXV is to control a radiator by room temperature. The venting still needs to be correct.

    That said, the last thing you want is a radiator that can control it self, even totally shut off being the main one that effects the thermostat.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • John Ruhnke
    John Ruhnke Member Posts: 882
    Options
    Check to see if the boiler is undersized.

    size a replacement boiler by counting all the radiation in the house. The total becomes the net EDR (equivalent direct radiation) rating of your replacement boiler. Steam doesn’t care about heat loss or anything else–only the amount of the length of piping. If the boiler is too small, part of the building will never heat; if it’s too big, the new boiler will short cycle, consume more energy and require more service calls.

    Sometimes large radiators require adding a extra vent. Drill a hole half way down the radiator under the first vent, tap it and add a second vent.

    Trying to diagnose a steam system from my house is difficult. If I was there at your house I would easily be able to find the problem by looking over the whole system. I am a low temp hydronics guy. There are some really great steam guys here on the wall. They know more about steam then I do. Check out "Find a Contractor" and invite one of those great steam guys to visit. I am sure they will spot something that you and I aren't thinking of right now.
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • ChrisJ
    ChrisJ Member Posts: 15,708
    edited October 2019
    Options
    > @John Ruhnke said:
    > Check to see if the boiler is undersized.
    >
    > size a replacement boiler by counting all the radiation in the house. The total becomes the net EDR (equivalent direct radiation) rating of your replacement boiler. Steam doesn’t care about heat loss or anything else–only the amount of the length of piping. If the boiler is too small, part of the building will never heat; if it’s too big, the new boiler will short cycle, consume more energy and require more service calls.
    >
    > Sometimes large radiators require adding a extra vent. Drill a hole half way down the radiator under the first vent, tap it and add a second vent.
    >
    > Trying to diagnose a steam system from my house is difficult. If I was there at your house I would easily be able to find the problem by looking over the whole system. I am a low temp hydronics guy. There are some really great steam guys here on the wall. They know more about steam then I do. Check out "Find a Contractor" and invite one of those great steam guys to visit. I am sure they will spot something that you and I aren't thinking of right now.

    If radiators are stealing steam you slow them down you don't replace the boiler unless it's an extreme case.

    I've got a boiler rated for 325sqft connected to 392sqft and it's fantastic. I'd never go back to the larger size.

    Right now the OP needs to fix his venting before attacking everything at once. One step at a time.......
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    tumbzCanucker
  • John Ruhnke
    John Ruhnke Member Posts: 882
    edited October 2019
    Options
    @ChrisJ
    You said
    "If radiators are stealing steam you slow them down you don't replace the boiler unless it's an extreme case.

    I've got a boiler rated for 325sqft connected to 392sqft and it's fantastic. I'd never go back to the larger size.

    Right now the OP needs to fix his venting before attacking everything "

    The op shut down all the air vents on the first floor and he still can't get enough steam to the second floor. That is impossible. Unless something isn't right. The op is missing something, The radiators should get hot in minutes. They do on my steam jobs.
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • John Ruhnke
    John Ruhnke Member Posts: 882
    Options
    @tumbz

    You Said
    "Its just that the thermostat turns off since the first floor reaches the set temp before the 2nd floor gets fully hot. I guess thats the nature of a 1 pipe steam system."

    No that isn't true. In 90% of the jobs I go to the second floor gets hot faster than the first floor. Unless something isn't right.

    Is there a big radiator next to the thermostat? Cause that would cause that problem too. If that radiator got hot fast. Proper location of the thermostat is important. Or shut that radiator 100% off.
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    > @John Ruhnke said:
    > @ChrisJ
    > You said
    > "If radiators are stealing steam you slow them down you don't replace the boiler unless it's an extreme case.
    >
    > I've got a boiler rated for 325sqft connected to 392sqft and it's fantastic. I'd never go back to the larger size.
    >
    > Right now the OP needs to fix his venting before attacking everything "
    >
    > The op shut down all the air vents on the first floor and he still can't get enough steam to the second floor. That is impossible. Unless something isn't right. The op is missing something, The radiators should get hot in minutes. They do on my steam jobs.

    If the boiler is hot and the mains are hot I can get steam to all 10 radiators in 90 seconds and they all get steam within a few seconds of each other.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • John Ruhnke
    John Ruhnke Member Posts: 882
    Options
    Is the thermostat mounted to a wall with the chimney in it?
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • tumbz
    tumbz Member Posts: 94
    Options
    @John Ruhnke its mounted on the wll in the living room right in the middle about 5 feet off the ground. There are 3 radiators nearby...

    Im thinking about trying to shut those down and run a regular cycle to see if thatll help my upstairs. If it does, ill just buy some slow venting valves... Maybe try the gorton 4 or danfoss thermostatic valves.

    @ChrisJ thanks guys for trying to help. Im listening to all suggestions.
  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    You said you have 2" mains with 3/4" taps for first and second floor radiators.....that sounds small. Are you sure of those sizes?
    ethicalpaul
  • John Ruhnke
    John Ruhnke Member Posts: 882
    Options
    @tumbz

    You said
    "There are 3 radiators nearby"

    Once the radiators get up to temperature then it is about the ratio of the heatloss. So here is what looks like the problem Room A has 3 radiators and is 300% oversized as heatloss goes. Rooms B C and D average 100% heatload. Even though B,C and D are properly sized with the thermostat in room A the thermostat shuts off as soon as room A gets warm. A heats up 3 times quicker than any other room. So the thermostat shuts off too early. The heat doesn't stay on long enough to heat the other rooms. The solution is to reduce the heating in room A by completely shutting off one radiator and reducing output with a slow flowing steam vents on the other two. You have to reduce the load of room A to 100% then the thermostat will stay on longer to heat the other rooms.
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • John Ruhnke
    John Ruhnke Member Posts: 882
    Options
    It is all about balance. If one room is 150% and another room is 100% sized you need to achieve balance. You either need to decrease the load in the first room or increase the load in the second room. I usually find it easier and cheaper to decrease the load from 150% to 100% than to increase from 100% to 150%.

    Of course if one room has 25% of the required load you need to increase that room. But I find 95% of the systems to be oversized so that is rare.
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • Fred
    Fred Member Posts: 8,542
    Options
    This is puzzling to me @tumbz . Is this a 1 pipe or 2 pipe system? From the way you describe the venting on your mains and on each radiator, I have to believe it is a 1 pipe system but then you say the run-outs to the radiators are 3/4" pipe. If that's the case, a 3/4" pipe may have the capacity to carry 15 or 20 EDR of steam and allow condensate to also return. Any radiator larger than a small 15 or 20 EDR radiator (typically used in small bathrooms) won't heat all the way across, no matter how you vent them.
    JUGHNEethicalpaul
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    > @Fred said:
    > This is puzzling to me @tumbz . Is this a 1 pipe or 2 pipe system? From the way you describe the venting on your mains and on each radiator, I have to believe it is a 1 pipe system but then you say the run-outs to the radiators are 3/4" pipe. If that's the case, a 3/4" pipe may have the capacity to carry 15 or 20 EDR of steam and allow condensate to also return. Any radiator larger than a small 15 or 20 EDR radiator (typically used in small bathrooms) won't heat all the way across, no matter how you vent them.

    I missed that....
    Yeah what's with the 3/4" piping?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    ethicalpaul
  • John Ruhnke
    John Ruhnke Member Posts: 882
    Options
    3/4 piping does sound small for a one pipe system.
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • JUGHNE
    JUGHNE Member Posts: 11,062
    edited October 2019
    Options
    Could we see pictures of your piping take offs; also some of the
    boiler piping showing floor to ceiling?

    What pressure does the boiler run at?

    Is there a chance you have a 2-pipe air vent system?
    Pictures of both ends of your radiators would be good.
  • tumbz
    tumbz Member Posts: 94
    Options
    @JUGHNE OK PICTURES coming now. Im just guessimating the main pipe size, im not a plumber. I said the run offs from main were 3/4 because the big mouth air vent i connected to it is a 3/4th. HAHA. Mains are probably 3 inches, and the run offs, im not too sure, but here are pics of everything!

    :D
  • tumbz
    tumbz Member Posts: 94
    Options
    Im sure i have a 1 pipe steam system.

    ***1) This is pic of my radiator teeing off my main. I think main is a 3 inch and the run off is a 1 inch???



    ***2) Here are pics of my boiler.






    ***3) THESE ARE BOTH MY ENDS THAT I CHANGED TO BIG MOUTH VENTS, BARNES AND JONES.


  • tumbz
    tumbz Member Posts: 94
    edited October 2019
    Options
    my basement is finished so i had to look for my mains. HAHA.
    Luckily i found them both on first shot. Hard part was taking off old valves in such a small space..

    @JUGHNE boiler runs at low pressure, about 1.5. Pressuretrol is at .5 and 2.

    @John Ruhnke
    @Fred
    @ChrisJ
  • John Ruhnke
    John Ruhnke Member Posts: 882
    Options
    The mains and branches look fine. That header is way undersized though.
    I am the walking Deadman
    Hydronics Designer
    Hydronics is the most comfortable and energy efficient HVAC system.
  • Fred
    Fred Member Posts: 8,542
    Options
    @tumbz , That main looks like maybe 2". The radiator run-outs look to be 1". Are all the run-outs, including the ones to the first floor radiators the same size or are the first floor run-outs 1.25"? Typically 1" Run-outs can support about 28 EDR of steam, which is still a fairly small radiator. They need to be pitched well to get the most out of them. From the looks of that piping, did someone re-pipe the mains and radiator run-outs at some time and did they down size any of the piping? Can you see where the vertical pipe goes up to the second floor? Is the vertical pipe larger?