Legionaires Kills at Sheraton in Atlanta.
You can choose to do what you want, but you cannot choose the consequences.
Comments
-
-
-
@Ironman I just took over service for the boilers and water heaters at about 30 retirement homes throughout VA, MD, and DC. Almost all of them are running heaters with storage tanks at 110 degrees. No mixing valves.Never stop learning.0
-
Better find the Code for that jurisdiction. If your the last one to touch them your responsible!Mike_Sheppard said:@Ironman I just took over service for the boilers and water heaters at about 30 Sunrise retirement homes throughout VA, MD, and DC. Almost all of them are running heaters with storage tanks at 110 degrees. No mixing valves.
That's WAY too low!0 -
Get the water tested. It is not that expensive.Mike_Sheppard said:@Ironman I just took over service for the boilers and water heaters at about 30 Sunrise retirement homes throughout VA, MD, and DC. Almost all of them are running heaters with storage tanks at 110 degrees. No mixing valves.
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I think 110F is the code suggested temperature for retirement and child care facilities. But the tanks really should be elevated at the very least, ideally the entire system should be elevated above 140F , and mixed to that 110F.
Attorneys are now specializing in legionella cases, down to the facility you may have contacted it at.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Take a look at this article: http://www.prweb.com/releases/liquitech_and_spartan_bioscience_partner_to_bring_innovative_real_time_legionella_detection_to_health_care_sector/prweb16431923.htm
"Spartan Bioscience, creator of the world’s first on-site Legionella DNA test, today announced a partnership with LiquiTech, a leader in Legionella prevention for the health care, commercial, and hospitality industries. Through this strategic partnership, LiquiTech will integrate Spartan’s innovative environmental DNA testing platform to provide a new approach to detecting Legionella contamination. With Spartan’s test, Liquitech can detect Legionella contamination in real-time and provide immediate remediation using their multi-barrier approach to dramatically improve patient and guest safety. This will provide unparalleled control of Legionnaires’ disease in health care and hospitality environments."President
HeatingHelp.com0 -
I’m working on it. According to them their inspectors require 105 minimum and 120 maximum at the outlets of the faucets / showers. So they all set their storage tanks and supply to ~110.Never stop learning.0
-
really the only way to cover both bases is install point of use ASSE 1017 valves at every single faucet, set at 110, then run the tank up to 140F or higher.Mike_Sheppard said:I’m working on it. According to them their inspectors require 105 minimum and 120 maximum at the outlets of the faucets / showers. So they all set their storage tanks and supply to ~110.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
> @hot_rod said:
> I’m working on it. According to them their inspectors require 105 minimum and 120 maximum at the outlets of the faucets / showers. So they all set their storage tanks and supply to ~110.
>
> really the only way to cover both bases is install point of use ASSE 1017 valves at every single faucet, set at 110, then run the tank up to 140F or higher.
The several that keep their storage tanks 140 or above use a master mixing valve in the boiler room to send 110 out to the building. I know that’s not the right way to do it but that’s how everyone does it around here.
You should have seen this one retirement home I ran a service call to. Different than the ones I’m talking about here. They used domestic hot water to heat the building. 4 inch copper pipes of domestic hot water leaving the boiler room at 120 degrees. Bronze floor mounted end suction pumps. Pipe to each room went to an air handler and their sinks / showers.Never stop learning.0 -
That's a disaster and lawsuit waiting to happen.Mike_Sheppard said:You should have seen this one retirement home I ran a service call to. Different than the ones I’m talking about here. They used domestic hot water to heat the building. 4 inch copper pipes of domestic hot water leaving the boiler room at 120 degrees. Bronze floor mounted end suction pumps. Pipe to each room went to an air handler and their sinks / showers.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
> @Steamhead said:
> You should have seen this one retirement home I ran a service call to. Different than the ones I’m talking about here. They used domestic hot water to heat the building. 4 inch copper pipes of domestic hot water leaving the boiler room at 120 degrees. Bronze floor mounted end suction pumps. Pipe to each room went to an air handler and their sinks / showers.
>
> That's a disaster and lawsuit waiting to happen.
WOW!Steve Minnich0 -
That is still a common system, combined heating, cooling, DHW sold in large and small applications IPS integrated piping systems.Mike_Sheppard said:> @hot_rod said:
> I’m working on it. According to them their inspectors require 105 minimum and 120 maximum at the outlets of the faucets / showers. So they all set their storage tanks and supply to ~110.
>
> really the only way to cover both bases is install point of use ASSE 1017 valves at every single faucet, set at 110, then run the tank up to 140F or higher.
The several that keep their storage tanks 140 or above use a master mixing valve in the boiler room to send 110 out to the building. I know that’s not the right way to do it but that’s how everyone does it around here.
You should have seen this one retirement home I ran a service call to. Different than the ones I’m talking about here. They used domestic hot water to heat the building. 4 inch copper pipes of domestic hot water leaving the boiler room at 120 degrees. Bronze floor mounted end suction pumps. Pipe to each room went to an air handler and their sinks / showers.
I suppose it could be argued they are safer as all the HW piping is circulated all the time. Coil purge timers and valve assure even the small fluid capacity in the HX coils get flushed daily. Small potential for dead legs in un-used sections of the building.
A plate DWHX would separate the building from the public supply for protection of the other water customers.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The several that keep their storage tanks 140 or above use a master mixing valve in the boiler room to send 110 out to the building. I know that’s not the right way to do it but that’s how everyone does it around here.
That is what I did in my house, but I send 120F (not 110F) to the building. The reason I did that was that while I would have been delighted to send 140F to the dishwasher, and put a mixing valve at the other delivery points, all the pipes are buried in the concrete slab where my heating pipes are also buried. And everything else is in the walls (ceramic tile in the bathroom) and behind kitchen cabinets and stuff. So there are two that I could not put a mixing valve in, and several others, but those mixing valves are too expensive.
The actual outlet temperature from my indirect hot water heater is in the range of 140F to almost 160F. I have a dial thermometer in the hot supply to my mixing valve, and another in the delivery line from the mixer to the house.-1 -
yes, 120F is what all the major plumbings codes show for residential use. 110F for at risk population.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements