Condenser Pad

I am going to be pouring a large concrete pad for a condenser . My question is this , How do I know at what size pad that I should install Re-bar? Thanks in advance for the help!

Comments

  • STEVEusaPASTEVEusaPA Posts: 3,336Member
    How big is the condenser, how heavy. If its a regular residential, you probably just need WWF (welded wire fabric)
    https://en.wikipedia.org/wiki/Welded_wire_mesh
    steve
  • Steve MinnichSteve Minnich Posts: 2,468Member
    I’d argue you don’t even need that for residential.
    PHC News Columnist
    Minnich Hydronic System Design & Consultants
  • beanbean Posts: 34Member
    8 Ton Carrier . Pad must also be larger to incorporate fence cover (vandalism)'.
  • STEVEusaPASTEVEusaPA Posts: 3,336Member
    I'd grab the install instructions and see how much clearance you need on all sides and above. At a minimum, 3ft all around would make a tech not curse you.
    steve
  • Jamie HallJamie Hall Posts: 11,169Member
    A related question: what is the pad going to rest on? If it is properly compacted subbase and base -- 90 to 95 percent modified Proctor -- and that base is level and smooth, and the slab is a reasonable thickness, then you probably only need the welded wire. On the other hand, if you aren't going to or aren't able to compact the subbase and base, then you are counting on the rebar to hold the concrete together to spread the load to where the base can sustain it. And at that point, may I respectfully suggest that you get a licensed or registered Civil Engineer to answer your question... since there is no one good answer, never mind a rule of thumb.
    Jamie

    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.

    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • EBEBRATT-EdEBEBRATT-Ed Posts: 6,047Member
    In general make the pad 6" larger than the equipment on all 4 sides. Check clearances. If it's a breathable fence (chain link) you could cheat on the clearance to the fence but you need access for the condenser coil cleaning and service Pad 4" thick with wire mesh set on top of compacted gravel
  • pecmsgpecmsg Posts: 903Member
    If the security fence isn’t removable then 36” all around.