I’m converting a boiler to direct vent with a fan. Supply house told me if I put the fan close to an outside wall I can use smoke pipe, when I get out side or on other side of fan I can use stainless steel? Would that be the correct way of doing this?
0
Comments
-
Powervent not direct vent.To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
Which boiler, which kind of fan.
There was an error rendering this rich post.
0 -
Weil McLain 140,000 btu chimney vented, changing to power vented, the boiler less then ten years old and there building an addition and want to remove the chimney.
Note... I was called from someone doing the plumbing to just put the boiler direct fan on the unit and run it outside the house. Not to try to upsell them anything.
0 -
Oil or gas? And is that boiler listed to be used with a power vent? If not... don't do it.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I’m not sure I think they want to convert it. It’s a gas CGA0
-
I don't see anything in the manuals for the CGAs which provides for power venting... I'd contact Weil-McLain to see if they have any comments. Otherwise... you may be experimenting on your own.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
I think that field control makes a conversion kit. Will probably void manufacturer warranty0
-
I think the boiler is past it’s warrantee, my supply house says they do make a fan in a can for this?0
-
@Snowmelt
Has nothing to do with the boiler age, warranty or what the supply house says.
Gas appliances are listed to be vented a certain way. I would call Weil McLain directly and ask
Just tryin to keep you out of trouble1 -
-
I think field control does make kits, which most importantly have pressure switches to verify fan operation just like an other induced draft appliance.
But I think you’ll need a barometric damper and combustion analysis to fine tube the airflow to get it back to specs.
Ultimately, the boiler doesn’t care what happens to the flue gases. Just so that the fuel air ratio is correct and secondary air is adequate to prevent condensation in single wall pipe while also not wasting too much energy. You will mainly end up with excess secondary air and waste energy sucking air out of the house. No different than having a really tall chimney.0 -
If the appliance comes with hood you require permission from utility and provincial safety to remove it.0
-
In the case of the Field and Tjernlund power venter kits, the existing draft hood or barometric damper stays in place. The combustion appliance itself is not modified.jumper said:If the appliance comes with hood you require permission from utility and provincial safety to remove it.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Those normally mount at the outside wall. Outside the house is a hood like a big dryer vent. You run b-vent to the power ventor. They also show a barometric i the horizontal run. We've used them on 80% furnaces but not atmospheric draft boilers.
0 -
I’m going to find out the hard way, that’s what I will be doing Friday0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements