Unusual 2-Pipe Steam System
New England SteamWorks
Member Posts: 1,526
When I walked in to the house and saw all the radiators with 2 floor-level valves and a vent, I expected to find that each of the returns in the basement dripped into a wet return.
But I did not. Instead what I found is on the hastily sketched and attached diagram: Dry returns. I found standard radiator vents, no orifice plates in the valves, no traps, no main venting, and no nomenclature to provide a clue.
Another oddity that is initially confusing is that, rather than using a larger diameter pipe for the radiator supply and a smaller diameter for the radiator return, they used (identical) larger diameter pipe for the 1st floor radiators, and smaller (identical) diameter pipe for the 2nd floor radiators.
The system is not heating well. Very unbalanced and noisy. Steam is in the returns, obviously.
Was there a special type of vent to limit the steam originally? Doesn't seem likely that all the orifice plates would have been removed. I am certain there were never traps. The install seems high quality, and no sign of it having been knuckle headed.
My thought is to remove the radiator vents, add in-line traps in the basement on each return, and add main venting.
But I thought I'd run it by everyone to see what percolates.
Thanks.
But I did not. Instead what I found is on the hastily sketched and attached diagram: Dry returns. I found standard radiator vents, no orifice plates in the valves, no traps, no main venting, and no nomenclature to provide a clue.
Another oddity that is initially confusing is that, rather than using a larger diameter pipe for the radiator supply and a smaller diameter for the radiator return, they used (identical) larger diameter pipe for the 1st floor radiators, and smaller (identical) diameter pipe for the 2nd floor radiators.
The system is not heating well. Very unbalanced and noisy. Steam is in the returns, obviously.
Was there a special type of vent to limit the steam originally? Doesn't seem likely that all the orifice plates would have been removed. I am certain there were never traps. The install seems high quality, and no sign of it having been knuckle headed.
My thought is to remove the radiator vents, add in-line traps in the basement on each return, and add main venting.
But I thought I'd run it by everyone to see what percolates.
Thanks.
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com
0
Comments
-
Sounds like 2 pipe air vent system. Add traps or run a wet return and leave the air vents0
-
Two pipe air vent system. There's a good writeup on the in Lost Art...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thank you Jamie! I found in TLAOSH.
What is interesting here is that the radiator supplies and returns are the identical size, presumably making things worse...New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Yep, 2 pipe, air vent. They can be touchy if anything's been changed.
Try throttleling the return valves a little.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Hmm, that’s not typical of a 2-pipe air vent system to have same size supply/return. And very interesting how they piped the 2nd floor radiator under the first floor radiator...I’ll be pondering this tonight for you @New England SteamWorks0
-
The counterflow steam mains are unusual. Maybe that was originally a gravity hot-water system and someone converted it to steam?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I thought that as well @Steamhead, but you had the guts to say it I have a customer who’s house was moved. I believe the same is true of her radiators. Before the house was moved it was hot water, but once it met its final resting place it became steam I theorized this because all the air vents were in the upper plug location and all the radiators were also plugged on their return side with a regular (ugly ) plug not a radiator plug (therefore assuming not original).0
-
We've seen several such conversions in Baltimore.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Are the radiator valves original?Retired and loving it.0
-
The radiator valves appear to be original, yes.
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Love to see a tight closeup if you have one.Retired and loving it.0
-
I'll get one for you. It will be a bit before I get back there however.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements