New pole barn build. Questions and info??
kaama82
Member Posts: 11
Hello. Starting a new pole barn this summer. So looking for some opinions on heat source. My existing barn has Radiant floor and now it works great. Want to do a few things different this time around. Would like to use a boiler. I am a do-it-yourselver. So please if you can educate me on the do's and dont's. The building will be 40 x 88 with 14 foot sidewalls. I have some Estimated heat required BTU'S/hour numbers from Radiantec. Curious if anyone would be interested in going over them with me. Thanks Todd.
0
Comments
-
It is my understanding that Radiantec has threatened to sue members of this forum for speaking freely about their systems. If you are looking for candid feedback, you can send a PM to people by clicking on the username and clicking the "message" tab.
Those open systems are great for building your immune system"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
> @Zman said:
> It is my understanding that Radiantec has threatened to sue members of this forum for speaking freely about their systems.
Seriously?0 -
Radiantec is welcome to sue me if they are upset by my saying they are a POS company with no business in hydronics.
With that said, my primary business is radiant floors in pole barns and stick frame sheds. Assuming you'll be insulating properly, 1/2" tubing in 250ft loops on 12" centers is pretty standard. Forget everything Radiantec has told you and listen to some of the brains here that actually know what they're doing4 -
Groundup, Yes. The basic stuff is not the problem. Boiler size? pump size? etc..0
-
Sizing of EVERYTHING is determined by a scientific heat loss calculation. Ignore online calculators that only use square footage. They can be grossly inaccurate. SlantFin has a free app that you can download and is fairly accurate.kaama82 said:Groundup, Yes. The basic stuff is not the problem. Boiler size? pump size? etc..
And I second what's been said about RadiantWreck.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
What he said^^^^. In my neck of the woods (MN), a building that size usually ends up in the 60-100,000 BTU neighborhood depending on overhead door size and insulation value. As was mentioned above though, you'll need to do a heat loss analysis to properly size anything. I did just do a 40x88x16 a couple weeks ago with R32 walls and R50 ceiling along with only two 12x12 overheads and it came out to 71,000 at a design temp of -20F. I installed an HTP UFT-100W in that one with the tubing split into two 7 loop manifolds pumped with a single Grundfos 26-99.0
-
Ironman, I took a look at the Slant Fin app. Seems to be pretty in depth. I will continue to work with it. ThanksIronman said:
Sizing of EVERYTHING is determined by a scientific heat loss calculation. Ignore online calculators that only use square footage. They can be grossly inaccurate. SlantFin has a free app that you can download and is fairly accurate.kaama82 said:Groundup, Yes. The basic stuff is not the problem. Boiler size? pump size? etc..
And I second what's been said about RadiantWreck.0 -
Ground up. Thanks. Sounds pretty similar to my building, and probably the same heating zone, considering I'm in southern Michigan.GroundUp said:What he said^^^^. In my neck of the woods (MN), a building that size usually ends up in the 60-100,000 BTU neighborhood depending on overhead door size and insulation value. As was mentioned above though, you'll need to do a heat loss analysis to properly size anything. I did just do a 40x88x16 a couple weeks ago with R32 walls and R50 ceiling along with only two 12x12 overheads and it came out to 71,000 at a design temp of -20F. I installed an HTP UFT-100W in that one with the tubing split into two 7 loop manifolds pumped with a single Grundfos 26-99.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements