should I shut off radiators in my attic
Comments
-
Going to need a lot more information than that. What type of system (steam or hot water)? Why do you want to shut them off? What do you think shutting them off will accomplish?0
-
old steam system 2 pipe my mom wants to shut off to save energy0
-
-
Don't do it. At least not until it gets warmer... what will happen (best case) is the just enough steam will get by the inlet valve and it will condense and get to the trap and freeze the trap. New trap. Worst case would be enough gets in there to pool in the bottom of the radiator -- it will -- and freeze. New radiator.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If it were me, and an unused space with no plumbing to worry about freezing, I would. I would wait until well after a heating cycle has ended (to let the condensate return), and then turn off the valve that's hopefully in the basement that leads up there.
The valve has to be operational of courseNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Optimist.ethicalpaul said:If it were me, and an unused space with no plumbing to worry about freezing, I would. I would wait until well after a heating cycle has ended (to let the condensate return), and then turn off the valve that's hopefully in the basement that leads up there.
The valve has to be operational of courseBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England3 -
LOL well surely there are SOME valves in this great nation that actually work!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
There are many opinions about this. Not sending heat to part of the house, to me doesn't save anything. Are all the interior walls and floors insulated? If not then all you have done is move the "cold" to another room (with no insulation and the load is presented to that room. So the reminder of the heating system just runs a little longer to satisfy.
0 -
Put a very small air vent on them (assuming it's single pipe steam) and then throw a blanket over each radiator. the small vent will slow the steam getting into the radiator and the blanket will all but stop convection. make sure the radiator input valve is open all the way.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
I like that solution, @BobC, but wouldn't an even slower vent be achieved by turning the vent upside-down?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Turning the vent upside down would let a lot less steam into thae radiator but I'd be concerned it might not let enough in to make sure condensate didn't freeze on a really cold night.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
OK, but with a lot less steam, there would be a lot less condensate
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
OP said it is a 2 pipe system.
If you want to leave these off for the long term future, I would disconnect the valve and trap. Remove both from the piping...could be difficult..... and then cap both pipes, assuming they drop straight down.
Tip the rad to drain any remaining water out.
Leave all parts for future use.
Then insulating the attic floor would save more.2 -
Good eye, @JUGHNE
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements