Is this Relief Valve install dangerous and illegal?

Is this install dangerous? any good ideas to make it legal? There's a big pipe under it. Many thanks.

Comments
-
-
It's dangerous in that the seat is susceptible to collecting debris and clogging. It needs to be turned upright. Unscrew the copper pipe and rotate the elbow and valve 3/4 of a turn clockwise to get the valve to stand straight up. Then do something else to get a discharge pipe back into the threads and pointed toward the ground terminating about 6" off the floor.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
I'm curious, what does the tag hanging on it say?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Steam boiler??? are you sure?
0 -
just seems awful low in the block for a steam boiler, like at the water line
0 -
-
I'd add trained and experienced. Plenty of book smart professionals that have never been in front off actual equipment. Hands on experience is worth at least as much as "training" Although not an either or.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Regardless,
I believe the orientation for both hot water and steam boiler pressure relief valves is the same, no? The stem must be vertical?
@pecmsg and @hot rod_7 It sure would be nice if there was a reliable way to find "Qualified experienced professionals" for residential work................. Aside from word of mouth which is highly unreliable.
Highest vs lowest bidder doesn't work either.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
-
Apparently looking at pictures is just as hard as reading.SlamDunk said:0 -
C'mon, no need to beat a person up who is looking for help. I know I have paid good money to smooth talking contractors and ended up with a sub par craftsmanship.
I work with geniuses who can't turn a wrench or install a hook to hang a picture. But, literally, they are geniuses!0 -
I don't think anyone here was beating up the OP?SlamDunk said:C'mon, no need to beat a person up who is looking for help. I know I have paid good money to smooth talking contractors and ended up with a sub par craftsmanship.
I work with geniuses who can't turn a wrench or install a hook to hang a picture. But, literally, they are geniuses!
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
"Apparently looking at pictures is just as hard as reading."
"It's a steam boiler that was installed by a "professional"."
Being snarky isn't being helpful.
0 -
All of that was directed towards the contractor the OP hired which is all carried over from another thread.SlamDunk said:"Apparently looking at pictures is just as hard as reading."
"It's a steam boiler that was installed by a "professional"."
Being snarky isn't being helpful.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Glad I read this. Looks like mine is also mounted 270 degrees off of where it ought to be as well (too far 90 degrees clockwise, so keep on spinning I assume?) Mine is, however, mounted with a T and close nipple fortunately. Thanks for the info!Leon82 said:As mentioned in the other thread it should be upright.
A tee with another close nipple and a plug would provide a vertical prv and a skim port.0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements