Steam Systems under big mouth vent
Thanks in advance.
Comments
-
You can get it here: https://www.amazon.com/Barnes-Jones-Big-Mouth-Vent/dp/B01F26P13C/ref=sr_1_1?ie=UTF8&qid=1542309900&sr=8-1&keywords=barnes+and+jones+big+mouth or by calling Barnes & Jones and ordering directly.
I've installed several around my town, and so far there's been no complaints, only praise. They spit a tiny amount of steam while closing, but then seal perfectly tight. They have an o-ring seal inside to ensure this.0 -
0
-
The only thing they don't do that Gortons do is close against water -- so so long as they are mounted high enough to never see water (28 inches above the water line for each psi of boiler pressure), they're really good.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Yep. Learned that one the hard way with a faulty water feeder... Upside, I got a free shower out of it..Jamie Hall said:The only thing they don't do that Gortons do is close against water -- so so long as they are mounted high enough to never see water (28 inches above the water line for each psi of boiler pressure), they're really good.
0 -
-
Good reason to have 2nd pressuretrol as a interlock wired ahead of the feeder. If it overfills and it's set to 1.5psi then as long as the gorton is over 3ft above the pressuretrol it will shut down the feeder. Assuming you re using a vapor stat set lower.0
-
Hi gang— I keep reading about this height warning, but doesn’t the equalizer keep the column from rising on the return or am I horribly misunderstanding? Thanks!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
The pressure in the boiler-(even ounces) will raise the water in the wet returns 1.75 inches per ounce of pressure.
If you connect a hose to the boiler drain, and mount the open end high, and fire the boiler, you can see the elevated level by moving the open end downwards until water come out of the hose. Using a hose made up of clear tubing, it is even easier to see the level changing. The difference between the at rest boiler level, and the firing level in the tube in inches divided by 1.75 equals the pressure in ounces.—NBC3 -
Thanks NBC!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el-1 -
So why should I shell out for a 0-3 PSI gauge, when I could just make my own out of a piece of clear hose, and probably would be more accurate as well?nicholas bonham-carter said:The difference between the at rest boiler level, and the firing level in the tube in inches divided by 1.75 equals the pressure in ounces.—NBC
0 -
Because a 0 - 3 gauge won't spew boiling water everywhere should the Pressuretrol fail.Shalom said:
So why should I shell out for a 0-3 PSI gauge, when I could just make my own out of a piece of clear hose, and probably would be more accurate as well?nicholas bonham-carter said:The difference between the at rest boiler level, and the firing level in the tube in inches divided by 1.75 equals the pressure in ounces.—NBC
4 -
Ah, good point...0
-
Or you do it so the "tube" is closed up with a long sight glass set up. This is for pressure control, but for just "seeing" pressure you can ditch all the controls.
https://www.gwgillplumbingandheating.com/webapp/p/365/wilkinson-steam-boiler-replacement
Or just buy a gauge.1 -
You can also make a U tube that will shut off using pieces of cork at the top as a valve.
The Dwyer Slacktube does this.
Personally.......I'll stick to using Magnehelics for continuous measurement.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements