Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Worth it to replace CycleGard with SafGard?

Options
If this was a new installation, there's no question. But the existing CycleGard is functional and the (new to me) boiler itself is about 15 years old.
I love to hate on the thing, but is it really worth it from a ROI (financial, comfort, or otherwise) to switch now?
Thanks!
Patrick

Comments

  • Dave0176
    Dave0176 Member Posts: 1,177
    Options
    To me it’s well worth it, the cycle guard shuts the burner down for no reason other then to do a water level check. Then you lose the steam and have heat it up to steam all over again. To me it wastes money.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
    Ironmankcopp
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Options
    Not only does it lose steam, but it also allows air back into the system, which must be pushed out during the next cycle.
    If you don’t change it over at least measure the backpressure of your main venting, and enlarge as necessary.—NBC
    Ironman
  • Maine Vent
    Maine Vent Member Posts: 130
    Options
    Just replaced mine with safguard. Boiler runs and builds steam much quicker. I love the thing.
    Weil McLean SGO4, Riello Gas Burner
    404 sq ft EDR
    Old Burnham V8 Removal