Furnace Roof Vent Ice Dam and Resuilting Roof Leak - HELP!!!
HVAC_Rookie
Member Posts: 4
in Gas Heating
Hello folks - I'm really hoping someone can help me with this problem I've been trying to solve since last winter. As you can see I from the pictures I had a vertical ice damn being formed by the furnace roof exhaust vent. First I thought it was a roof problem but the roofer of the recently installed roof rightfully pointed out that there is no water leaking even after the heaviest rain. And then we saw theses vertical ice dams. Problem seems to be that none of the HVAC people I've spoken to seem to know how to address this. Two claim its a roof problem, while the last one side I should saw off the exhaust vent so that it is vertical pointing upwards which he feels means there will be nothing dripping out of it and thus no ice dam accumulation... ANY THOUGHTS PLEASE??
0
Comments
-
What model equipment is that venting.
Straight up is a good idea provided the manufacture approves."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Zman thanks for the comment.. it is a Comfortmaker furnace - can't seem to find anything that looks like a model name or number.0
-
I would cut it off and go straight up, just like in the manual. https://www.utcccs-cdn.com/hvac/docs/1011/Public/0C/44001201003_ICP_5970.pdf
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein2 -
The exhaust should go straight up, keep elbow on the intake. They should be a minimum of 18" apart.0
-
Go straight up. If you are concerned about the possibility of rain getting into the pipe -- which is a very minor problem and one I wouldn't worry about (the top cap on chimneys for fireplaces which you often see is there to keep the birds out, not the rain) -- you can put a lid over the top opening -- a flattish cone (tip up!) about twice the diameter of the pipe and set the diameter of the pipe above the top of the pipe. If that makes any sense.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Looks to me like it's an ice stalactite. Formed either by dripping water or cold steam vapor condensing on roof.
Just curious, have you ever seen it grow so tall it meets the pipe?
If I didn't have the installation manual I might have installed a Tee fitting on the vertical pipe ( as they like to do in England)0 -
-
Guys thanks very much for all of the great comments. I took the advice and had the vent cut so that it goes straight up. However as you can see now there is ice somehow accumulating along the based of the vent/flashing. Any ideas on what can now be causing this?? Could the cap somehow be causing the problem??
Thanks in advance for any help!
0 -
It looks like they put a cap on it, I am pretty sure that isn't necessary and probably causing the issue.1
-
My two cents. If the new roof is properly installed and the two pipes properly installed with appropriate materials at the base; the ice should not matter. I would guess it is possible for melt and remelt could affect the roofing. But it should not cause damage.
I have a question: should the exhaust pipe be below the intake? Or does it matter. It would seem to me that in the new configuration the intake would inhale some of the exhaust.0 -
-
-
It's a problem, because the moisture in the flue gases (steam) hits the cold cap, condenses, and then drips down and freezes on your roof. Without a cap any condensation will flow back down the vent pipe and be dealt with thru the condensate drain at the bottom.HVAC_Rookie said:Guys so is the cap a problem because air going up is being forced back down to the roof and then freezing?
Thanks.0 -
Don't forget that that condensate is VERY CORROSIVE. Not something you want running down your roof, gutters, siding....0
-
-
-
Yup, blow straight up. There's a drain in the furnace if a little bit of rain gets in it. I see these elbowed over all the time. Like DZoro said, you don't want that stuff on your roof. I have a picture somewhere of one that blew on an adjoining chimney and the mortar is totally gone between the bricks.1
-
A permanent solution would be to not use your boiler in the winter time.
Ya, saw off the coupling at the pipe and glue a new coupling on the exhaust pipe. You could also glue a vertical facing pvc vane in the top of the coupling that would help with down drafting.
In case you're wondering, the exhaust vent is the one with the ice stalagmite.0 -
NeverDone said:Also it might be a good idea to put a reducer on the end of the pipe to drop 1 size, for example 1-1/2 -to- 1-1/4. Lennox calls this an 'accelerator' and it increases velocity to help blow the exhaust further away from the termination point to prevent exhaust from being drawn into the intake.
Do not do this without consulting the installation manual for the exact make and model of your furnace. Don't do it if it is not in the manual.
0 -
The flashing should seal any water from getting inside, is it in good condition? The rubber seal tight and flexible?
In snow country we would run those vents up near the ridge, to prevent damming, which often lead to shearing off of the pipes. Assuming the vent tables and fittings
fell within the max. Length tablesBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Sorry but this notion of poor roof insulation is wrong or misguided. Unless the attic is finished, you don't want any "roof insulation". You want the attic to be cold, so it would be expected that the roof would be cold and water on it would freeze.
And even if the attic is finished, the rooftop itself should be cold due to the insulation between the conditioned space and the outdoors.
You want a lot of snow on your roof.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
Well it WAS a 4 year old thread LOL
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements