Out here in Colorado where the steam is alittle cooler =D

Built in 1927 this building has 10 apartments. 4 on the 3rd floor, 4 on the 2nd floor and 2 in the basement.
Old boiler's tags read: S 2900. 5 K. New boiler is a 64-08 sized to the EDR and elevation.
This is my first 4inch header, fun stuff. the book called for 2x 2 1/2 risers but i calculated the exiting velocity to be 25-27fps. Upping the size to 3inch risers slowed that down to 16-17fps.




Here's James before we started smashing it to pieces.




Got the new boiler down and as some of you saw, we had a leaky end section.
Peerless has a 1 year parts and labor warranty apparently, so all of the extra labor and headaches will be compensated.
putting the boiler together the second time around was much easier using a gantry, never again will i ignore that thing calling my name.



We had King Squirrely to keep us company on our breaks.. this guy had 2 slices of pizza, a full taco shell and an apple in just one day! and thats only what i spotted.





Here are the end results! When the owner of the building came down and said "It is beautiful," it made all of the hardwork, tired bodies and stress absolutely worth it! Gotta love steam.
























Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,859
    Even labelled the wires! Nice job!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    SeanBeans
  • gerry gill
    gerry gill Member Posts: 3,078
    Should work good.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

    SeanBeans
  • Steamhead
    Steamhead Member Posts: 17,385
    I think that was an Ideal Water Tube boiler- one of the better ones available at that time.

    Boiler looks great. How about the rest of the system?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    SeanBeans
  • SeanBeans
    SeanBeans Member Posts: 520
    I’m working on calculating how many main vents they need. I have roughly 75’ 3.5”main and 25’ 2” dry return
  • Ironman
    Ironman Member Posts: 7,550
    Nice job Mr. Beans.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    SeanBeans
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,479
    Those old American Radiator boilers were tanks. We just had one let go in a school installed in 1938. Unfortunately we were underbid on the replacement.

    The new ones won't last 80 years
  • SeanBeans
    SeanBeans Member Posts: 520
    edited October 2018
    The building was also connected to a “central Freon system” described by the owner. Each apartment had a small cooler box recessed in the wall outside of their door, the grocer would come by and put their food in the cooler until the resident got home from work. And below the cooler box was a small box for the mans work boots.
  • Dave0176
    Dave0176 Member Posts: 1,178
    Nice header Mr Beans........
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
    SeanBeans