Wiring a Taco valve control box 404-4-exp, question one.
cnmdesign
cnmdesign Member Posts: 103
edited September 2018 in Radiant Heating
On a Taco 404-4-Exp zone valve control box, can I wire the 120v fan from my air/water HX to the 120v pump end switch on the left. If so, can someone show me a rough schematic. I want the fan on the HX to come on when the zone calls for heat. I use a single Alpha2 ,
https://www.ecomfort.com/manuals/burnham-5aeb718d763ba5a773a0a0f937640ec1.pdf
The fan spects:
Axial fan Motor
YWF4E-250B-2T
120v 60Hz 0.58A 70w 1580 r/min
120v 60Hz 0.32A 40W 1310 r/min
7uf/450V CLF
https://chillxchillers.com/air-to-water-heat-exchangers/zephaire-2-speed-air-to-water-heat-exchangers?sku=ZAU0120500ZA-2&gclid=EAIaIQobChMIvs-b_PPJ3AIVA5ppCh2CuQ_KEAkYASABEgIrNvD_BwE
Combat Veteran owned, Final Salute LLC on FaceBook & Twitter.
www.afinalsalute.com
  • Ironman
    Ironman Member Posts: 7,903
    A blower would draw more amperage than the control allows for those contacts. You'd need to use an isolation relay.
    Bob Boan
    cnmdesign
  • Zman
    Zman Member Posts: 7,609
    You might consider controlling the fan with an aquastat mounted on the pipe at the heater. That way the fan won't blow cold air waiting for the boiler to heat up.
    Albert Einstein
    cnmdesign
  • Ironman
    Nah, nothing that expensive.
    This is what you need:
    Bob Boan
  • cnmdesign
    The fan spects:
    Axial fan Motor
    YWF4E-250B-2T
    7uf/450V CLF
  • Ironman
    If the amp draw is less than 2 amps, you don't need the relay.
    Bob Boan
    cnmdesign
  • cnmdesign
    So according to the sticker on the fan, it's OK?
  • Ironman
    Yeah.
    Bob Boan
    cnmdesign
    HVACNUT Member Posts: 7,446
    Only .58 RLA on a 1580 RPM blower motor?
  • cnmdesign
    That's what it says.
  • cnmdesign
    Hot Rod, am I correct in assuming when wiring a Caleffi four wire Z-one zone valve to this control box it's 1Bk, 2Bk, 3R, 4R with no + or - using an Alpha2 pump?