Wiring a Taco valve control box 404-4-exp, question one.
cnmdesign
Member Posts: 103
On a Taco 404-4-Exp zone valve control box, can I wire the 120v fan from my air/water HX to the 120v pump end switch on the left. If so, can someone show me a rough schematic. I want the fan on the HX to come on when the zone calls for heat. I use a single Alpha2 ,
https://www.ecomfort.com/manuals/burnham-5aeb718d763ba5a773a0a0f937640ec1.pdf
The fan spects:
Axial fan Motor
YWF4E-250B-2T
120v 60Hz 0.58A 70w 1580 r/min
120v 60Hz 0.32A 40W 1310 r/min
7uf/450V CLF
https://chillxchillers.com/air-to-water-heat-exchangers/zephaire-2-speed-air-to-water-heat-exchangers?sku=ZAU0120500ZA-2&gclid=EAIaIQobChMIvs-b_PPJ3AIVA5ppCh2CuQ_KEAkYASABEgIrNvD_BwE
Thanks
https://www.ecomfort.com/manuals/burnham-5aeb718d763ba5a773a0a0f937640ec1.pdf
The fan spects:
Axial fan Motor
YWF4E-250B-2T
120v 60Hz 0.58A 70w 1580 r/min
120v 60Hz 0.32A 40W 1310 r/min
7uf/450V CLF
https://chillxchillers.com/air-to-water-heat-exchangers/zephaire-2-speed-air-to-water-heat-exchangers?sku=ZAU0120500ZA-2&gclid=EAIaIQobChMIvs-b_PPJ3AIVA5ppCh2CuQ_KEAkYASABEgIrNvD_BwE
Thanks
Combat Veteran owned, Final Salute LLC on FaceBook & Twitter.
www.afinalsalute.com
www.afinalsalute.com
0
Comments
-
-
-
Nah, nothing that expensive.
This is what you need:
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The fan spects:Ironman said:A blower would draw more amperage than the control allows for those contacts. You'd need to use an isolation relay.
Axial fan Motor
YWF4E-250B-2T
120v 60Hz 0.58A 70w 1580 r/min
120v 60Hz 0.32A 40W 1310 r/min
7uf/450V CLF
https://chillxchillers.com/air-to-water-heat-exchangers/zephaire-2-speed-air-to-water-heat-exchangers?sku=ZAU0120500ZA-2&gclid=EAIaIQobChMIvs-b_PPJ3AIVA5ppCh2CuQ_KEAkYASABEgIrNvD_BwECombat Veteran owned, Final Salute LLC on FaceBook & Twitter.
www.afinalsalute.com0 -
-
-
Only .58 RLA on a 1580 RPM blower motor?0
-
Hot Rod, am I correct in assuming when wiring a Caleffi four wire Z-one zone valve to this control box it's 1Bk, 2Bk, 3R, 4R with no + or - using an Alpha2 pump?
https://www.ecomfort.com/manuals/burnham-5aeb718d763ba5a773a0a0f937640ec1.pdfCombat Veteran owned, Final Salute LLC on FaceBook & Twitter.
www.afinalsalute.com0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements