Piping Around Obstructions

I saw this and started scratching my head. The boiler is immediately to the right (it's big, 32" waterline). The returns are wet, and are also clogged (which is the job here. Replace the wet returns).

But why the piping above the door and the vent? Unnecessary no? Or am I missing something?!


New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,986
    I have one of those, too, in one of the places I care for. I've never yet figured out what it's supposed to do...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Danny Scully
    Danny Scully Member Posts: 1,433
    Hmmm...I’ve seen a diagram exactly the same but for above waterline piping, such as a steam main or runout...those dead mean always keep us on our toes.
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,521
    Deadmen did not do this one @Danny Scully . It was done about 20 years ago. I am thinking they saw the same diagram you saw for piping steam around obstructions and didn't realize they were piping condensate?
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Fred
    Fred Member Posts: 8,542

    Deadmen did not do this one @Danny Scully . It was done about 20 years ago. I am thinking they saw the same diagram you saw for piping steam around obstructions and didn't realize they were piping condensate?

    That's what it looks like to me.
  • Pumpguy
    Pumpguy Member Posts: 676
    edited April 2018
    This is referred to, oddly enough, as a DOOR LOOP, and is the piping arrangement used when piping around obstructions.

    Water, or as we call it condensate, being heavy, falls to the bottom run to flow by gravity. Air, being lighter, flows through the upper part of the door loop.

    The attached file explains in greater detail.

    This is also illustrated and explained on Page 95 of The Lost Art of Steam Heating.
    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
  • Fred
    Fred Member Posts: 8,542
    Pumpguy said:

    This is referred to, oddly enough, as a DOOR LOOP, and is the piping arrangement used when piping around obstructions.

    Water, or as we call it condensate, being heavy, falls to the bottom run to flow by gravity. Air, being lighter, flows through the upper part of the door loop.

    The attached file explains in greater detail.

    It would seem that a vent, either on the end of the Main or anywhere on the return, before it drops below the Boiler water level would take care of any air issues.
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,521
    So, being only condensate, what would happen if I remove the upper door loop? The condensate would still flow, right?
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Pumpguy
    Pumpguy Member Posts: 676
    Maybe so, unless maybe it was a 2 pipe vacuum return system?

    I don't do steam piping, but when I see an arrangement like that, I immediately recognize it as a door loop.
    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,347

    President
    HeatingHelp.com

  • New England SteamWorks
    New England SteamWorks Member Posts: 1,521
    Exactly @Erin Holohan Haskell . Except that's for piping steam around obstructions. In this case, we are just piping condensate...
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Pumpguy
    Pumpguy Member Posts: 676
    The file I posted is for either steam or condensate flow. Only difference is the size and location of the pipes.
    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,600
    @New England SteamWorks That is used to vent the air in the piping. If you did not have that, the air would not vent and flow would stop. Its a good thing to keep
    Ray Wohlfarth
    Boiler Lessons
  • Steamhead
    Steamhead Member Posts: 17,177
    But, if the boiler's water line is 32" off the floor in the pic, which makes this a wet return, the whole pipe is full of water so the loop over the door isn't needed.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    New England SteamWorksCanucker
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,521
    Steamhead said:

    But, if the boiler's water line is 32" off the floor in the pic, which makes this a wet return, the whole pipe is full of water so the loop over the door isn't needed.

    Right? That's what I think. Waste of time, energy, & material to put it back.

    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    This is a wet return so that door loop is pointless. The diagram @Pumpguy posted is for a steam line and a DRY return. Both of which would be require to be piped like this. But being that this is a WET return, I don’t see how the loop above the door is needed.
    Never stop learning.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Looks like if you removed the pipe over the you would just have a second Hartford Loop. I wonder if it was put in initially because the returns were clogged, and they came up with this 'idea' because they saw it somewhere else.

    There was an error rendering this rich post.

  • Double D
    Double D Member Posts: 447
    I have a couple of Hoffman books that show that arrangement for looping a dry return around a door. I have seen it done on 1 pipe wet returns. The only difference is the drop went below the floor for wheelchair access from an elevator.
  • ratio
    ratio Member Posts: 3,742
    It might just be there to allow the wet return to prime. I have more experience with condensate drains, but a double trap will stop water flow without a doubt.
  • the_donut
    the_donut Member Posts: 374
    Shouldn’t be a problem unless the wet return is emptied and line gets airlocked somehow.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,998
    edited April 2018
    @New England SteamWorks Is it possible that at one time the original boiler was in a pit that has since been filled and the water line is now raised making the loop not needed?
  • Fred
    Fred Member Posts: 8,542
    edited April 2018
    32" is probably a couples into those verticals. It is all water below. That loop over the door can not serve any purpose and that vent isn't venting anything. That is one vent that will never fail.
    New England SteamWorks
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,578
    If it's a gravity wet return, the upper pipe isn't necessary. But if the end of the condensate return goes to a vented receiver on a boiler-feed pump, the upper pipe would be there to allow system air to pass to the vented receiver.​
    Retired and loving it.
  • JUGHNE
    JUGHNE Member Posts: 11,182
    I wonder if this was installed by a hot water heat guy who studied some steam piping and saw this setup in a book.

    But he still had his HWH hat on most of the time and knew that any high point in piping could trap troublesome air in water lines and an auto vent would take care of it.

    So he should get credit for studying piping diagrams and his workmanship looks good IMO.
    Also get points as the dead man who sparked this post, thereby exposing more of us to the "over and under" steam piping. :)
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,521

    If it's a gravity wet return, the upper pipe isn't necessary. But if the end of the condensate return goes to a vented receiver on a boiler-feed pump, the upper pipe would be there to allow system air to pass to the vented receiver.​

    No vented receiver, no boiler feed pump. And there was never a pit.

    I think @JUGHNE pretty much has it. It's not original Deadmen piping per owner. I think someone studied the "Steam Piping Past Obstructions" page and mis-applied.

    Anyway, we'll all find out, because when I re-do the wet returns the door loop is gone...