New heat pump with 5/16" liquid line?
Comments
-
About 25 years ago, I had a compressor fail within the warranty time frame. I was denied the warranty because I used a 7/8" suction line on 4 ton system that should have had a an 1 1/8" suction line because of its extended length. That was a hard lesson to learn. I never give them an opportunity to deny, anymore.Steve Minnich1
-
Was this 5/16 on an old R-22 system?
Ruud/Rheem did the 5/16 years ago.
A new 410A HP?0 -
Thanks for the response. It is a Trane 1987 2 ton, r22 air handler, and we would be installing an 410a hp and air handler0
-
Should be ok up to 3 tons. Add as much 3/8th as you can at the unit. I have never had a warranty job denied.0
-
Is the remaining oil from the R-22 system a concern?
Or how do you deal with it?
Or is it as much of the issue that was thought when 410A became popular?0 -
Rheem is fine with it in long lengths up to 3 on, above better be pretty short.
Otherwise I'd check with tech support on the brand you want to use. I called 1 brand once and was told absolutely nothing less than 3/8". Dead comps usually don't go back so yes, warranty won't be denied but it will cost someone!
Old lines blow out with nitro and unless you had a burnout, should be OK. Of course if easy to change I'd much rather see shiny new copper. POE oil is a GOOD cleaner removing any crud built up on the inside of the old lines.0 -
On a walk in cooler I had both TXV plugged screens twice after 134A and new oil.
So for a heat pump with possibly TXV inside and out, also reversing valve, where is the best place for the bi-flow filter drier.....would one for each end be a consideration?0 -
5/16 will be fine for 2 tons. Blast it with nitrogen first0
-
-
Flushes cause more damage and are not advised. just blow out the line set. No issues with a mixture of POE & MO.
Remember the POE oil is a cleaning agent, We recommend a suction filter in use for several days to trap any and all crap that will come back to the compressor. Remove it after a few days.3 -
Hey guys, I have a similar situation as the original poster here. Replacing a 2.5 ton R22 Trane HeatPump that has an existing 5/16" liquid line. Replacing the unit with a Goodman GSZ140301 (2.5 ton HeatPump) and a Goodman ARUF37C14 a/h. The existing lineset runs through interior finished space of the house and the HO doesn't want a new lineset running up the exterior wall. In this case, the a/h is in the attic with a total 50' lineset run with approx 18' of that being a vertical lift. Goodman's technical publication 107 makes a 5/16" for a/c only applications, but, makes no mention of heatpump applications. Thought I'd reach out to you for your thoughts. Do you think I can get away with using the existing lineset? Thanks in advance.0
-
and there's your answer.Cayman said:Hey guys, I have a similar situation as the original poster here. Replacing a 2.5 ton R22 Trane HeatPump that has an existing 5/16" liquid line. Replacing the unit with a Goodman GSZ140301 (2.5 ton HeatPump) and a Goodman ARUF37C14 a/h. The existing lineset runs through interior finished space of the house and the HO doesn't want a new lineset running up the exterior wall. In this case, the a/h is in the attic with a total 50' lineset run with approx 18' of that being a vertical lift. Goodman's technical publication 107 makes a 5/16" for a/c only applications, but, makes no mention of heatpump applications. Thought I'd reach out to you for your thoughts. Do you think I can get away with using the existing lineset? Thanks in advance.
Contact Goodman tech support before taking on the job.0 -
3/8 is good for 3 1/2 tons at 25' so I don't see 5/16 being an issue on 2 1/2 at 25'
Heat pump or ac makes no difference it's the same amount of liquid flowing only the direction changes. The weight of R-22 and R-410 in a liquid phase is virtually the same0 -
In the lineset sizing paperworks I've read, the liquid line size was dictated by refrigerant velocity as well as pressure drop & often gave a range of sizes. That said, I can't recall seeing any R-410A A/C system that permitted anything smaller than 3/8". It's possible that it'd work, but I'm quite sure that Goodman, or any other mfgr, will not honor a warranty that doesn't meet their minimum spec.
If it were me, I'd walk away. I don't know how reasonable the homeowner is, but I know how those kind of things fall out for me.
1 -
we did that on a condo 3 years ago, no issues yet. 2 ton0
-
-
I just came across a doc about this today, attached. It shows a 5/16" liquid line as being acceptable for up to 31/2 ton with 120' of lift to the condenser.
And a maximum equivalent length of 90' for a 1/2" suction line on a 11/2 ton unit!!
0 -
That's for Trane the OP is installing Goodman!ratio said:I just came across a doc about this today, attached. It shows a 5/16" liquid line as being acceptable for up to 31/2 ton with 120' of lift to the condenser.
And a maximum equivalent length of 90' for a 1/2" suction line on a 11/2 ton unit!!
0 -
Sure, but it's the same physics. Should work fine (although that's no guarantee the factory will honor their warranty [if necessary]).
TBH, I posted it for the next person looking for info on using a 5/16 liquid line.
And to marvel about a 1/2 suction line. I don't do much refrigeration, that sounds way small to me!
0 -
That chart shows the extra charge if a 5/16th is the liquid line. It also states the new equipment will not have a AHRI # or meet the DOE energy requirements.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements