1 1/2" threads won't seal
Comments
-
Only the obvious ones, I'm afraid. Is the reducing bushing really round? Are the threads cut properly? Does it bottom out before the threads seal (threads again -- cut far enough into the fitting). Ditto on the male threads on the tank fitting.
And one less obvious -- are both NPT? I've hit that one, like an idiot...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
It is possible to over-tightens fitting and either pull the thread or expand, maybe crack the fitting. Teflon and a large wrench can tempt you to overdo it
Is the nipple round, no shipping damage?
If you can get both male and female completely clean, Loctite will seal most anything. The super glue of fittings.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
-
How does one thread a reducing bushing onto a male nipple?0
-
If the connection is permanent, I would use J-B Weld or lock-n-seal (loctite) which can be undone. Even J-B Weld can be undone if heated hot enough.
I think he means coupling, but I have been wrong before.0 -
My question as well.JUGHNE said:How does one thread a reducing bushing onto a male nipple?
Another question is against what pressure do you want to seal?
Something that worked for me sometimes is to dope the male thread and grease the female thread. Also I never use extreme force on anything threaded. I don't understand why short (stubby) wrenches for larger sizes are so unusual.
0 -
-
Making sure you use a small wrench with a pipe on the handle for maximum egging.HomerJSmith said:'hot rod' says, "It is possible to over-tightens fitting..."
Myself, I always tighten a fitting until it busts and then give it one more turn.2 -
Permabond LH050/150 or Loctite 565/567 have gotten me out of more trouble than I care to admit. I all but gave up on tape and dope (never bare tape, just don't do it) on 2" and less many years ago and can literally count on one hand the amount of leaks I've had since- this is a fulltime job. Of those few leakers, all of which were fixed with more tightening or some heat. Used to use X-Pando for the real stubborn ones back in the day, but that will never come apart again if it doesn't fix it. If the nipple or fitting is egged enough to kill sealing, it won't thread on either IMO. Just ordered another case of Permabond on Thursday, I love it0
-
Two grunts on anything 1" or smaller, 3 grunts for larger sizes up to 3"HomerJSmith said:'hot rod' says, "It is possible to over-tightens fitting..."
Myself, I always tighten a fitting until it busts and then give it one more turn.
Up to 1-1/4" I use this 14" Reed aluminum offset style pipe wrench for assembly. I have worn out 3 or 4 of theses over the years. Sometimes a cheater for disassembling
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream3 -
On stuborn connections I like to use ball or string wicking first, 3 / 4 wraps of quality Teflon, and then a coating of pipe joint compound........0
-
This.hot rod said:Up to 1-1/4" I use this 14" Reed aluminum offset style pipe wrench for assembly. I have worn out 3 or 4 of theses over the years. Sometimes a cheater for disassembling
Around here, I noticed that the gas company guys (& gals!) use an 18" offset wench for pretty much everything, so I picked one up. It seems to be able to get in to more places that a regular wench. I'm not completely sure, but there might not be a case where only a standard wench will work.
And Aluminum all the way!
0 -
A brass coupling would have a little stretch to it and perhaps mate with the nipple a little better especially if the nipple is SS.0
-
I would have to look it up again, but i am fairly sure it is against the plumbing code to put pipe dope on the inside of a female fitting. As you tighten the pipe in, it pushes the pipe dope into the inside of the fitting, which as you all know is not good.EBEBRATT-Ed said:Try regular Teflon tape and wrap it tight. Put some pipe dope on the male threads and dope the female threads as well. Crank it up tight.
Use whatever dope you have , I like Rectorseal True Blue. On the can it says to dope the inside threads on anything larger than 1 1/4"
I can just hear what Icesailor would be saying right know if he heard someone saying to dope the female threads. It would be in all capitol letters!
My method is like some others here. I use Megalock dope on the threads, followed by at least four wraps of Monster tape, and depending on the thread, more dope on the outside.
I haven't had to deal with many straight threads yet, so have not had to use wicking, nor have I ever even seen the stuff. I hope to continue that trend.
Rick0 -
I was taught to dope the female connector if it was larger than
1-1/2", But I do 1-1/4" too. You only have to do, sparingly, a couple of threads. I gave up using Rectumseal for the newer sealants.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements