Regulator position
kcopp
Member Posts: 4,700
in Gas Heating
Anyone ever seen an installation on a LP gas regulator in this position? I thought it odd. Would/ could it cause fluctuations in the gas pressure?
if you are having fluctuations in pressure, the valve could be going bad, there should be another by the unit"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
That might be the entire LP reg set up.
It looks like a combo.....2 regs.
Lbs to Lbs on the left then the right part of it is LBs to inches.
Might use this if tank is close to load or load not so big.0 -
The upside down regulator shouldn't be a problem, although you may want to check the mfgr's paperworks in case they disallow it. I've used many regulators in this position, it's only an issue if there's no clearance to get in to adjust it. In fact, turning the regulator upside down is the easiest fix when the plumber's helper uses an indoor regulator outside with the vent pointed up.
Just a thought.
3 yr old boiler. no issues....until they ran out of gas in January. Now they get a sporadic resonation at times. Combustion numbers look ok. Monometer stayed steady (9.5" wc) under a massive load... (boiler, furnace, oven and fireplace)0 -
Not much experience with LP, but it sure sounds like it sucked something up into the system. If something is resonating at audible frequencies in the gas supply, you might not see it on a manometer.
Have you caught it doing it? It probably only happens at a specific flow, it may go away if the flow increases.
I have not seen it. I have a video from the owner.... no rhyme or reason...0
Ask the supplier to replace the regulator. And never hurts to put a little methanol in the tank at the same time.. what was your lockup pressure and static pressure on the regulator? I like 12.5 to 13 static and flow no lower than 10"... I generally aim for 10.5"
The Rego book I have suggests the vent port should point down. But we commonly see vent ports horizontal. Under cover it may not be as critical.Bob "hot rod" Rohr
Living the hydronic dream0
- 128 Chimneys & Flues
