Lennox Gas Furnace Dead
This morning there was no heat. Put new batteries in the thermostat just in case, played around with that. The blower fan will turn on if the thermostat is turned to manual on but not the burner.
There is 120v power going to the furnace and I assume there is gas because the separate natural has water heater is working fine. I tested 26-27 volts at the transformer in the furnace. I hear a click in the tstat when it calls for heat but there is zero activity at the furnace. No clicking, igniter, gas sounds, etc. I checked and re-seated wiring connectors inside the unit with no change. Any ideas? Thank you
Comments
-
-
-
Thanks guys. To check voltage I multi meter the PV terminal and which other terminal?SuperTech said:I would bet it's the ignition module. I would check for voltage at the PV terminal. If it has 24 volts I would replace it with a Honeywell S8610U.
What is all that blue crap stuck inside the blower compartment?
That blue crap is filter material. Looks like a jury rig to me but it seems to have brackets to hold it in place. Are these units supposed to take a regular 1" filter?
The black wire looks like it has always been dangling there. As far as the green wire with yellow stripes connected to terminal 5 24v (GND), is that the correct terminal? It may have gotten switched by accident. thank you0 -
Blue filter media.....the infamous Lennox "Hammock" filter system. Wasn't too bad of a system. Lot of area. Usually only the furnace cut out side got dirty.......if not changed then you would use the rest of the area.
Real old school......you guys must be young.
Today is considered a PIA to change.1 -
-
check the relay"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
-
Do you guys know where to test for power at the module? I am assuming the 24v (GND) and TH-W?0
-
" It may have gotten switched by accident. thank you, "How would that happen?m Were you goofin with the wires? Do you have a humidifier on the system? If yes check the condensate pump.0
-
I was re-seating the connectors to make sure they had a good connection. It should be on the 24v GND, the other terminal is not used in my application. No humidifier.0
-
Lennox always had wired stuff. I remember the hammock air filters. My boss at the oil company 40nyears ago loved Lennox.
@JUGHNE , how about there oil burners with the belt drive oil pump? anyone remember those??1 -
-
This may have come prewired for a vent damper option.
Some had a Molex connector on the top with a jumper plug inserted if no motorized damper was installed. More wiring to troubleshoot.
The most troublesome part of these I have seen is the spark, flame sensor, pilot assembly. Need cleaning often.
You should hear the tic-tic of the spark unless the tip is burned too far back to reach ground.
Yes, check the cond pump, it has a safety overflow switch which could cut the 24vac to the system. Often not used.
Look, an actual real metal push button on the door switch!
Ed, I probably have 2 of those belts in stock......why??
(IIRC, I think they drove the fan on the burner. )-1 -
Try by passing the limit. Two brown wires on the black control with numbers on it next to the spark igniter. The other black wires are are 110v it's the only limit I see. there may be one in the blower compartment need a wiring diagram to be sure. If it starts you need to call someone to replace it. You need 24v between 5 and 7 on the sparker. If you have that and nothing happens you need a new one of those.1
-
You have the Honeywell S8610U Universal replacement control. This means the original module has been replaced at least once. The gray plastic is the older Universal replacement there have been two others since that one which is the S8610U-3009 Black plastic. I assume there is no vent damper on this furnace so the dummy plug on the module should be in place. If you get a new S8610U - 3009 it will come without a dummy plug DO NOT PLUG ONE IN TO THE NEW CONTROL AS IT WILL DAMAGE THE CONTROL. The new control will not have two terminals on the valve to read microamps direct.
With the thermostat calling you should have 24 volts at THW and 24 gnd. If you do then there should be 24 volts at PV to gnd (MV/PV) and the pilot should be energized and gas should flow to the pilot. At the same time the spark should start and the pliot should light and prove microamps sufficient to cause the MV valve to be energized 24 volts from MV to gnd (MV/PV). The miroamps should be between 2 to 10 - 3 to 5 is normal. Then the spark should shut off and the system should be running as far as gas flow. A short time later the system blower should come on. Make sure you have a good ground connection from GND on the module to ground on the furnace if not run a new wire.-1 -
@jughne, I don't know. When I saw Lennox posted It just popped into my head. The one I am thinking of had a big round dial with a set screw to adjust the air and the oil pump was belt drive with a little skinny belt. Had some sort of idler pulley on the belt that drove the oil pump used to break off some times. very weird0
-
Ed, I meant why do I still have those belts when I haven't seen an oil burner for 30 years.0
-
Thanks for all your help guys, I really appreciate it! It turned out to be several issues. The thermostat was bad for one and was working intermittently making it difficult to troubleshoot. Also the lower door switch. When the tstat was calling for heat, I was not getting any power to the ignition module. I went to take the lower door off, and as I started to remove it, suddenly I had power. I discovered that the door button/switch was not getting pushed all the way in. There is a piece of sheet metal on the inside of the door to push on the button. Over the years it seems that sheet metal has bent away from the button and didn't make adequate contact. I bent it toward the button and it makes good contact and fully depresses the switch. See pic below. The other issue was the connector on the 24v gnd connected to the module was cracked, I put a new connector on. So far so good. Thanks for all the great info
1 -
wow, my old house had that exact same furnace, hammock filter and all. Only difference is I still had all the original controls in it, no ignition module, and a standing pilot gas valve. Thing is a beast. I would start thinking about replacement though, it is well past its service life and the heat exchanger will start leaking at some point which is something you don't want. I replaced mine before I sold the house. Glad it is up and running now!-1
-
Delta, how can you tell when the heat exchanger is leaking? You start smelling fumes?delta T said:wow, my old house had that exact same furnace, hammock filter and all. Only difference is I still had all the original controls in it, no ignition module, and a standing pilot gas valve. Thing is a beast. I would start thinking about replacement though, it is well past its service life and the heat exchanger will start leaking at some point which is something you don't want. I replaced mine before I sold the house. Glad it is up and running now!
0 -
-
@jeffceo sorry missed this, you can do as Jughne said above, it is certainly not conclusive, but is a good inidicator of a problem. Really you need a high quality CO detector designed to detect down to 1 ppm of CO with a probe you can place in the supply plenum. Any competent HVAC contractor will have one. This will tell you if exhaust gases are getting into the plenum (this is the most likely indication of a crack in the heat exchanger).
Regardless of whether you get a new furnace or not, get some CO detectors for your house. period.0 -
I have this same unit. I need to know where the yellow wire from the 24v low voltage transformer goes? I think I miss wired it and blew out the low voltage transformer. I ordered a new transformer and waiting for it in the mail. In the mean time I was hoping to find out where to put it. When I miswired it I smelt an electrical odor and I ohm'd out the coil. nothing. I think I hooed it up to 120v instead of 24v. if anybody knows where to the yeallow wire goes, please let me know. Thanks,0
-
@philthyphil post a picture of your furnace on a new post. This furnace has many changed parts that yours may not have exactly.0
-
ok0
-
Why is there an orange wire capped off? What was/is it for?0
-
Probably electronic air cleaner or humidifier or other accessory that runs on a heat or a fan call.0
-
Mattmia, Thanks. One more question for this unit...from what I can see in the photo, the limit switch/fan control ground disappears behind the gas valve. Is it grounded to the valve or to the furnace metal? Does it even matter? I would have thought it would be grounded to one of the terminals on the control.0
-
Any ideas for where to connect a common wire on this unit? Thanks!0
-
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
It can be any problem(failure of any device) in the safety circuit. Since the ignition module is the last device before ignition and opening the gas valve. You need to determine if you have the 24Vac at the ignition module. If you do, the safety circuit is intact. If you don't hear the ticking and see the spark at the pilot assembly, suspect the ignition module failed. Jumping to conclusions doesn't cut it. You must verify.
I'll tell you what happens with these ignition modules for the 7th time. I only know because I have taken numerous ones apart. I like to know why things fail. What happens is that the relay in the module vibrates, opening and closing the points, and breaks the solder bond on the circuit board. That break is very obvious to the naked eye. Necessitating a replacement of the module. If you have 24Vac at the module that's probably the problem.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements