Velocity Boilerworks - Mega Stor II - Leaking New??
Greggor2
Member Posts: 4
Hi everyone, I am pulling my hair out...
Had a Velocity Boilerworks MS2-40 Megastor II installed and 11 days later, it started to leak... returned for a new one... second unit installed - worked perfect... for 11 more days... at which point... it sprung a leak.
Does anyone know anything about this company??
Serial numbers of the two units are 5 apart... defect in the production line?
Should have put in another Weil McClain!!
Had a Velocity Boilerworks MS2-40 Megastor II installed and 11 days later, it started to leak... returned for a new one... second unit installed - worked perfect... for 11 more days... at which point... it sprung a leak.
Does anyone know anything about this company??
Serial numbers of the two units are 5 apart... defect in the production line?
Should have put in another Weil McClain!!
0
Comments
-
Where is it leaking from?0
-
Good question. There is a plastic top and bottom that wrap over the outside metal jacket. It appears to be leaking from underneath the unit, as well as perking up over the top lip of the bottom plastic piece.
All joints, fittings, unions and TP valves are bone dry.0 -
Sounds like you need to get the rep involved. In any case, they're going to start denying your claims if you don't.0
-
It could be leaking from a weld and be a manufacturing defect on a production run.
You need to press the company tech people for an answer as they may not be forth coming with an answer, but they may be aware that it is a problem. It depends on the reputation of the company as to the course they take. Ask for a Rep to visit your install. Document everything with photos and get any opinions as to the cause in writing.
If you don't get any satisfaction, insist that the seller take the unit back and refund your money. Then buy one from another manufacturer. Don't expect them to pay the labor costs.0 -
Velocity is/was Crown Boiler Co. I remember looking at this brand when I was considering a stainless steel indirect. They claim to use 444 grade stainless.
Five units apart on the assembly line does sound suspect. Hope your installer followed the manual so there's no question about the installation.
Just curious, how long did the WM indirect last?0 -
This problem has only gotten more strange.
Again, all sweat joints, fittings and unions are bone dry.
After second unit leaked, unions were disconnected, tank drained, and then reconnected, filled, and then didn’t leak for 2-3 days... then it started leaking a little bit for a few days (it’s now sitting in a pan for safety), then it just opened up and leaked like crazy after about a week.
What the heck would cause a leak to vary in intensity. Thermal expansion I have to assume?
Have spoken with rep and he thinks my water quality is bad....? Almost impossible for me to imagine however that bad water (which we have been drinking for 3 years) is to blame...?
Working with vendor and rep... they are demanding water sample... but... again... seriously?0 -
Weil McClain lasted around 10 years I think? (Here before I moved in)0
-
check the chloride levels in your water. i’ll bet the tank or manual has a range or limit for ph and chlorides. Warranty could be void if you water does not meet the specBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
From the Mega Stor II manual.
Not covered under warranty.. Any indirect‐fired water heater that has potable water with the following characteristics: chloride levels in excess of 80 PPM, measurable amounts of any compound containing chlorine, or PH less than 6.0 or greater than 8.0.
Also not covered is operating the indirect above 150 degrees or 150 psi. And, using a water softener that isn't operating within mfg specs.
http://www.velocityboilerworks.com/documents/MegaStor_II_Manual.pdf
If any of the above apply to your situation you may be SOL for warranty by the book. Assuming domestic water pressure and temperature were within spec you may have a good argument with two failed units within a month.0 -
"...they are demanding water sample..." I don't care how much chlorine is in your water, if it's drinkable, the tank shouldn't be leaking after 11 days.
I sounds to me that the vendor and rep is just trying to get out of replacing the unit or refunding your money by claiming the warranty is void, I hope not.
I like HTP ultra-stor tanks. I only had a problem with one and they stood behind it. Rattling of the heat exchanger.
Sometimes a letter from a lawyer can get things moving, if you reach an impasse. This is why I say, document everything in writing.0 -
After 11 days? You could probably fill it with bottles of bleach solution or and it should last several weeks. Clearly have an issue with their weld quality since the serial numbers are close together. That’s the only thing that could cause a failure that quickly. Basically after just a couple of heat cycles where the metal expands and contracts, the weld is breaking open. These might get welded with a robot or machine, so possible the settings were a little off somehow. But when they did QC testing, they passed a static pressure test, but when heated multiple times, they fail.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements