For heating system mechanics? I feel like I was guided when I found a cracked heat exchanger.
0
Comments
-
Pictures or you are a tease.0
-
I found a Patron Saint of Boilermakers, a few Patron Saints of Craftsmen, or maybe one of the Patron Saints of Homemakers, who also have an interest.0
-
Eligius it is.0
-
-
It's in the family home. I live 600 miles away so I don't spend much time up there. Members of my family spent a night and called me out of concern that furnace is unsafe. It is a 100 year old octopus with an oil burner from the early 90's. I flew up and did a combustion analysis.
AS FOUND: O2 19%, CO more than 5000ppm-disconnected probe from analyzer to avoid damage. excess air 370%.
AS LEFT: O2 16.2%, CO 16ppm, excess air 363%.
Mind you, I am not an HVAC person. I work on my company's high pressure steam system that runs 24/7. I check flue gasses three times a year. My burners can put out 25200 MBH . But excess air is usually 20%+/-. I only did an analysis on this out of necessity. I do not work on residentila equipment. Not my job.
Clearly, because of its age, it wasn't going to be air tight. but the excess air was crazy. Removed the smoke stack to vacuum soot, discovered stack was aged out and needed replacement. after removing stack, found source of excess air inside furnace.
She is finally DEAD! And I am thankful.
0 -
Good catch!
I'm not sure I'd fly 600 miles to look at a furnace, even for family. My hat is off to you, sir!
0 -
You may have saved some lives. CO detectors are cheap insurance and I always recommend them especially on any furnace older than 15 yrs.0
-
CO detectors never alarmed. Yet the house smelled like a truck stop from the 1970's. Eyes burned.
Before burner tune , I measured 12 ppm CO out of an air register inside the house after burner ignition; then CO dropped to zero ppm during firing. After burner tune 0-2 ppm after ignition then zero ppm during firing. I let my analyzer record all night and thought we were home free.
It was confusing at first because soot blew onto my analyzer while measuring from the air register and O2 + excess air were uncontrollable. Yet CO seemed under control.
The broken flue exiting the heat exchanger answered all my questions.
I'm just grateful that I didnt blow off removing the stack and missed it. If that stack shifted and opened the crack wider and someone in my family were poisoned or killed, it would have been unbearable because it was me who returned it to service.
Hence, someone was looking out for me. This isn't my line of work.0 -
-
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements