SuperStor SS-40 Aquastat Immersion Well LEAKING
StahlMaster
Member Posts: 18
in Plumbing
Comments
-
Well if it's leaking because of a weld failure (typically), then you need a new SuperStor.
If it's just the threads, drain system, back out well, re-tape, re-install (which may or may not be possible with your tank).There was an error rendering this rich post.
0 -
The company that makes the SuperStor does sell replacement wells so I'm guessing its not welded. The leak is coming out of the end of the tube where the aquastat goes in, not at the threaded end.0
-
Seems to me like you sort of have answered your own question. If you know why it's leaking, then you also know where. There are exactly three choices: is it a repairable leak in the assembly? Then repair it. Is the assembly replaceable with less hassle than repair? Replace it. Is the assembly neither repairable or replaceable? Replace the tank.
Since we don't know where the leak is nor why, we really can't say much about how that specific leak could be repaired...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
It's leaking out of the end of the tube where the aquastat is connected. Drip, drip, drip.0
-
Keep in mind the well for the SS is stainless, not brass.0
-
Swap it out. Get everything ready tape threads of new well have it within reach. disconnect the control turn of the boiler. Cool the tank off by running cold through it, just cool enough so you don't get burned during the next step. shut off water supply. Loosen the leaking well to hand tight and drain tank from boiler drain until you can hear the suction at the well. you'll have developed a vacuum at that spot, enough to quickly swap out the wells with out having to drain the whole tank.Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker1
-
cut away the insulation first and make sure it is not the weld or thread.
The leak could be either the tank weld around the port, the thread connection, or a pin hole in the well itself.
If you pull the sensor out and water flow out of the well, it's the problem.
Most often wells fail, but welds and threads can leak also.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Is there a product that will prevent corrosion in the well from the dissimilar metals? If so, where can I get it?0
-
This is an HTP SuperStor Ultra 45 tank? These are very thin wall stainless tanks subject of collapse if a vacuum occurs in the tank.
Better to shut off the cold water supply to the tank and open several hot water tap in the house then drain the tank and replace the well using a good sealant. I don't recommend opening the pressure relief valve as you may end up replacing it because it may thereafter leak.
We use a heat transfer paste on the aquastat probe before reinstalling the aquastat. I'm not aware of any heat transfer paste the act as a dielectric, if you think that dissimilar metals may have caused the leak. It would be a new one on me.0 -
and the well's are usually tough to get lose. Use a big wrench...0
-
-
However, the bulb for the aquastat is copper. Will that cause corrosion?0
-
It may not be shot, maybe just clean threads, retape and redope.
Reinstall and see what happens....
0 -
Better have a proper socket, breaker bar and persuader. The only time I had the same call I just grabbed a pipe wrench thinking no problem. Well there isn't a lot to grab and being factory installed it wasn't long before I was in trouble. Had to cut away a fair amount of the jacket in order to get enough bite on anything. Finally got it out but would never try it again without proper socket.0
-
-
A stainless well with a stainless bushing would lessen any electrolysis between the metals.
Brass and lower grades of stainless are far apart on the series. The electrolyte (water) has a bit to do also. If your water is softened or has high TDS, it will accelerate electrolysis. Area effect can increase electrolysis corrosion also.
Possibly hotter water accelerates electrolysis? I know hotter water causes more minerals to precipitate in DHW tanks.
A good, easy read on dissimilar metals here.
A 6 point deep socket is a sure way to remove and install wells with the least amount of wrestling.
https://www.assda.asn.au/technical-info/technical-faqs/galvanicdissimilar-metal-corrosionBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I have the new well ordered along with a new aqustat and pipe compound. There is about three inches of well sticking out from the tank with plenty of access all around. I do have 6 point sockets along with 6 point box wrenches. I will snap a few photos of the install and post them here. Thanks for all the information. I am determined to keep my "HydroTherm" AM 100 and SuperStor tank running long after others have written them off as not worth fixing.0
-
Sorry for the delay. Installing the new aquastat and aquastat well went very "well" (no pun intended). I was able to use my large 12pt box wrench to remove the old one. The new on was smaller in diameter but had the sleeve to fit my bigger opening. In the photos you can see where the leak was showing up on the aquastat box. I removed the bulb from the well with
a torch and some oil. I shot some compressed air into the old well and saw that a leak had formed at the tip of the well. Upon closer inspection I noticed a few pinholes where a plug was soldered onto the tube. I took a long screwdriver and tapped the plug from behind a few times and it popped right out. It looks like the plug was poorly soldered onto the tube, causing the leak.
1 -
I had the same problem as yours, and my unit is also ss-40. What is the part number you ordered? I can not find the same part, new part looks different and with a 3/4 adapter.
https://shophtp.com/ecommerce/product/pmw-3senp-1/aquastat-immersion-well-12
Thanks0 -
That looks just like the one I installed. They now come with an adapter (which you will need). I just unscrewed the old one (3/4") and put pipe joint compound on the new one and screwed it in tight.0
-
I have used never seaze to help slow or prevent this. Seems to be working fine to this day. Usually just coat the surfaces that need it.
Good to see all is complete.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements