Uponor ADS
Tom_133
Member Posts: 910
Anyone using the Uponor ADS software? If so I got a question
I was working on a heat loss for a friend using the ADS Software, his build was tall ceilings a bit of glass and R19 walls, quality windows. When I got to the construction quality settings, I put in best. Here is where I am a little perplexed. After plugging in all the heat loss factors the project called for plates, and a temperature of 110 at -20 and 20mph winds. Ok no problem, thats what I did, sadly at -20 (which we had for 2 weeks on and off, more on) it didn't keep up.
I had the system at no setback, no ODR, after turning the water temp to 135 it maintained the temp but wouldn't climb any higher. Water going out 135 coming back on all zones 125. Plenty of boiler, piping arrangement is correct.
After this I went back in and looked at construction quality and changed it to average, then my water temp with plates was 168 and needed supplemental.
Why is there such a vast difference when it comes construction quality on the program? What are the factors that make up that setting?
I was working on a heat loss for a friend using the ADS Software, his build was tall ceilings a bit of glass and R19 walls, quality windows. When I got to the construction quality settings, I put in best. Here is where I am a little perplexed. After plugging in all the heat loss factors the project called for plates, and a temperature of 110 at -20 and 20mph winds. Ok no problem, thats what I did, sadly at -20 (which we had for 2 weeks on and off, more on) it didn't keep up.
I had the system at no setback, no ODR, after turning the water temp to 135 it maintained the temp but wouldn't climb any higher. Water going out 135 coming back on all zones 125. Plenty of boiler, piping arrangement is correct.
After this I went back in and looked at construction quality and changed it to average, then my water temp with plates was 168 and needed supplemental.
Why is there such a vast difference when it comes construction quality on the program? What are the factors that make up that setting?
Tom
Montpelier Vt
Montpelier Vt
0
Comments
-
wow whats your loop length0
-
Because best is BEST and Average is garbage . It's really that simple . Your key would be to look at ACH that appears on each room entry sheet . Best and average are very different , that is your difference , one may show .3 ach while the other shows =<1 ACH . ACH is short for air changes per hour , pretty self explanatory that it takes more heat energy to heat a space that has 1 ach than one that only has .3 ach . Hope that helpsYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
-
I don't think I've ever used "Best"? Call me cynical but I just don't trust anything or anyone that much. I'd have to see the workmanship of the door and window installations, the quality of the insulation installation, and so on to put my name on it. Or, the person guaranteeing me "Best" would have to sign off on it.Steve Minnich1
-
Thanks guys, this helps. I now know that average is what I go with unless its spray foamed and blower door tested. Its funny that they have poor, average, and Best but the drop between best and average is quite substantial. Oh well, gotta figure this one out!!
Tom
Montpelier Vt0 -
If the average where you're at is anything like the average where I'm at, the average is pretty poor!0
-
In the Manual J calculations, "average" is a new home built to today's standards.0
-
WOW! If you are having your wholesaler or their salesman do your heat losses you better be very careful what they are plugging in there!!
I was very surprised the dramatic drop between the two selections, best was 110 degree water, average was 160 or something unbelievable.
They should have a dumb, dumb warning for me.Tom
Montpelier Vt1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements