Hydronic Manometer
Zman
Zman Member Posts: 7,609
edited January 2018 in THE MAIN WALL
I have been looking for a decent moderately priced hydronic manometer.
I would like to be able to verify flow at balancing valves and check pump delta P accurately.
This one looks like it would do the trick https://www.amazon.com/Dwyer-490A-4-HKIT-HVAC-Manometers-Micromanometers/dp/B073D8FWNN
Does anyone have experience with these?
Albert Einstein
  • ratio
    ratio Member Posts: 4,238
    That link goes to an air hood...
    I too have been, off 'n on, looking for a hydronic manometer. As near as I can figure, the Dwyer is the standard. I've found them for ≈$2-300 for nonames, there are several in the kilobuck range, and the Dwyer is in the middle. The Dwyer has a kit that looks like it's the bees knees, but it costs a lot more than I want to pay.
    I'd be willing to try a noname if someone has a good experience with one.
  • STEVEusaPA
    I've been playing with this one, seems to work fine. No display, you have to link it via Bluetooth to your smart phone.
    http://aabsmart.com/products.html
    They sell them at RE Michel.
    Don't know about checking pumps with it..
  • Zman
    Can I get the Dwyer and put a simpler kit on it. I am having trouble finding hoses and probes.
    Albert Einstein
  • Dan Foley
    Dan Foley Member Posts: 1,268
    edited January 2018
    I have used this one for years. Accurate and easy to use.
    http://www.tsi.com/hydronic-manometer-hm675/
    Zman
  • ratio
    Sure looks nice. But it's twice the price of the Dwyer kit (that I can't afford), and you have to fill out a form with 9 required fields to even download the manual from the TSI website. <sigh>
    @Zman; I'm not sure, but it looks like the hoses are standard ¼" flare fittings, = refrigerant hoses. You'll need a handful of brass fittings as well, and maybe a few adapters for Pete's Plugs as well.
    Zman
  • GW
    GW Member Posts: 5,184
    You would need to drill in Pete’s taps?
    Are there any good ultrasonic clamp on flow meters on the market?
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • RPK
    RPK Member Posts: 120
    I’ve been using the Dwyer wet/wet manometer that comes with that kit for a couple years. No complaints. I bought Pete’s adapters separately and adapted the connections on Pete’s plug adapters and manometer to 1/4 male flare fittings, and use a couple old refrigerant hoses with ball valves. The kit looks nice, but I don’t think it’s worth the extra cost.
    Zmanratio
    EBEBRATT-Ed Member Posts: 20,177
    I used to us a Bell & Gossett analog flow meter , used refrigerant type hoses and was good to 25' of head I think.. It was ok. @GW , usually you put in a balancing valve or "circuit setter" and it comes with Petes plugs installed. I like the Armstrong circuit setters.
    Also I have herd ultrasonic is unreliable. I know it won't work with any bubbles in the system and won't work with glycol. I think the professional balancers use them when they have to no tapings etc.
  • Bob Harper
    Bob Harper Member Posts: 1,162
    You can measure delta P with a manometer but for flow you really need a flowmeter instead of trying to calculate flow off pressures and temps. You can use something like this if the budget is no concern: https://www.gemeasurement.com/flow-measurement-control/ultrasonic-liquid/transport-pt900-portable-ultrasonic-flow-meter-liquids for about $6.2K
    For a fraction of that you could mount a magnetic flowmeter inline. If you need to make it portable you could use a spool piece. Much depends on how accurate you need to be. Check out instrumart for a huge assortment of types and brands of flowmeters. I used to use this program daily: http://www.flowexpertpro.com/
    Enjoy
  • Zman
    I purchased and returned a fairly expensive ultrasonic meter about a year ago. I read the entire manual then checked it on various pipe sizes with a water meter. The closest it was to accurate was 20% off.
    Albert Einstein
  • Zman
    I think the Dwyer with separate hoses and probes is going to be the trick. I wish someone sold an affordable set with all the different size probes
    Albert Einstein
    ratio
  • GW
    RPK so can you tap into the piping; drill the petes in?
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • Zman
    edited January 2018
    I think he is referring to using the tapped ports on circulators and using Pete's there.
    Pete's ports on a straight pipe would not do any good because you need an engineered restriction in the pipe like a balancing valve to know what the pressure drop means in terms of flow.
    Albert Einstein
  • GW
    makes sense, so for us residential guys, no good tools out there?
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    You can use a flow meter to measure the delta P on a circulator but it's no different than installing 2 pressure gages, subtracting the readings and converting to ft of head. The flow meter or manometer just reduces the chance for error because your using 1 instrument and it eliminates the math.
    If you need to check flow as @Zman mentioned you need a balancing valve or circuit setter "a known restriction" to plot the readings against to give you the flow reading
  • GW
    Yes great, Kinda would be nice to have a tool that you could strap on and take a reading.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    Could use a single gauge with 2 ball valves plus a 3rd to depressurization it and a couple Ts. See that on heat exchangers a lot to check pressure drop. But yes you need to do the math.
  • Zman
    That is very common way to do commercial pumps.
    With the balancing valves, you are usually reading inches WC. Kind of need a meter...
    Albert Einstein
  • Zman
    I agree. I just don't think the technology is there. If you get a chance to demo one, clamp it on a pipe with a water meter and see how accurate it is. I would love to find one that works. :)
    Albert Einstein
  • ratio
    That's strange. ISTR hearing that the ultrasonic flowmeters were pretty good, and the chinese knockoffs were not much worse than the expensive models.
