Going against Dan Holohan's advice

I've read, and been re-reading Lost Art of Steam Heating. So I'm really bothered that I've inherited an inefficient running steam boiler. I just moved back to the Bronx and am a Franciscan brother who serves the homeless. So whoever "fixed" our system has left problems that no one else sees.
Firstly, it's a relatively new steam boiler, 2 pipe system, steam traps appearing to work. The easiest problem to see is that it cuts in at 2 psig and cuts out at 10psig, and the gauge confirms it. Then I noticed the inlet to the condensate pump was not on, probably intentionally. The brothers said (and the boiler room paint confirms) that "this pipe was shooting out steam", the open air pipe from the condensate pump, so steam coming through the return at some point. It looks like the F&T is new. There is a functioning air vent at the top of the return in the boiler room; I can hear it venting. But it looks like there is new copper piping that may have tried to bypass the condensate pump and turn it into a gravity feed. It works, so I shouldn't complain, but they have it cranked up.
I "cranked it down" to cut in at 1/2psig and out at 2. I ran into trouble. Although I couldn't watch the boiler the whole time, it seemed to be cutting out due to low water, though I could still see it in the gauge glass. Thermostat was calling for heat, and it wasn't cutting out because of pressure. Turning up the pressure seems needed to return the condensate.
So should I think this is fine and not worry since we have heat? Is this a reasonable and desirable alternative to replacing a faulty condensate pump? Would it be cost effective long term to buy a pump (not asking for prices)? Thanks guys.

Brother Max CFR





Comments

  • Ironman
    Ironman Member Posts: 7,555
    You may have an issue with your return lines.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    BrotherMax
  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    Interesting...

    Almost certainly more than one problem. There are at least two possible reasons for steam shooting out of the condensate tank -- one is that one or more of the steam traps on the radiation is not closing properly (which, at 10 psi, wouldn't surprise me a bit). The other is hot condensate getting into the tank (that wouldn't surprise me on 10 psi either!) and flashing into steam in the tank. [edit: I just thought of a third way -- what is keeping boiler water from backing into that condensate tank when the pump is off???]

    I think the first thing I would do is get an IR thermometer -- they're not all that expensive -- and go around to every single steam trap in the building and verify that they are, in fact, really closing. Just to satisfy curiousity, if nothing else.

    Then really think about how the whole thing is piped, and where vents are. In particular, how are the steam mains vented? In some systems they have their own vents. In others, though, they are connected to the dry returns with crossover traps -- which also need to be checked, if they are there, to make sure they are closing properly. In either case, the dry returns should have very little pressure in them, if any, and never any steam (in a perfect world, the vents on a dry return would never close. The world is far from perfect).

    I have to admit that I can't see how high pressure would keep water in the boiler, while low would let it out and cause it to turn off on low water.

    Would you take a few more pictures of the boiler and the associated piping? We might see something... might not, too.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    BrotherMax
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    Steam coming out of the condensate vent pipe is caused by only one thing....Bad steam traps.

    Bad traps will cause high fuel bills and the overheated condensate will damage the condensate pump eventually. Loosing steam will cause more make up water (and oxygen) to be added to the boiler which is bad

    Also the F & T trap on 1 condensate return is probably a "master Trap" which is a band aid for not fixing the defective steam traps in the system.

    In short your system won't work right until these items are addressed. You need a good steam man (if you can find one)

    None of this constitutes an emergency I wouldn't touch it until the weather backs off a little bit but these items should be taken care of to avoid future problems
    BrotherMax
  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    @BrotherMax -- if you can get @Mad Dog to come look at it, it will be plain sailing after that! One of the very best.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,519
    Thanks Jamie..means a lot. Mad Dog
    Robert O'Brien
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,563

    @BrotherMax -- if you can get @Mad Dog to come look at it, it will be plain sailing after that! One of the very best.

    Ditto!
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • BrotherMax
    BrotherMax Member Posts: 6
    So to follow up: Brother Mariano was working on a much trickier boiler on the same grounds, but different building. I've got the only 2 pipe system on the grounds. Bro Mariano was really bright and a good worker, but isn't with us any more.
    Re: steam traps...We had water hammer (the priests and brothers all thought it was normal) due to steam getting into the return, which immediately made me think bad traps, which I found out were 10+ years old. I changed some where I thought it was originating, and I got lucky and it fixed the hammer. I expect to wait until spring to replace the other elements.
    Would it be worth my while to vent the F&T trap? It occurs to me that any air probably would have nowhere to go unless it is vented...
    I found that the 2 pipes that feed into the return are the condensate return, which has a (spitting) Gorton air eliminator on it. Would a spitting air vent indicate pressure, as in steam passing a trap and in the return?
    The F&T trap is on the end of the steam main, the same pipe that feeds the radiators in the basement. Does it make any sense?
    There's a check valve on the return, which with a condensate pump made sense, but it could be slowing things (at regular pressure).





  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,519
    Yes, Brother, some of it makes sense, but very hard to nail it down without seeing the while picture. Are you affiliated with the Franciscan Brothers of Saint Francis Preparatory H.S. in Fresh Meadows & The College in Brooklyn? Mad Dog
  • BrotherMax
    BrotherMax Member Posts: 6
    We aren't the same as those Franciscans you know. We are the Franciscan Friars of the Renewal, started under Cardinal O'Conner in New York in 1987. 156th & Melrose. Our initials that we use at the end of our names to identify ourselves to others is CFR.
    I'm trying to piece things together with the boiler situation, but I expect the previous brother responsible will just say "steam came out of the condensate open air vent, and that the plumber fixed it". It was probably a cheap fix, with a bigger cost in utilities. Is it reasonable to think that a condensate pumped return could be converted to a gravity fed return?
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Look for the "Dimension B" in TLAOSH.
    Factors are water line, last steam trap height and pressure.

    I danced with a situation where they tried to use gravity return and eventually learned that the new boiler was installed about 4-5' above the original. Condensate would not return, hammer in mains, boiler would auto overfill etc.
    So the pump was required.
  • Steamhead
    Steamhead Member Posts: 17,387
    edited January 2018

    So to follow up: Brother Mariano was working on a much trickier boiler on the same grounds, but different building. I've got the only 2 pipe system on the grounds. Bro Mariano was really bright and a good worker, but isn't with us any more.
    Re: steam traps...We had water hammer (the priests and brothers all thought it was normal) due to steam getting into the return, which immediately made me think bad traps, which I found out were 10+ years old. I changed some where I thought it was originating, and I got lucky and it fixed the hammer. I expect to wait until spring to replace the other elements.
    Would it be worth my while to vent the F&T trap? It occurs to me that any air probably would have nowhere to go unless it is vented...
    I found that the 2 pipes that feed into the return are the condensate return, which has a (spitting) Gorton air eliminator on it. Would a spitting air vent indicate pressure, as in steam passing a trap and in the return?
    The F&T trap is on the end of the steam main, the same pipe that feeds the radiators in the basement. Does it make any sense?
    There's a check valve on the return, which with a condensate pump made sense, but it could be slowing things (at regular pressure).


    In the middle picture, two pipes come thru the wall and drop to the pump. One has an F&T trap in it, if that's the end of a steam main and the other one is the end of a dry (overhead) return line, the setup is correct. @BrotherMax , can you verify this?

    The spitting vent indicates steam in the return line. That's wrong. Some of that steam is obviously getting into the tank and coming out the vent.

    That system was designed to run at less than a pound of pressure. 10 PSI is 9.5 PSI too much. Get the pressure down, and if you still have steam in the return, fix the traps.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    JohnNY
  • BrotherMax
    BrotherMax Member Posts: 6
    So in the picture, the water returns on the left, the steam main ends on the right. I talked with the brother who was taking care of it, and he said the plumber thought the condensate pump wasn't necessary. I turned it on and it's working, but I'll watch to make sure it's working correctly. I'll turn down the pressure, because I hate to have it high. I haven't gotten to fix all of the trap elements, but I finally have them on hand. Thanks.
  • Steamhead
    Steamhead Member Posts: 17,387
    Let us know how you make out!
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    BrotherMax
  • BrotherMax
    BrotherMax Member Posts: 6
    Thanks for all your input. I talked with the brother who handed me a small mess. He took bad advice from a plumber who told him he didn't need a condensate pump and then proceeded to crank up the boiler pressure. The condensate pump is back on, I cranked down the pressure, and we've got heat, we've got efficiency, and there isn't any more spitting from the main return line. I don't know why this plumber thought to do this stuff, but I'm glad it was easy to put right. Thank you all for your advice.