Pex for condensate lines?
rhodebump
Member Posts: 152
Comments
-
-
NO, it was a genuine question. In the last week, I have had to replace 20 feet of 1/2 black pipe that is used to return condensate to the steam system. It's piping that comes from the steam trap.
Working with black pipe is very difficult, and you have to get the measurements just right. It would be so much easier if I can just use pex. There are some pex connections that go from NPT threads to pex.
Since the condensate should be just water and air, I would think PEX could be used. It's also no pressure in this pipe.
Thanks!0 -
No. not a good idea. 200F is max temperature. You might get away with it on uninsulated wet returns near the boiler, but you are pushing it. Above 180F it starts losing strength and pressure limits drop. But pressure isn't an issue on steam.
That being said, latex paint isn't supposed to be used over 200F, but 1/2 my radiators are painted and I have no issues at all.
Best alternate cheaper, easier to work with option is copper tubing. That's what's used for mini tube systems.-1 -
-
I'd look at hoses.0
-
Not only temp limitations for just hot condensate, but sometime you will have a trap fail and live steam will shoot around the returns.
Also, a dry return has to have good pitch with no pockets to drain water and no traps caused by those pockets to impede air removal........something to keep in mind if you go to copper is to use rigid copper and not soft tubing which never really straightens out no matter how much you try.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements