Click here to Find a Contractor in your area.
In fairness to all, we don't discuss pricing on the Wall. Thanks for your cooperation.
Need to contact us? Visit https://heatinghelp.com/contact-us/.

Octogenarian Marries Two Youngsters

IronmanIronman Posts: 4,223Member
This 100+ year old system was originally coal fired, gravity flow. Someone converted it to forced flow, gas fired with this beast 50+ years ago:






The old gal was still chugging along at 472k btus.

The new owners wisely decided that they needed something more efficient after a March natural gas bill of $1,000.

The load calc came to 195k btus with a design temp of 10*. More than enough for Staunton, VA where ACCA specs 14*. It's interesting that the EDR came to 227k btus and when I ran the load calc with a design temp of 0*, it came to 227k btus also. It was common many years ago to use 0* design temp around here. The dead men may have been a lot more scientific than we give them credit for.

We chose to go with two HTP UFT 120 boilers + a 40 gal. indirect. Because we were going with 2 boilers and we also wanted to protect the new boilers from rust and debris from the old system, we made our own LLH/dirt separator/MBR. Don't ask what's inside: it's top secret.







Bob Boan







You can choose to do what you want, but you cannot choose the consequences.

Comments

  • Danny ScullyDanny Scully Posts: 935Member
    Roll of gritt cloth? :lol:
  • EBEBRATT-EdEBEBRATT-Ed Posts: 3,946Member
    rolled up pc of expanded metal and a magnet
  • kcoppkcopp Posts: 3,054Member
    Do you plan on installing a mag filter or treating the system w/ an inhibitor?
  • IronmanIronman Posts: 4,223Member
    kcopp said:

    Do you plan on installing a mag filter or treating the system w/ an inhibitor?

    Sorry, but I can't answer that at this time.
    Bob Boan







    You can choose to do what you want, but you cannot choose the consequences.
  • I love secrets:



    Work looks great, even if mysterious...
    Serving Rhode Island & Eastern Massachusetts
    Old Houses & Steam Heat Our Specialty
    newenglandsteamworks.com
  • IronmanIronman Posts: 4,223Member
    A few almost final pics. One of my men is gonna spray paint the header tomorrow.




    Bob Boan







    You can choose to do what you want, but you cannot choose the consequences.
  • John MillsJohn Mills Posts: 826Member
    National US Radiator. We had one in the house I grew up in. Would have had coal snowman when built and in the 50s the gas boiler and pump was installed. Heated great. Split open a year after the gas valve stuck open and about blew the thing to the moon. I'm still amazed my Dad knew how to shut off the gas to it! In 1989 a WM HE was installed then the folks moved out.
  • Solid_Fuel_ManSolid_Fuel_Man Posts: 936Member
    @Ironman is that cell-core pvc for venting?
    Master electrician specialising in boiler and burner controls, multiple fuel systems, radiant system controls, building controls, and universal refrigeration tech.
  • JUGHNEJUGHNE Posts: 4,360Member
    Maybe for air inlet only?
  • IronmanIronman Posts: 4,223Member

    @Ironman is that cell-core pvc for venting?

    Just on the intakes; the exhausts are schedule 40. I wondered how long it would be before someone asked that.
    Bob Boan







    You can choose to do what you want, but you cannot choose the consequences.
  • cgdelzellcgdelzell Posts: 21Member
    I need some education please. I have always found that you do not screw copper into steel, when did it become OK to do that?
  • Danny ScullyDanny Scully Posts: 935Member
    It’s a closed system @cgdelzell, less of a concern. But I’m wondering about the bushings on the gas piping @Ironman? That’s allowed in your area?
  • I like it. But maybe you could just whisper to us the top secret bits, and no one else will be the wiser?
    Serving Rhode Island & Eastern Massachusetts
    Old Houses & Steam Heat Our Specialty
    newenglandsteamworks.com
  • captaincocaptainco Posts: 376Member
    Seeing how Schedule 40 PVC can only handle 140 degrees I assume these boilers operate at a low water temperature?
  • IronmanIronman Posts: 4,223Member
    edited October 2017

    It’s a closed system @cgdelzell, less of a concern. But I’m wondering about the bushings on the gas piping @Ironman? That’s allowed in your area?

    The IFGC prohibits cast iron bushings, but the UPC allows them. Brass, steel and stainless bushings are okay according to the IFGC. That 1 1/4 X 3/4 bushing is the thickest fitting in the line. IDK why the IFGC still prohibits them. That would be a good question for @Tim McElwain .

    If you have a Honeywell replacement gas valve on your truck that says 1/2 X 3/4, you'll find a 3/4 X 1/2 bushing included.

    captainco said:

    Seeing how Schedule 40 PVC can only handle 140 degrees I assume these boilers operate at a low water temperature?

    PVC is rated for 149*, not 140. But the pipe manufacturer does not certify it for appliance venting, the APPLIANCE manufacturer does that. HTP certifies PVC venting for that boiler as long as the included CPVC nipple is used. The boiler has a flue temp sensor which limits flue gas temp to 145* inside the boiler. Keep in mind that flue gas temps drop quickly as they move down the pipe.

    Bob Boan







    You can choose to do what you want, but you cannot choose the consequences.
  • IronmanIronman Posts: 4,223Member

    I like it. But maybe you could just whisper to us the top secret bits, and no one else will be the wiser?

    Maybe a little down the road.
    Bob Boan







    You can choose to do what you want, but you cannot choose the consequences.
  • IronmanIronman Posts: 4,223Member
    Dressed up a little:

    Bob Boan







    You can choose to do what you want, but you cannot choose the consequences.
  • Danny ScullyDanny Scully Posts: 935Member
    We’re ignoring you and all your subsequent posts until you tell us what’s in it :wink:
  • IronmanIronman Posts: 4,223Member
    edited October 2017
    Soon. I may be able to tell one of the ingredients soon. We're still testing.
    Bob Boan







    You can choose to do what you want, but you cannot choose the consequences.
  • Leon82Leon82 Posts: 492Member
    I'll guess 1/4" steel mesh formed into a roll
  • Solid_Fuel_ManSolid_Fuel_Man Posts: 936Member
    I'm guessing some stainless steel wool....and some type of magnet in there.....
    Master electrician specialising in boiler and burner controls, multiple fuel systems, radiant system controls, building controls, and universal refrigeration tech.
  • kcoppkcopp Posts: 3,054Member
    I have done both on a couple of my prefabbed headers...
  • unclejohnunclejohn Posts: 1,272Member
    Duh *It's water.
Sign In or Register to comment.

Welcome

It looks like you're new here. If you want to get involved, click one of these buttons!