Repeated water heater failure
Comments
-
Water heaters are not intended to function as sources for space heating. Period. Without knowing what aspect of the water heater is failing, it would be foolish to say that it was, for instance, excessive use of the elements and scaling on them, or just excess flow through the heater, or just what -- but for sure it's the wrong piece of machinery for the application.
Get a small proper boiler for the space heating -- air handler -- and a good water heater for the domestic hot water. You will be a lot happier.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Do you have an expansion tank on the water heater tank?
Typically a water heater backs the increased water pressure into the cold water system. However with this being heating there should be a back flow or check valve between the hot water and house cold domestic.0 -
We do have an expansion tank as a part of this system for that reason.0
-
-
Is the hydro coil seperate from the domestic with a heat exchanger, or is there street pressure going through the hydro coil?0
-
It has happened that an expansion tank is placed on the wrong side of a check valve feeding the tank. Of course this makes the expansion tank isolated from the water tank.0
-
-
Hello, Have you looked at the old tanks to find clues for failure? This would include where they leaked, what condition the anode rod was in, the nature of sediment from the tank, (if the tank was subject to too much pressure, you will likely see blue glass flakes in the sediment), evidence of relief valve activity, tank bulging (you might see this in the combustion chamber), a pile of rust on the burner, (from too much condensation in the flue or bad supply air) and lastly, streaks of rust running down the heater's legs or in the pan (this would be another sign of condensation from too heavy usage.
Try putting a pressure gauge on the drain valve of the existing tank and see if it ever gets over 80 psi. Use a gauge that has a pointer that records the highest pressure.
What is the water quality like? Do you soften the water?
I'm sure we'll have more questions!
Yours, Larry0 -
Larry - All great ideas. Because I'm 3000 miles away from the house and the water heater (tenant is in the house currently) I've had plumbers replace the tank but haven't gotten any info from them as to why they failed - and I'm not there to examine it all myself. Seems like a very logical activity that I'll have them undertake with this tank.
I know there was a pressure gauge on the drain valve (when I left 5 years ago), but don't know what the reading is currently. Will ask my tenant to look for/at it and see what that tells us.
We don't soften the water. The water quality is good. (?) We're on the city of Oakland water system.0 -
Sorry to sound like a stuck record. Whether it's electric or gas, it's a water heater. You are trying to use it like a boiler. It isn't, and was never meant to be. I'm sure with some detective work -- as suggested above -- you find the direct cause of the failure, but that won't fix the problem.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
There are a lot of those Apollo systems out there, they are still installed in some areas.
In addition to excessive pressure I'd look at the operating temperature also. If they have it cranked to 150- 160 or hotter, that really diminishes the life of tanks.
The type of water, hardness and ph as well as how much water goes through the tank is part of it. Checking anode rods would also give clues to what is happening inside the tank.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Jamie - Appreciate your thoughts. I understand your suggestion. The challenge is that Apollo's recommended installation for the unit is with a water heater, not a boiler. Which is why we initially installed it with a water heater and not a boiler. Two other clients of the architect who designed our system are using it with a water heater without failure. But it could very well be that we need to replace one large water heater with a smaller water heater and a boiler for the Apollo system. Right now, I'm just trying to consider all the things it could possibly be so that we can be thoughtful about the solution. I'd rather not be back here again in 18 months after spending $5500.0
-
@Jamie Hall, I agree with what your thinking and your right but were use to 2' of snow.
This things in Oakland. They probably run heat for a total of40 hours for an entire heating season0 -
Ebebratt - Correct. It probably runs maybe December to February on some days/nights and only heats three rooms in the house. But if we need to put in a boiler, so be it. That can't be much more expensive than what they quoted me for a high performance 70-gallon water heater (every 18 months).0
-
-
-
Water heaters are used commonly for space heating in north east area...Manufactures approve it with certain models....Condos with hydro air are a big time user of them...Jamie Hall said:Water heaters are not intended to function as sources for space heating. Period. Without knowing what aspect of the water heater is failing, it would be foolish to say that it was, for instance, excessive use of the elements and scaling on them, or just excess flow through the heater, or just what -- but for sure it's the wrong piece of machinery for the application.
Get a small proper boiler for the space heating -- air handler -- and a good water heater for the domestic hot water. You will be a lot happier.-1 -
-
There are LOTS of thing you CAN do.... but Should you
Need to move to a different set up.
0 -
Point is, they are acceptable, per manufacture....0
-
Some engineers design combined systems for large commercial buildings. This company was shopping for approved low lead zone valves, air seps, etc to use with their systems.
http://www.williamscomfortprod.com/integrated-piping-system/Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Is the tank actually bursting? Or, does the plumber you use change it because the relief valve is leaking. Don't laugh, I have seen it done. There are a lot of those hydro setup around here running on oil fired water heaters. Technically they are not a boiler, but they do work fine.
Rick0 -
-
> @j a said:
> Rick I would have never thought of the guy replacing it for a relief valve popping, only because I assumed it was a tech of sorts....that worked on it.....But now that you say that it is possible....But I would hope nobody is that stupid
>
>
> or sly and greedy, knowing the owner is 3k miles away and hasn't been on site in 5 years.
Warranty after 18 months? You'd think. But not labor.
The science of deduction hits a fork in the road.0 -
-
JUGHNE - Great thought on the pictures. I'll have my tenant take some photos. He sent me this one today. It's the pipe that comes out of the top of the water heater. It should be perpendicular to the tank top and it seems bent at about a 20-30 degree angle. To me that seems to indicate some serious distortion of the tank. But I'm not a professional.
My tenant said they had a plumber come out and look at it, saw this pipe and said he'd never seen that happen before.
Thanks all for the continued thoughts. It's been a puzzlement to me.
0 -
A simple lazy hand test gauge would identify an over-pressurization condition. Tanks will seriously distort when over pressurized.
Most plumbers would check the operation of the relief valve and add a gauge to monitor the pressure fluctuations for a few days after seeing that connection. It took a lot of force to tweak that tapping like that, I doubt it left the factory in that position.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
A gauge similar to this can be found at plumbing suppliers, maybe even the box stores. Screw it onto to drain valve at the tank bottom and watch the red hand as it will record the highest pressure.
By code and usually shipped and installed in water heaters is a temperature and pressure relief valve to prevent pressure in excess of 150 psi.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot rod said:
A gauge similar to this can be found at plumbing suppliers, maybe even the box stores. Screw it onto to drain valve at the tank bottom and watch the red hand as it will record the highest pressure.
This. Even the lipstick Lowe's in my neighborhood has three of those on the shelf, albeit without the test teat on the side.
0 -
I would have never thought that water heater can deform like that under pressure. Wow. And prv not being triggered? Is there a prv? I'd hate to see this thing turn into a rocket.0
-
That's crazy! I wonder what the flue looks like down the center?russhmeyer said:JUGHNE - Great thought on the pictures. I'll have my tenant take some photos. He sent me this one today. It's the pipe that comes out of the top of the water heater. It should be perpendicular to the tank top and it seems bent at about a 20-30 degree angle. To me that seems to indicate some serious distortion of the tank. But I'm not a professional.
My tenant said they had a plumber come out and look at it, saw this pipe and said he'd never seen that happen before.
Thanks all for the continued thoughts. It's been a puzzlement to me.
this is why we need to be detectives also. Be curious as to what could cause such events. Then correct them.
0 -
Gordy - what should we be looking at with the flue? How would the flue cause pressure build up in the tank? (Sorry if these are dumb/obvious questions but I'm not a pro. Trying to know as much as I can before the plumber comes out to investigate next week.)0
-
The flue won't cause a pressure build up. However, a pressure build up in the tank could cause the flue to collapse, or partially collapse. Which would interfere with the draught and possibly get combustion gas rolling out into the structure. Overall, not good. Not good at all.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England-1 -
-
-
That is crazy, someone's gonna get hurt.....Highly advise moving fast on getting to the bottom of the issue...Gordy said:
That's crazy! I wonder what the flue looks like down the center?russhmeyer said:JUGHNE - Great thought on the pictures. I'll have my tenant take some photos. He sent me this one today. It's the pipe that comes out of the top of the water heater. It should be perpendicular to the tank top and it seems bent at about a 20-30 degree angle. To me that seems to indicate some serious distortion of the tank. But I'm not a professional.
My tenant said they had a plumber come out and look at it, saw this pipe and said he'd never seen that happen before.
Thanks all for the continued thoughts. It's been a puzzlement to me.
this is why we need to be detectives also. Be curious as to what could cause such events. Then correct them.
-1 -
Thinking out loud here. There should be an x tank for the air handler loop as well as the domestic side.
What I'm finding odd here is that the water heaters are only lasting 18 months. Is the failure from aggressive domestic water weakening the tank? Causing the tank to deform from domestic pressure which may not be high enough to pop the relief valve? Yet high enough to deform the tank?
Hard to believe these water heaters all had defective relief valves.....
What is water pressure on domestic?1 -
No need to have multiple expansion tanks, it all the same water. One properly sized ThermTrol should do the trick.
These tanks are supposed to be better quality and enameling than standard WH tanks. Glass lined tanks are usually able to handle most any water condition.
Relief valve and expansion tank installation and operation needs to be confirmed.
http://www.ableair1.com/pdf/apollo_brochure.pdf
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Gordy - Thanks for the thoughts. Photo of the expansion tank below with pressure gauge. Date on the tank (1/23/16) is when we replaced the expansion tank and put in the current WH, which started leaking about 2 weeks ago.
To your questions: "aggressive domestic water" - do you mean the chemical composition of the water? We haven't heard any of our neighbors having similar WH problems and we're all on the same Oakland city water line - wouldn't they have problems too if it were the composition of the water?
"Domestic water pressure" - I ordered a high quality water pressure gauge to be sent to my tenant in Oakland. I'm going to have him put it on a hose bib near where the city line comes into the house, as well as on the drain valve of the WH to get a read of what the standing water pressure is in the house. About 12 years ago, the pressure from the city was so high we put in a water pressure reducing valve at the main water line in, But I don't know if it got set correctly at instillation or if it has somehow changed over time.
I'm having the tenant take some more pictures of the tank, as well as close ups of the relief valve per other questions on this thread.
I have someone coming in this week to examine and propose a solution. It's a plumbing company that also installs hydronics (for the air handling system that's that is attached to the WH). The plumber I've traditionally used isn't getting it fixed - after 3 tries.
Thanks for all the various thoughts and threads. They're extremely helpful.
0 -
My bad on the double X tank. I thought there was an exchanger in the water heater for the airhandler loop. Now I really don't care for that setup.hot rod said:No need to have multiple expansion tanks, it all the same water. One properly sized ThermTrol should do the trick.
These tanks are supposed to be better quality and enameling than standard WH tanks. Glass lined tanks are usually able to handle most any water condition.
Relief valve and expansion tank installation and operation needs to be confirmed.
http://www.ableair1.com/pdf/apollo_brochure.pdf
Is it possible the fitting took a blow from an external force?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements