"Octopus" gravity furnace/boiler!

donaldmc
donaldmc Member Posts: 35
Here's one I haven't seen before!
I'm visiting a friend near Colgate in upstate New York, he asked me to look at his attic expansion tank.
It was leaking, obviously it needed to be replaced.
I went down to see the boiler because I was seeing radiators and air ducts all over the house and found this!
I've never seen one before !
Check out the pictures.....

Anyone know of an 'off the shelf' open expansion tank for a gravity system?






delta TSuperTech

Comments

  • ChrisJ
    ChrisJ Member Posts: 16,323
    Wait.


    What?

    That does both hot air AND hot water?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • donaldmc
    donaldmc Member Posts: 35
    Yup! Both.....
  • bob_46
    bob_46 Member Posts: 813
    Interesting . Maybe instead of hydro-air we should be looking at air-hydro. A furnace is cheaper than a boiler, just stick a coil on it.

    There was an error rendering this rich post.

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Save that door, and the piece above it!

    There was an error rendering this rich post.

  • JUGHNE
    JUGHNE Member Posts: 11,295
    Do the CI radiators get hot when the heat is on?
    Are there actually any pipes connected to the furnace?
    What heats the domestic water for the bathroom/kit?

    Perhaps, just perhaps, the old rad system is abandoned.
    The boiler was removed and replaced with forced air.
    The expansion tank in the attic still has the cold water feed connected and the valve that should have been shut when the boiler was decommissioned is allowing cold water to seep thru and filling the leaky tank. Just a WAG
  • Jamie Hall
    Jamie Hall Member Posts: 24,984
    I have one just like that in the basement of the main house I care for. Looks almost the same! Except that mine is rusted out, and not in use any more... ask @Charlie from wmass -- he's seen it.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Charlie from wmass
  • ChrisJ
    ChrisJ Member Posts: 16,323
    JUGHNE said:

    Do the CI radiators get hot when the heat is on?
    Are there actually any pipes connected to the furnace?
    What heats the domestic water for the bathroom/kit?

    Perhaps, just perhaps, the old rad system is abandoned.
    The boiler was removed and replaced with forced air.
    The expansion tank in the attic still has the cold water feed connected and the valve that should have been shut when the boiler was decommissioned is allowing cold water to seep thru and filling the leaky tank. Just a WAG

    There be pipes going into the sides of that furnace if you look closely.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ratio
    ratio Member Posts: 3,803
    They shore don't make 'em like that ennymor.
  • kcopp
    kcopp Member Posts: 4,474
    That's a cross between a Rube Goldberg and Frankenstein's Monster.....
  • Jamie Hall
    Jamie Hall Member Posts: 24,984
    ratio said:

    They shore don't make 'em like that ennymor.

    There are times when even I will allow as to how some progress has been made, and is good! Though in defence of those old monsters, I would point out that they needed no power to operate at all -- just a strong back and some skill at making the fire go.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,588
    You could get a plain steel compression tank and use it (if you can find one with a tapping on top for a vent)
  • HVACNUT
    HVACNUT Member Posts: 6,373
    The original owner must have been the envy of the town in 1908.
  • ChrisJ
    ChrisJ Member Posts: 16,323
    HVACNUT said:

    The original owner must have been the envy of the town in 1908.

    Styling to me, screams 1930s-1940s.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • jumper
    jumper Member Posts: 2,389
    Wish I had thought of combined hot water & air heating. Steam and air may be an even better idea. Think of the B dimension one could accomplish.
  • ratio
    ratio Member Posts: 3,803
    So, an 80 year lifespan. Hmmm. What residential unit coming off the assembly line today will have an 80 year lifespan? Judging by the unit's I've seen the most of, you'd need maybe 5 to get to that lifetime. Think they'd save enough fuel over 80 years to replace it four additional times?
  • ChrisJ
    ChrisJ Member Posts: 16,323
    ratio said:

    So, an 80 year lifespan. Hmmm. What residential unit coming off the assembly line today will have an 80 year lifespan? Judging by the unit's I've seen the most of, you'd need maybe 5 to get to that lifetime. Think they'd save enough fuel over 80 years to replace it four additional times?

    No, that's been my argument all along but I seem to be all alone in that suspicion.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ratio
    ratio Member Posts: 3,803
    ChrisJ said:

    ratio said:

    Think they'd save enough fuel over 80 years to replace it four additional times?

    No, that's been my argument all along but I seem to be all alone in that suspicion.
    Not all alone. I also see it as Pretty D@mned Obvious that moving costs around falls more under the heading "sleight of hand", and not necessarily pure efficiency. But my observations are more philosophical than economic in nature.
    ChrisJ
  • Jamie Hall
    Jamie Hall Member Posts: 24,984
    ChrisJ said:

    ratio said:

    So, an 80 year lifespan. Hmmm. What residential unit coming off the assembly line today will have an 80 year lifespan? Judging by the unit's I've seen the most of, you'd need maybe 5 to get to that lifetime. Think they'd save enough fuel over 80 years to replace it four additional times?

    No, that's been my argument all along but I seem to be all alone in that suspicion.
    You're certainly not alone, @ChrisJ -- I feel exactly the same way. And sometimes even say so... !
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ChrisJ
  • JUGHNE
    JUGHNE Member Posts: 11,295
    edited June 2017
    I have been gone for 2 days.
    The 3 questions I asked have not been answered by the OP.
    I see the pipes but are then just hanging abandoned or actually connected.
    Perhaps a domestic HW pre-heat coil inside??

    I removed a nearly exact gravity hot air furnace from my brother-in-law's basement. It had an after market blower fan on it though. I took it apart piece by piece for removal. The same hot air heat exchanger was inside. It was large enough that maybe you could have a boiler HXC or HW coil inside. Not in this one.

    There must be rule # something about working for in-laws. But the concern was for my sister. There were rooms without heat runs, no air filter and no AC. I installed a 90+ condensing furnace with a used AC unit. For the track record, in the last 16 years they have had to replace the inducer fan assembly and 1 HSI. The brother in law will not comment about the current NG bill (give no quarter in my direction :| ) so I believe it must be less than with the old furnace and gives better heat distribution.

    PS: Jamie was yours a combo unit?
  • Jamie Hall
    Jamie Hall Member Posts: 24,984
    @JUGHNE -- no, it wasn't. And it just heated the north end of the main building. Installed in 1893! Most of the ductwork is still there -- I'm not quite sure why I haven't taken it, or the furnace, out yet, but I haven't. Not really in the way. I've toyed with the idea of getting the ducts thoroughly cleaned (boy would they have to be -- nothing like coal dust!) and using them for AC -- but it doesn't get hot enough often enough to be worth the effort.

    Back in the day, the hot water was supplied by a coil in the wood/coal stove in the kitchen once running water was installed (about 1905). I can't believe that there was that much of it, but it must have been an improvement on schlepping kettles of luke warm water for a bath. The plumbing was interesting, shall we say. I've replaced almost all of that, though.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,392
    the original water furnace
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • donaldmc
    donaldmc Member Posts: 35
    This unit is fully functional. The boiler part is a water jacket (see pics) around the combustion chamber and water circulates via gravity, feeds 81-10 cast iron radiators.
    The LARGE air vents slowly give heat in almost every room (so says the home owner) I could not find a fan on the duct work so it too must be gravity! The return air vents are neatly placed in the bottom risers of the staircase, nice touch.
    The DHW is from a electric water heater.
  • Jamie Hall
    Jamie Hall Member Posts: 24,984
    It was gravity air. If it is anything like the one in the place I care for, it worked remarkably well -- once one gets it going. It can take hours for the air circulation to get established, but once it does it's really quite pleasant -- and utterly silent. Response time is a bit slow... There is probably an outside air intake to the return plenum, controlled by a damper, as well as the building returns.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • donaldmc
    donaldmc Member Posts: 35
    sorry 8-10 CI radiators
  • JUGHNE
    JUGHNE Member Posts: 11,295
    That is a pretty unique system.
    Some old water gravity systems had a plain steel compression tank hung between the floor joists in the basement to replace the attic open top tank. However a pressure relief valve must be added to the system as the relief previously was the attic tank overflowing into the drain pipe.

    IIRC the add on fan blowers went on the top of the furnace with the wheel into the plenum. Belt drive motor was obvious on the exterior of the top.

    Good longevity yes. However waiting, as Jamie said, possibly hours for the air to circulate and maybe longer for hot water to circulate, meant a lot of heat up the chimney before BTU's were delivered to the house. IMO
    John Mills_5
  • donaldmc
    donaldmc Member Posts: 35
    With winter coming, can anyone recommend a good heating guy to service the above antique? It is located in the Hamilton, NY area near Colgate Univ.
    I'm in Westchester county - too far for a service call!
  • leonz
    leonz Member Posts: 1,347
    edited October 2017
    I would call The folks at Isaac Plumbing and Heating in Syracuse and ask for help. They have been doing plumbing and heating for a long time and they have expanded as well. They may also be able to clean the all ducts for your friend as well.
  • newagedawn
    newagedawn Member Posts: 586
    havnt seen one of those for awhile, nice antique
    "The bitter taste of a poor install lasts far longer than the JOY of the lowest price"
  • Dale_3
    Dale_3 Member Posts: 58
    Demolished many Octopus furnaces in my younger days. You never know what you will find in the debris on top of that plenum and in those pipes. That's where my marble & Mil collection started. "That I can't seem to find now. ;) " A lot of history there.
  • kathyann54
    kathyann54 Member Posts: 1
    This is what is heating my house, but one of the vents isn't working. Checked it nothing is blocking it, no heat travels through it...does anyone know what to check or Do? Thank you
  • Fred
    Fred Member Posts: 8,542

    This is what is heating my house, but one of the vents isn't working. Checked it nothing is blocking it, no heat travels through it...does anyone know what to check or Do? Thank you

    Are you sure that"Vent" isn't a gravity return air for the furnace?
  • JUGHNE
    JUGHNE Member Posts: 11,295
    Try holding a single tissue over that grill after all the others are heating, if it is drawn towards the grill then it is a return air duct.

    The cold air returns were often under the windows and the hot air came out in the middle of the house, sometimes....usually.....not always.

    Plus sometimes the hot pipes had a damper built into the register and perhaps also in the pipe in the basement. There would be a lever on the pipe, it runs a shaft going into the pipe.
  • Kybeans403
    Kybeans403 Member Posts: 56
    Right from that beauty into the Lennox Complete Heat System......
    Charlie from wmassSuperTech