Larger PEX piping for hot water heating?
Chuck_17
Chuck_17 Member Posts: 148
How practical is it to use PEX piping for heating hot water systems in commercial (old churches) exposed installations?
It makes total sense in wood frame construction. The only time I have seen larger PEX used, it was strapped to wood floor joists (of a church).
What about in installations where it would have to be hung by regular hangers?
What about risers exposed through a floor to ceiling (to the floor above)?
The reason it is being considered is for cost reasons (a old church that as a small cash poor congregation). (plus copper has a habit of disappearing)
    Jamie Hall Member Posts: 26,169
    The problem with PEX is that when it gets hot it sags and tends to stay sagged. If you can support it adequately, not a problem.
  • Ironman
    Ironman Member Posts: 7,727
    edited March 2017
    Another consideration is the fittings and tools required to join it. They can be very expensive and unless you're planning on continually using them in the future it makes no sense to purchase them for one job.
    Bob Boan
  • Zman
    Zman Member Posts: 7,611
    There are metal trays the allow you to support pex like conventional rigid piping. Another factor to consider is the wall thickness of the larger pex. You often have to go up a pipe size in order to get the same flow. In the end, you may not save money with pex.
    What size pipe? Is steel pipe with Vitolic connections an option?
    Albert Einstein
    hot_rod Member Posts: 25,328
    watch the ID also. The pex doesn't always cross over with copper, capacity wise.
    EBEBRATT-Ed Member Posts: 18,219
    and something I have difficulty getting answers on. The od of pex seldom matches pipe, difficult to insulate and problems if used for chilled water with condensate between the pex and the insulation
  • Zman
    That's what I was getting at. Especially on the larger pipes, the inner diameter is much smaller because of the pipe wall thickness. It has significant impact on flow rates.
    Albert Einstein
  • Chuck_17
    Thanks for the comments.
    Black steel is an option.
    Copper with press fittings is an option.
    Any mix.
    2" or less except near the boiler for which it will be steel (or copper).
    If you are in an area where copper has a way of wandering off... first, my sympathy. Second, it probably would be worth the effort and trouble to use the PEX, supported in a tray or at least at very frequent intervals. All things considered.
  • Zman
    Dan wrote and article about painting the copper black so it would get stolen. Still makes me chuckle....
    Albert Einstein
  • Chuck_17
    I didn't see the article (I'd like to). Sounds like an idea.
    It's not that bad (though I have seen a few situations....) First cost is more of an issue.
  • Grallert
    Grallert Member Posts: 969
    I've hidden my vertical pex risers in black pipe to get from one floor to another. Looks like a steam pipe and in my area there are a lot of steam systems so it's not an unusual thing to see.
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,360
    @Chuck, here's the article about the copper in NYC: https://heatinghelp.com/blog/nyc-one-pipe-steam/
    And here's an article about PEX for hydronic distribution piping that you may find helpful: https://heatinghelp.com/systems-help-center/pex-for-hydronic-distribution-piping/
    President