LP gas pipe question

MBaker
Member Posts: 2
in Gas Heating
I have a 100,000 BTU LP gas heater. Will the piping in this diagram provide enough gas to the heater?

0
Comments
-
80 ft is sufficient for 262,000 BTU0
-
Is there no other equipment? What kind of a "heater" is it a furnace or a boiler?0
-
How far is it from the LP tanks to the house?0
-
using the longest run method puts you at just shy of 91 ft. Using the rego serviceman's guide indicates the 1/2 black iron will be good for 84k. I would size the entire line with at least 3/4" and drop at the unit. It will also leave you a safety net if something is added down the road. Just make sure your twin stage is connected directly to the 3/4 pipe, not with a 1/2 piece of copper...Also want to check the unit and verify they dont require a larger size...some are fussy when it come's to supply and drops in pressure..1
-
It is a reznor 100 udap heater. The tanks are against the outside wall. the 8" section of 1/2" pipe passes through the wall to the outside. I don't foresee anything being added in the future. It is in a warehouse.0
-
Categories
- 81.2K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 37 Biomass
- 394 Carbon Monoxide Awareness
- 2.7K Controls
- 1.4K Domestic Hot Water
- 3.8K Gas Heating
- 101 Geothermal
- 133 Indoor-Air Quality
- 2.4K Oil Heating
- 32 Pipe Deterioration
- 580 Plumbing
- 4.3K Radiant Heating
- 334 Solar
- 12.3K Strictly Steam
- 38 Water Quality
- 11 Industry Classes
- 51 Job Opportunities
- 8 Recall Announcements