LP gas pipe question
MBaker
MBaker Member Posts: 2
I have a 100,000 BTU LP gas heater. Will the piping in this diagram provide enough gas to the heater?
  • Henry
    Henry Member Posts: 998
    80 ft is sufficient for 262,000 BTU
  • Zman
    Zman Member Posts: 7,614
    @Henry
    It looks like ~40' of 3/4" and ~60" of 1/2"
    I think from a code point of view it is slightly undersized.
    Unless the heater is finicky about pressure, it will probably "work".
    Albert Einstein
  • Tim McElwain
    Tim McElwain Member Posts: 4,660
    Is there no other equipment? What kind of a "heater" is it a furnace or a boiler?
  • JUGHNE
    JUGHNE Member Posts: 11,591
    How far is it from the LP tanks to the house?
  • lchmb
    lchmb Member Posts: 2,997
    edited January 2017
    using the longest run method puts you at just shy of 91 ft. Using the rego serviceman's guide indicates the 1/2 black iron will be good for 84k. I would size the entire line with at least 3/4" and drop at the unit. It will also leave you a safety net if something is added down the road. Just make sure your twin stage is connected directly to the 3/4 pipe, not with a 1/2 piece of copper...Also want to check the unit and verify they dont require a larger size...some are fussy when it come's to supply and drops in pressure..
    kcopp
  • MBaker
    It is a reznor 100 udap heater. The tanks are against the outside wall. the 8" section of 1/2" pipe passes through the wall to the outside. I don't foresee anything being added in the future. It is in a warehouse.
  • Henry
    Zman said:
    @Henry
    according to code, 100 feet of 3/4 is good for 232,000 BTU. I would reduce at all to the apliance