Latest steamer install
Dave0176
Member Posts: 1,178
Princeton NJ EG-50 with all new wet returns. Old boiler was an EG-55 installed in 1980 which was oversized.
ins
in
.
ins
in
.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
5
Comments
-
Wow, that old boiler was nasty! Nice job as usual on the new one.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Nice pipe fitting indeed.
Interesting LWCO installation on that old boiler. There appears to have been no way to blow it down.
All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
Beautiful install as always @Dave01760
-
That's quite a hole there. I wonder how long it took them to notice it!
Why the 90 in the left riser? Asthetics?
0 -
Great job, Dave. Where was this located? I'm wondering about chlorides in the feed water.Retired and loving it.0
-
Hey @DanHolohan it is in Princeton NJ the old boiler was installed in 1980 so 36 years. There was a lack of maintenance too. I'm sure chlorides are a factor too.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
-
-
-
-
-
@ChrisJ The old boiler was installed in 1980 so 36 years, not too bad. Also though the boiler was poorly maintained throughout the years. The current owner was taking care of it however I think the problem started years before as I removed some newer piping. There was newer piping on the return and Hartford loop and the riser from the boiler was definitely replaced.ChrisJ said:Good looking install as always Dave.
Any idea how old the previous boiler was? Why did it rott?DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
Nice job as always @Dave0176ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company1 -
Nice pipe work, you need to fill in the hole under the boiler so your secondary air isn't screwed up.
There was an error rendering this rich post.
0 -
thats an install to be proud of..very nicegwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.1 -
You nailed it @Dave0176! Starting with throwing out the old header. Well planned, well thought out, well executed.
Home run.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com1 -
@RI_SteamWorks funny thing is technically according to Weil-McLain minimum specifications that header on the old EG-55 is piped right!! 3" all the way with a 1-1/2 equalizer. Gives a steam exit velocity of 22.59 FPM, waaay to fast for my liking!!!! LolRI_SteamWorks said:You nailed it @Dave0176! Starting with throwing out the old header. Well planned, well thought out, well executed.
Home run.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
There's piping to the minimum specs, and then there's good. You took the time and trouble (and had the expertise) to take it apart and install dual risers into a dropped header, which is really good. Good for you.
And really good for your customer.
But you're modest, I know...New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Nice work....0
-
Hi I am the homeowner the proud new owner of Dave's latest masterpiece. The pictures tell you guys all you need to know about the quality of Dave's work. I would like to comment on the quality of the guys who did the work. Dave and his dad Walt (he helps Dave with installs) made me feel like I had family doing the job. From the energy they poured into their work to just being fun to have around. I mean who the heck would work until 10 PM on a Saturday and then come back Sunday morning with a smile. I also found myself heading down to the basement not to check on them but just to hangout I am sure I got in their way but they didn't complain. In fact Walt who's full-time job is running his Walts Jerky Shop in New Jersey even brought me a ton of free samples (which were fantastic). My teenage sons think I'm nuts making them come down to the basement to stare at the sexy beast that is my new boiler. My younger son just asked me who I am going to hangout out with now that the boilers done? I told him Dave and Walt I mean the things got to be serviced every year.
I know I waited way to long to get this new boiler. In fact I have read a couple of Dan's books and come to the forum often since I moved in 12 years ago. From what I had learned here I never felt comfortable with anyone who came out to see the boiler before Dave. While it could have ended badly with that old steamer I am glad I held out until now. Thanks guys!!3 -
-
Thats great that you had @Dave0176 and his dad install your steam boiler... they do fantastic work....ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company1 -
Yep, gotta agree with all comments of praise. Perfection indeed.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Very nice to know a customer who appreciates a good (way better than good) job. So many only care about the price.
Happily, one of those good customers cancels out several of the ignorant ones.
Nice job , Dave0 -
Really nice0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements