Negative Building Pressure Effects on Category IV Boilers?
RyanO
Member Posts: 4
in Gas Heating
There is a particular boiler manufacturer who is claiming that a slight negative building pressurization has led to a cracked on a cracked heat exchanger on a 2 Million BTU, Category IV Condensing Boiler. Anyone have any experience with this? The negative condition exists but the boiler is sealed combustion and has had no flame failures. It seems to me that if the building pressurization was effecting the boiler then there would have been a flame failure.
0
Comments
-
I would ask for the technical data from the manufacturer which supports such a thing happening. I have over 50 years in the business and have had a lot of strange things happen but this would be a new one for me. I have had many a boiler with negative pressure in the building but can't say I ever had it cause a cracked boiler.
What is the make and model of the boiler?3 -
-
-
I'm going to guess its an Aerco benchmark 2.0.
I would doubt that the pressure in the building has anything to do with the boiler have a bad heat exchanger.0 -
How hard have you followed up on this?0
-
First off... definitely not my boiler. I'm retro commissioning a 10 Million BTUH boiler plant (and the rest of the BAS/HVAC system) with issues and the manufacturer is using the building negative an escape clause for warrantying the HX. kcopp, I totally agree...that's why I came to The Wall. BTW its a Camus.
There are 3 Condensing (Cat IV) and 2 Non-Condening (Cat I), all 2 MBTHU, same make. They share Combustion Air Ducting with isolation dampers. They are flued separately. This was a public project, so I really think the design engineer needs to step up. Of course everyone is pointing fingers and no one wants be accountable or working towards a solution. Nevertheless, I'm determined to find a solution for them.0 -
Check out this thread that references Camus. The last few posts might explain some of what you're experiencing...............
http://forum.heatinghelp.com/discussion/118404/camus-dynamax-residential-modcon-boilers#latestAll Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Thanks, Steamhead! They're DynaFlames also. Maybe its a metallurgic design flaw.
Tim, I'm at least the third guy on the scene here. No as-builts, no start-up docs. Could the combustion air be too cold? If only one of the 5 boilers is running and the other dampers are shut its almost like the 7 times rule backwards but with suction pressure. But then again I would think the burners would love cold air.
I told the Town's Engineer that he needs to hold their feet to the fire. They being: the design engineer, boiler installer, and Camus to make this right for them. I recommended the same thing you did. Call Camus and make them explain how the negative building pressure effects sealed combustion...0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements