How is a Heat Loss Test done?
I'm not sure if you mean a blower door test or a heat loss calculation.Bob Boan
Slant/fin and Taco have freebie PC-based programs for estimating heat loss. Others are available for a price. You enter a bunch of data regarding the room sizes, windows, insulation, etc. Figure about three hours with the help of a tape measure and an assistant.
If you use natural gas, I can suggest a simple quick-and-dirty way using the gas meter and some arithmetic.0 -
Over several hours during cold weather, clock the gas meter to determine usage, in cubic feet. Convert to Btu/hr. Then divide by boiler efficiency, maybe 80% for an older unit. If you run the test at the design ambient temp, then you have calculated the heat loss.
If you run the test at a higher temp than the design temp, adjust the Btu/hr by multiplying by (72-Td) /(72-Ta), where:
Td = outdoor design temp
Ta = actual outdoor temp0 -
Whoops - multiply by boiler eff, not divide, to get heat loss.0
The same method works for oil, if you have a way of measuring the amount of oil used. 138,000 BTU/gallon.Br. Jamie, osb
HDD per btu per sqft. Best method once you nail down the boilers performance. All that is needed is logged run times for heat calls. A digital thermostat does this.
True then that gets complicated. But if you did the math the mod/con would be right size.0