Using and Pulling a Vacuum on oil tank to allow oil line repair.
Comments
-
I'd be really cautious about doing this -- it wouldn't take much vacuum to collapse the tank. Which could ruin your whole day...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
We I have done about 30... I just started doing it a bit different.... Be sure tank is 1/2 full if at all possible,,... Use a tie strap on vent with red rag to block some of vent... be sure fill is tight.. remove plug in basement .. get on floor loosen valve just a bit... put dope on new valve.. have your partner turn on vac... 2 seconds off and 2 seconds on... done...2
-
Done many that way too burnerman. Alone usually
0 -
Done it too, it works. But you won't find anything documented.0
-
I have pulled a plug inside the basement...put the hose in, put an extension cord next to me an turn it on when ready....I wont generally do it if the tank is 10+ years...not sure my heart can handle the stress on old tanks...memory serves me right, there used to be an adapter you could purchase. you set the adapter to how full the tank was and it set the vacuum...1
-
-
I don't think a shop vac will collapse an oil tank.Jamie Hall said:I'd be really cautious about doing this -- it wouldn't take much vacuum to collapse the tank. Which could ruin your whole day...
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
The trick is you don't need absolute suction. Don't seal the vent, then seal around your hose on the supply.
I always use 2 people and we talk on the phone.
Slowly open the valve (pan underneath) and it's basically communicating "a little more, a little less, hold it there". Swap out valve leave it open. Soon as it's in, stop vac, close valve.
A soot vac can collapse a tank. I use an 18 volt Milwaukee.There was an error rendering this rich post.
0 -
A soot vac can collapse a tank?STEVEusaPA said:The trick is you don't need absolute suction. Don't seal the vent, then seal around your hose on the supply.
I always use 2 people and we talk on the phone.
Slowly open the valve (pan underneath) and it's basically communicating "a little more, a little less, hold it there". Swap out valve leave it open. Soon as it's in, stop vac, close valve.
A soot vac can collapse a tank. I use an 18 volt Milwaukee.
Are we talking oil canning the sides that'll just pop back out, or?
I'm just finding it a bit hard to stomach that a simple single stage high volume centrifugal blower could literally crush an oil tank.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Supposedly the little mechanical pump in old cars could collapse your gas tank if it were not vented.
How about the old school overhead hanging compression tank,
could just draining with long hose be enough to collapse it?0 -
That'd a liquid pump pumping liquid.JUGHNE said:Supposedly the little mechanical pump in old cars could collapse your gas tank if it were not vented.
How about the old school overhead hanging compression tank,
could just draining with long hose be enough to collapse it?
Not even close to the same.
I'm sure if the hose is long enough, yes it could collapse a tank. Or, a water heater for example.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
My business was located near a US Coast Guard base. I was called to a tank leak only to find a Coasty in Dress Blues lying under the tank with this finger on the hole that he had just uncovered by flicking a flake of rust off the bottom. He was in a panic because he was going to be late for his deployment on a Cutter leaving within the hour.
I plugged in my soot vacuum cleaner and relieved him of duty (as the "Little Dutch Boy" holding back the environmental insurance claim flood dike.)
This is something I was taught by a service manager from my father's 4000+ customer fuel oil business. Sometimes this is the only way many of the tricks of the trade are passed down.
Who in the right mind would want the liability of a disaster happening as a result of an idiot trying to follow published instructions on how to properly complete the procedure. As I have said in previous posts: "This is why McDonald's coffee cups say CAUTION: CONTENTS HOT. "
This is why you will almost never see an official "How To" on this procedure. BUT Geroge Lanthier, a frequent contributor to several HVAC publications, did include the procedure in this article a few years back: https://fueloilnews.com/2016/05/26/a-few-tricks/
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
A new tank, probably not. An old tank, weak/compromised tank? I'm not saying it's going to crush like a tin can, but it will pull in, even a little violently (did that by accident once). Especially, if it's an old tank when people were using 14 gauge tanks.ChrisJ said:
A soot vac can collapse a tank?STEVEusaPA said:The trick is you don't need absolute suction. Don't seal the vent, then seal around your hose on the supply.
I always use 2 people and we talk on the phone.
Slowly open the valve (pan underneath) and it's basically communicating "a little more, a little less, hold it there". Swap out valve leave it open. Soon as it's in, stop vac, close valve.
A soot vac can collapse a tank. I use an 18 volt Milwaukee.
Are we talking oil canning the sides that'll just pop back out, or?
I'm just finding it a bit hard to stomach that a simple single stage high volume centrifugal blower could literally crush an oil tank.
You could get a soot vac and try it for yourself...:)There was an error rendering this rich post.
0 -
Agree with @STEVEusaPA above. With an additional observation. Many fuel tanks fail as a result of corrosion from inside the tank. Think about the old tank with several compromised locations that are almost rusted thru. Now, a vacuum will take away the pressure of the fuel holding down some tank bottom deposits on those locations. Maybe some microbubbles start to enter thru the pin-holes. If the repair takes more time, the pinholes grow with the effects of erosion of the air across the openings as long as the vacuum is operating.
Ok, now you are finished your repair. You turn off your vacuum and... oops, the bottom of the tank starts to weep. Now it is time to remove the oil and replace the tank. But at least the oil is not in the ground!Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Point taken.
However, if the tank is that compromised, wouldn't you insist on replacing it rather than waiting for it to fail in a few months or a year?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Yes, Definitely. The procedure works on new tanks that need a new valve that broke off and left the threaded part in the tapping AND on old tanks that need replacing. You keep the oil in the tank and off the ground.
Once the emergency is over, now you take the time to make the necessary remediation. That can be to just clean up the minor spill on a good tank or to replace the bad tank. I recall another emergency fix I used when I was on a service call alone and had to stop a leaking tank.
It was an outside above ground tank that was less than 1/2 full. I disconnected the fuel line from the tank valve, put a plug in the vent opening, removed the gauge and plugged that opening also, and pushed the tank on its side. The oil level was now below the leak in the bottom and the top openings where you fill and vent the tank.
This won't work on a full tank for obvious reasons. Once the oil can no longer leak on the ground, you can take your time and pump into drums.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Just for a giggle check on the collapse possibility. Let's suppose that your vacuum -- soot, shop, whatever -- can develop 2 psi of vacuum That's less than the vacuum picking up a bowling ball ad. Then let's suppose that the tank has a flat side 4 feet long and 2 feet high. That's about 1,000 square inches. The vacuum, given time and no leaks, will exert a force of 2,000 pounds on the sides... might not collapse, but I wouldn't want to bet on it.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Well, a few things. "that compromised" is hard to quantify (qualify)? We're not X-Raying them. Now if it's leaking, that's another thing.ChrisJ said:Point taken.
However, if the tank is that compromised, wouldn't you insist on replacing it rather than waiting for it to fail in a few months or a year?
Second point, if I replaced every tank where people took my recommendation to replace it, I'd be doing mostly tanks.
Most people just wont replace it until it leaks, weeps or their insurance company or realtor (new buyer) makes them. Or they yank them and switch to gas. Even staining around the end welds on older tanks doesn't scare them.
Back to the original post topic. This is why I hate firomatic valves. Their failure rate is quite high, as opposed to nearly zero failures on a ball valve. The vacuum trick has almost always been used exclusively for firomatics, and some old gate valves. If the whole thing is rusted, like a side bung on an old tank and valve, I won't put a wrench on it. But I will add a second valve, until tank replacement. I'm done with super speedy filter replacement over a bucket or pan.
I always use a ball valve at the tank, then a firomatic. Never even had an inspector notice.There was an error rendering this rich post.
1 -
George is the best. I'm partial to that article as he put my power vacuum bleed pot in it Also he mentioned not to do the vacuum trick on 14 ga tanks.EdTheHeaterMan said:My business was located near a US Coast Guard base. I was called to a tank leak only to find a Coasty in Dress Blues lying under the tank with this finger on the hole that he had just uncovered by flicking a flake of rust off the bottom. He was in a panic because he was going to be late for his deployment on a Cutter leaving within the hour.
I plugged in my soot vacuum cleaner and relieved him of duty (as the "Little Dutch Boy" holding back the environmental insurance claim flood dike.)
This is something I was taught by a service manager from my father's 4000+ customer fuel oil business. Sometimes this is the only way many of the tricks of the trade are passed down.
Who in the right mind would want the liability of a disaster happening as a result of an idiot trying to follow published instructions on how to properly complete the procedure. As I have said in previous posts: "This is why McDonald's coffee cups say CAUTION: CONTENTS HOT. "
This is why you will almost never see an official "How To" on this procedure. BUT Geroge Lanthier, a frequent contributor to several HVAC publications, did include the procedure in this article a few years back: https://fueloilnews.com/2016/05/26/a-few-tricks/There was an error rendering this rich post.
0 -
Soot vac.. the best tool (underated) it the the truck.
Boiler drain, done.
Fuel tank, done.
Water heater issue, Done.
A Slight pressure difference is all that is needed.
Not trying to implode anything.0 -
BDR529 said:Soot vac.. the best tool (underated) it the the truck. Boiler drain, done. Fuel tank, done. Water heater issue, Done. A Slight pressure difference is all that is needed. Not trying to implode anything.0
-
For a boiler drain or relief valve if I can’t drain what I need, I have used a little pump that you hook to a vs cordless drill (with a washer machine hose) to pull a slight vacuum to swap it out.
There was an error rendering this rich post.
0 -
As a retired underground tank tester, we had to go thru a bunch of steps before determining how much "negative" pressure to "pull" on the tank to "lift" the product, to test the bottom of the tank. We had to be certified with the equipment manufacture and State to do this.
We used expensive manometers, backup gauges, blower motors, and followed a set protocol. It was about $1,200 a year, just for the yearly calibration of the equipment.
But at the end of the day......we are both "sorta" doing the same thing. Lifting the product off the bottom of the tank.
So, a tank with 24" of heating oil in it would require about .774 of negative psi to start to lift the product. Then add .5 psi for insurance and you got 1.244 of negative pressure.
As a tank tester, we talked in positive and negative pressures. For some reason we were told not to say vacuum, not sure why.
So to comment on Jamie Hall above, 2 psi of negative pressure on a standard 275 heating oil tank would be slightly more than I would pull on it.
As a note, I would pull the same amount of negative pressure on a 20,000 gallon tank with 24" of heating oil as I would a 275 gallon tank with 24" of fuel oil.
The 20,000 gallon tank, because of the large ullage (air space) might take 30 minutes to get to the test pressure.
The 275 tank might 2-4 seconds, because of the small ullage. The small tank would be very difficult to maintain a constant negative pressure and care would have to be taken that it was not going too negative.
Back when I worked, I was Pa. DEP certified Underground Inspector, Installer, Removal, Tank Tightness Tester and everything else. If I would have used a shop vac and rags to pull a vacuum on a tank, I might have got into trouble, ah no, big trouble.
But in Pa., a heating oil tank, even a 20,000 heating oil tank is not a regulated tank. Sure there's responsibilities, but its not a regulated tank.
0 -
@Ignatz
Best I can tell, a typical vacuum cleaner produces at best around 2.25 PSI of vacuum.
Do you feel that could collapse or damage an oil tank that is in reasonably good shape?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
No, but I would have never been that high. I would have been around 1.5 psi max. Also a smaller tank has more rigidity and is less likely to pull a side in. You never hear about people collapsing home heating oil tanks.
Years back, there were single wall steel tanks that had compartment baffles in them, so one side had regular, and the other side premium. You had to "pull" them down equally, but many times they "Bonged" where you heard it and felt it thru your feet.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements