Steam replacment coming up
Comments
-
ChrisJ, you might be right. I don't know what the operating characteristics of the boiler are when derated by manifold pressure. I know that the LGB series is available with a 2-stage valve and I have been told that it remains very efficient on low fire. So, for the EG, I don't know. Did you do any efficiency testing on yours in an underfire operation? I was told by one of the pros that my old Pennco, which was firing at a reduced rate would have a high amount of excess air and a significant loss of efficiency. The huge improvement when the boiler was replaced seemed to substantiate that.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
No testing on mine in that regard as I don't plan in underfiring it. When it gets cooler out Jstar will be coming out to set things out so maybe he'll be interesting in trying that, I don't know.Dave in QCA said:ChrisJ, you might be right. I don't know what the operating characteristics of the boiler are when derated by manifold pressure. I know that the LGB series is available with a 2-stage valve and I have been told that it remains very efficient on low fire. So, for the EG, I don't know. Did you do any efficiency testing on yours in an underfire operation? I was told by one of the pros that my old Pennco, which was firing at a reduced rate would have a high amount of excess air and a significant loss of efficiency. The huge improvement when the boiler was replaced seemed to substantiate that.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Final pics of installDL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
What's up with that connection into the chimney?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
-
The chimney was just lined, thats the bricks just shoved back into place, it all needs to be cemented. The boiler is fully connected to the flue.ChrisJ said:What's up with that connection into the chimney?
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements