Low water cutoff and water feed Suggestions
The water feed and the low water cutoff combo stopped working years ago due to leaks, so I started to fill the water manually with no problem. However I plan to leave in the winter coming up for an extended period and I want to add the cutoff and the water feed back.
I just bought the Model 67 Mcdonnell Miller LWCO as I got a good deal on it and now I am looking for a compatible water feed unit to work with it. I have seen several advertised
WFE24 Unimatch
WFE 120 Unimatch
101A-120
101A-24
I believe I need the 24 volt versions in each case. I am leaning towards the WFE24 Unimatch unless someone knows of a better part to use. The others are more expensive. I have heard the 101 A-24 gasket leaks
Any ideas?
Comments
-
-
I'd prefer the Hydrolevel -- I have one, and the built in water meter is very handy indeed.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Does the Hydro level VXT measure the actual gallons of water fed, or merely the time the valve is open?
I have resisted an auto feeder up to now, but now have a very small leak in one of the rubber gaskets between sections of my 2007 installed PB 211A-1,050,000 BTU, (confirmed by an overfill test).
Maybe I just should bite the bullet, and have the end section taken off for examination as soon as the heating season is over. However, if one has developed a leak, I wonder about the others.-NB-C
1 -
If it has not been leaking long you can probably just rejacket that section
1 -
My idea is leave it like it is and have a friend check your house once per week.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Hydrolevel measures by the gallon…
There was an error rendering this rich post.
0 -
Not really. They measure by the assumed gallon. It has no mechanism to measure how much water actually passes through. It just measures how many minutes, it's supposedly feeding. It assumes that it's one gallon per minute. Let's say for example you shut the ball valve upstream of the feeder. It will feed nothing, but it will still register the minutes that it thinks it's feeding.
2 -
Even so, the VXT is by far the best choice.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
That's good to know ..
There was an error rendering this rich post.
0 -
Thanks -that’s what I needed to know.
I will probably leave it valved off, and just top it off from time to time, as needed, but I will have an idea about how much water loss occurs in the future. -NBC
0 -
i HAVE SEEN MORE BOILER FAIL BECAUSE THE FOLKS WHO WERE ASSIGNED TO CHECK IT, QUIT, MOVED, WENT ON VACATION. BAD MOVE. Get the feeder and leave the feed valve partialy open, if you don't want the water to rush in.
I cut back my feed valves quite often. Boilers are not receiving condensate fast enough and can often add too much water.
John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.0 -
Your story rings false.
A boiler is going to fail if it fires without water. We all understand this.
The LWCO triggers the boiler to stop, and it also triggers the auto-feed to feed.
If you don't have an auto-feed, the boiler will simply stop firing. It will not fail.
Unless the LWCO has failed first.
But if the LWCO has failed, it won't call for water either.
So you cannot blame the failure of a boiler simply on the lack of an auto feed.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
If the mc d miller is full of mud due to lack of blow down practice to clear it, the ball will be stuck on top of the mud. The water fill will not be triggered. Combine that with the secondary lwco failure, which is seldom cleaned, the boiler will cook down and fail. Seen it too many times.
John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.0 -
Yes, if you don't blow down a float LWCO it can get stuck. But that problem isn't solved by an auto-feeder. If the float is stuck the auto-feeder won't be called upon.
My suggestion that you disagreed with to have a friend check their boiler weekly is compatible with proper weekly flushing of a float-style LWCO (which itself is getting very rare today in single and double residential situations).
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
When the friend doesn't show up is when you have a problem. I have seen it often enough, that this method should not be an option.
John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.0 -
I agree! But you are the one who warned of float LWCOs not getting flushed…so I guess you agree with me too! If having a friend check on your property isn't an option, who is flushing the LWCO?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
MC Mil flushing is not necessary that often. Depends on how dirty your system water is. I have seen them flushed once every six months and they still operate well in between. You will know when you flush it. If the water is clean you can do it less frequestly. Its like soup , taste and adjust. If there is a lot of dirt when you flush, clean the boiler.
John Cockerill Exquisite Heat www.exqheat.com Precisions boiler control from indoor reset.0 -
I agree with that too, but the manufacturers say weekly. But anyway those are finally going the way of the do-do, at least in residential it seems.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 119 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements