Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Balancing my Heating system . Help .

1235»

Comments

  • misterheat
    misterheat Member Posts: 158
    edited November 2017
    Quick question . A few people have recommened changing the pressure guage on my boiler , if I change my pressure gauge to a wika 0 to 3 gauge. When performing a blow down how do you know when you get to 10 lbs in the boiler? Thanks.
  • Canucker
    Canucker Member Posts: 722
    Put the low pressure gauge on a tee with your 30 psi gauge. Have a valve to isolate the small gauge when you do blowdowns
    You can have it good, fast or cheap. Pick two
    misterheat