considering putting a radiator in the basement

24

Comments

  • maybemark
    maybemark Member Posts: 1,131
    I have a count of all the radiators, how tall, how many sections, how many columns
  • maybemark
    maybemark Member Posts: 1,131
    SWEI
    ok, thank you for your time
  • SWEI
    SWEI Member Posts: 7,356
    51,000 BTU/hr would need 5.1 GPM at a 20˚F ΔT or 3.4 GPM at a 30˚F ΔT. Head loss on 3/4" Type L copper is 1.9 feet per hundred feet at 4 GPM and 2.9 feet per hundred feet at 5 GPM. Isn't most of your loop larger diameter steel pipe?
  • maybemark
    maybemark Member Posts: 1,131
    yes, my loop starts off with 3" pipe, goes down to 2" pipe amd the last 20' os 1 1/2" pipe. most brances are 1" and the 4 radiator Fred added are 3/4" copper
  • maybemark
    maybemark Member Posts: 1,131
    I'm a 60 year old baby when it comes to the boiler. I am trying to learn, and i have learned a little bit, for the short time i have been on this site. All the help that has been given to me, I truely appreciate. There is so much more to learn. I am not the one that will be doing the install. i will be helping, but, Fred will be doing the work. But he's old school, and needs knowledge when it come to mod/com boilers. I am trying to learn for him.
    thanks everyone
    Mark
  • Gordy
    Gordy Member Posts: 9,546
    Mark I did your edr calcs you lose them??
  • maybemark
    maybemark Member Posts: 1,131
    Gordy, did you calculate on an e-mail? I can check or from this site?
  • maybemark
    maybemark Member Posts: 1,131
    Gordy calculated it before

    You are over radiated for your heat loss that's good. 136000 btus for the whole house. that's based on 150 btus per sf of radiation at 180* water temp. So that means you can run lower water temps to the radiators so your HE boiler will be more efficient.
    * is this what your looking for?
  • maybemark
    maybemark Member Posts: 1,131
    Living Room:
    142.8 SF EDR. 21420 BTUS at 180* water
    84.0 SF EDR 12600 BTUS

    Hall
    30 SF EDR 4500 BTUS

    Dining RM
    51 SF EDR 7650 BTUS

    M.Bed
    39 SF EDR 5850 BTUS

    Bed 2
    30 SF EDR 4500 BTUS

    M.Bath
    21 SF EDR 3150 BTUS

    Kitchen
    58.74 SF EDR 8811 BTUS
    74.76 SF EDR 11214 BTUS Figured these at 20" tall

    Office
    48 SF EDR 7200 BTUS

    Powder RM
    17.5 SF EDR 2625 BTUS

    2nd Floor
    Kitchen
    60 SF EDR 9000 BTUS

    Bed 100.8 SF EDR 15120 BTUS

    Dining
    29.37 SF EDR 4405.5 BTUS

    Living RM
    60.62 SF EDR 9093 BTUS.
  • maybemark
    maybemark Member Posts: 1,131
    SWEI
    is this what you were asking me for?
  • SWEI
    SWEI Member Posts: 7,356
    The BTU numbers shown are calculated from the EDR -- what are the heat losses for each of those rooms?
  • maybemark
    maybemark Member Posts: 1,131
    front hall 5496
    living room 15565
    hall 327
  • maybemark
    maybemark Member Posts: 1,131
    dining room 6279
    middle hall 723
    master bed 6065
    bathroom 2353
    kitchen 7351
    office 4266
    powder room 1271
    2nd bed 1360
  • maybemark
    maybemark Member Posts: 1,131
    2nd floor
    hall 116
    bedroom 6527
    kitchen 5472
    bathroom 2604
    dining room 3224
    living room 7499
  • SWEI
    SWEI Member Posts: 7,356
    Some of those names don't match up. Here's what I have, but something is amiss:

    EDR Heat Loss
    Living Room 227 15,565
    Hall 30 5,496
    Dining RM 51 6,279
    M.Bed 39 6,065
    Bed 2 30 1,360
    M.Bath 21 2,353
    Kitchen 134 7,351
    Office 48 4,266
    Powder RM 18 1,271


    Kitchen 60 7,351
    Bed 101 6,527
    Dining 29 3,224
    Living RM 61 7,499
  • maybemark
    maybemark Member Posts: 1,131
    swei
    I don't understand these numbers, and what do you mean that something is amiss
  • maybemark
    maybemark Member Posts: 1,131
    some rooms have a couple radiators and the halls do not have any radiators
  • maybemark
    maybemark Member Posts: 1,131
    I see the front hallway was left out with the radiators
  • maybemark
    maybemark Member Posts: 1,131
    I see you missed the bathroom on the 2nd floor
  • SWEI
    SWEI Member Posts: 7,356
    There is no 2nd floor bathroom shown in the EDR post. Just fix them so we have correct numbers, matching total EDR for each space with the heat loss for that same space.
  • maybemark
    maybemark Member Posts: 1,131
    ok, I'll fix them sorry
  • maybemark
    maybemark Member Posts: 1,131
    1st floor
    room heat loss output
    front hall 5496 4500
    living room 15565 34020
    hall 327 no rad
    dining room 6279 7650
    mid hall 723 no rad
    mast bed 6065 5850
    mast bath 2353 3150
    kitchen 7351 20,025
    office 4266 7200
    powder rm 1271 2625
    2nd bed 1360 4500

    2nd floor
    hall 116 no rad
    bed 6527 15120
    kitchen 5472 9000
    bath 2604
    dining rm 3224 4405
    liv rm 7499 9093


    bathroom radiator
    8 sections 20" tall 9.5" wide 6 columns
  • maybemark
    maybemark Member Posts: 1,131
    I typed it better than how it came out
  • SWEI
    SWEI Member Posts: 7,356
    I was looking for EDR, but I can derive that from your output figures. Do the two halls have any exterior walls? It looks that way, in which case their ceiling and/or floor areas should have been factored into something else. Not enough to worry about in any case.
  • maybemark
    maybemark Member Posts: 1,131
    I can give you edr, and no, the halls are inside
  • maybemark
    maybemark Member Posts: 1,131
    front hall 30
    liv rm 227
    hall 0
    dining 51
    mid hal 0
    mast bed 39
    mast bat 21
    kitch 133
    powder rm 17.5
    2nd bed 30
  • maybemark
    maybemark Member Posts: 1,131
    2nd floor
    hall 0
    bed 101
    kitchen 134
    bath 18
    dining rm 29
    living room 61
  • maybemark
    maybemark Member Posts: 1,131
    when i did a heat loss I used the slant fin calculator, that took everything into account
  • maybemark
    maybemark Member Posts: 1,131
    what i wrote on the wall of the dimentions of the radiator in the bath is wrong
    18 edr is correct
  • SWEI
    SWEI Member Posts: 7,356
    System balance seems worse than I would have expected from the Dead Guys. The third column (ahem) here shows how many BTUs per square foot of EDR are needed to heat the room to the indoor design temp at outdoor design conditions:

    EDR Heat Loss Btu/sqft
    Living Room 227 15,565 68.6
    Front Hall 30 5,496 183.2
    Dining RM 51 6,279 123.1
    M.Bed 39 6,065 155.5
    Bed 2 30 1,360 45.3
    M.Bath 21 2,353 112.0
    Kitchen 134 7,351 55.1
    Office 48 4,266 88.9
    Powder RM 18 1,271 72.6


    Kitchen 134 7,351 54.9
    Bed 101 6,527 64.8
    Bath 18 2,604 144.7
    Dining 29 3,224 109.8
    Living RM 61 7,499 123.7
  • maybemark
    maybemark Member Posts: 1,131
    so, when you say worse, what does thiss mean?
  • Gordy
    Gordy Member Posts: 9,546
    May be the dead guys did not do as bad as we think a lot depends on original floor plan verses modern changes through the structures history. Definitely some imbalances I was noticing too. But then we really don't know the floor plan, except obvious private rooms , bed rooms, baths.


    I have to ask Mark did your heat loss reflect unconditioned space below main level floors?
  • Gordy
    Gordy Member Posts: 9,546
    edited January 2015
    maybemark said:

    so, when you say worse, what does thiss mean?


    What it means Mark is experimenting with a one AWT fits all. Or TRVs. Or manual balancing with the rad valves.

    In a perfect world which is a rarity your required btu per SF would be the same for each rad to heat the space with one AWT.
  • maybemark
    maybemark Member Posts: 1,131
    I did not calculate the basment, and when i figured the 1st floor, i calculated as unheated area below
  • maybemark
    maybemark Member Posts: 1,131
    did i mess up when i did my heat loss calculations?
  • Gordy
    Gordy Member Posts: 9,546
    edited January 2015
    Only you would know. Your basement is 50* usually you indicated from previous posts. This would create a loss to the space above. Your room heat loss calculator asks floor detail for the space.( floor factor) What did you use?
  • maybemark
    maybemark Member Posts: 1,131
    my house is not in the pefect world it seems, will the whn085 be good for me, and can i put a radiator in the basement, and I still not sure what is meant by worse.
    will my system work?
  • maybemark
    maybemark Member Posts: 1,131
    I did not figure the basement at all in the calculations.
    I asked on a few posts i did, how it should be done
  • maybemark
    maybemark Member Posts: 1,131
    did I mess up? is the 85K going to work for me?
  • Gordy
    Gordy Member Posts: 9,546
    Say on the main floor living room. That floor is over a 50* basement. The floor factor on the slant fin calculator asks if the floor for the living room is over conditioned space meaning heated. Over unheated enclosed space etc what did you enter?