Zone line thermowells
Options
Brad White
Member Posts: 2,399
Go up one pipe size. My ideal location is in a tee at a bend such that the stem points into the flow and the leaving flow goes out the branch. Good turbulence around the bulb too.
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad
-Ernie White, my Dad
0
Comments
-
I am going to be installing solder type thermowells in my zone return lines for thermometers, and am concerned that the probe intrusion into the T's might have an ill effect on circulation. I was unable to find this addressed anywhere in the archives. Are my concerns unfounded?
Jon L.0 -
Thermwells
Instead of a tee I use a cross,very expensive, as compared to a same size tee but the restriction is less.0 -
Thermowell
Thank you for the input. The step up in size seems to be just the ticket for us. Thanks again.
Jon0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 76 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements