boiler for domestic hot water load
Options
Jed_2
Posts: 781
Call Pierre at Turbomax, dump the 500 gal. behemoth, and get into the 21st Century.
Jed
Jed
0
Comments
-
how do i size this
how would i size a boiler that is only going to run a 5 hundred gallon indirect for a sixty unit appt. building.0 -
would love to
we are on a strict budget and the owner wants us to use the tank it is only 5 years old. just need some help sizing the boiler properly.0 -
What is
the fixture unit demand load? It all starts from there. Then, it is simple math.
Jed0 -
loads
the units are all 1 bed, 1 bathroom and kit sink. Peak demand would be in the morning and evening. There would be 60 showers and 120 sinks.0 -
sizing
What u have there now to heat the water?
Are u running out of hot water?0 -
find out the make & model of the tank. go on their website & they should provide performance stats at a specific boiler btu & water temp. That would be the btu's required for domestic hot water production. If the boiler is being used for space heating, do a heatloss to make sure your covered for both scenarios.0