boiler for domestic hot water load

Jed_2
Jed_2 Member Posts: 781
Call Pierre at Turbomax, dump the 500 gal. behemoth, and get into the 21st Century.

Jed

Comments

  • mark_75
    mark_75 Member Posts: 3
    how do i size this

    how would i size a boiler that is only going to run a 5 hundred gallon indirect for a sixty unit appt. building.
  • mark_75
    mark_75 Member Posts: 3
    would love to

    we are on a strict budget and the owner wants us to use the tank it is only 5 years old. just need some help sizing the boiler properly.
  • Jed_2
    Jed_2 Member Posts: 781
    What is

    the fixture unit demand load? It all starts from there. Then, it is simple math.

    Jed
  • mark_75
    mark_75 Member Posts: 3
    loads

    the units are all 1 bed, 1 bathroom and kit sink. Peak demand would be in the morning and evening. There would be 60 showers and 120 sinks.
  • sizing

    What u have there now to heat the water?
    Are u running out of hot water?
  • John_82
    John_82 Member Posts: 63


    find out the make & model of the tank. go on their website & they should provide performance stats at a specific boiler btu & water temp. That would be the btu's required for domestic hot water production. If the boiler is being used for space heating, do a heatloss to make sure your covered for both scenarios.