EDR
Am I right when I use 230 BTU's per square foot when sizing steam radiators?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
  • 240
    for steam, less for hot water.
    Noel
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Most references I find (including Dan's) state 240 btu/hr per sqft EDR (assuming 1psi steam @ 215° in a 70° room).
  • Right on
    Thank's guys. This is for a house in SF. They want to change out some of the radiators and I want to get the sizing right.
    Best wishes,
    Alan
    A STRANGE thing
    about some EDR tables, the ones that show a 10 btu/hr increase in output for each 5° increase in temperature...i.e. 110 btu @ 150°
    At 95° (following that progression) the radiator is putting out ZERO btu/hr!!!!
    Simple math: 95° is (11 * 5) or 55° lower than 150°.
    11 "increments" times 10 = 110. 110 - 110 = 0 btu/hr @ 95°
    IMPOSSIBLE!!!!!
    Some of the radiators in my house heat the space to 70° when 8° outside (design temp) with a surface temperature LESS than 95°!!!!! This IS verified, I promise.
    By using this formula I was able to quite accurately predict the surface temperature of a radiator (measured top, center) based on outside temperature:
    Rad Output = (surface temp - room temp) * 1.5 * sqft EDR. This DOES NOT THOUGH have a 1psi STEAM rad putting out 240 btu/hr/sqftEDR!
    I really believe some tables have an error that comes mainly from a delta-t error regarding water vs. steam!!!!!!