Am I right when I use 230 BTU's per square foot when sizing steam radiators?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
240
for steam, less for hot water.
Noel0 -
Most references I find (including Dan's) state 240 btu/hr per sqft EDR (assuming 1psi steam @ 215° in a 70° room).
0 -
Right on
Thank's guys. This is for a house in SF. They want to change out some of the radiators and I want to get the sizing right.
Best wishes,
Alan
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
A STRANGE thing
about some EDR tables, the ones that show a 10 btu/hr increase in output for each 5° increase in temperature...i.e. 110 btu @ 150°
At 95° (following that progression) the radiator is putting out ZERO btu/hr!!!!
Simple math: 95° is (11 * 5) or 55° lower than 150°.
11 "increments" times 10 = 110. 110 - 110 = 0 btu/hr @ 95°
IMPOSSIBLE!!!!!
Some of the radiators in my house heat the space to 70° when 8° outside (design temp) with a surface temperature LESS than 95°!!!!! This IS verified, I promise.
By using this formula I was able to quite accurately predict the surface temperature of a radiator (measured top, center) based on outside temperature:
Rad Output = (surface temp - room temp) * 1.5 * sqft EDR. This DOES NOT THOUGH have a 1psi STEAM rad putting out 240 btu/hr/sqftEDR!
I really believe some tables have an error that comes mainly from a delta-t error regarding water vs. steam!!!!!!0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 418 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 58 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements